The idea of regular testing is to essentially detect failures on your time 
schedule rather than entropy's (or Murphy's). There can be flaws in your 
testing methodology too. This is why generic load bank tests and network load 
simulators rarely tell the whole story.

Customers are rightfully unpleased with any testing that affects their normal 
peace-of-mind, and doubly so when it affects actual operational effectiveness. 
However, since no system can operate indefinitely without maintenance, failover 
and other items, the question of taking a window is not negotiable. The only 
thing that is negotiable (somewhat) is when, and only in one direction (ahead 
of the item failing on its own). 

So, taking this concept to networks. It's not negotiable whether a link or a 
device will fail, the question is only how long you are going to forward bits 
along the dead path before rerouting and how long that rerouting will take. 
SONET says about 50ms, standard BGP about 30-300seconds. BFD and other things 
may improve these dramatically in your setup. You build your network around 
your business case and vice versa. 

Clearly, most of the known universe has decided that BGP time is "good enough" 
for the Internet as a whole right now. Most are aware of the costs in terms of 
overall jitter, CPU and stability if we reduce those times too far. 

Its intellectually dishonest to talk about never losing a packet or never 
forwarding along a dead path for even a nanosecond when the state-of-the-art 
says something very different indeed. 

Deepak Jain
AiNET

> -----Original Message-----
> From: Dylan Ebner [mailto:[email protected]]
> Sent: Wednesday, August 26, 2009 11:33 AM
> To: Dan Snyder; Ken Gilmour
> Cc: NANOG list
> Subject: RE: Data Center testing
> 
> I would hope that the data center engineers built and ran suite of
> tests to find failure points before the network infrastructure was put
> into production. That said, changes are made constantly to the
> infrastructure and it can become very difficult very quickly to know if
> the failovers are still going to work. This is one place where the
> power and network in a datacenter divulge. The power systems may take
> on additional load over the course of the life of the facility, but the
> transfer switches and generators do not get many changes made to them.
> Also, network infrastructure tests are not going to be zero impact if
> there is a config problem. Generator tests are much easier. You can
> start up the generator and do a load test. You can also load test the
> UPS systems as well. Then you can initiate your failover. Network tests
> are not going to be zero impact even if there isn't a problem. Let's
> say you wanted to power fail a edge router participating in BGP, it can
> take 30 seconds for that routers route to get withdrawn from the BGP
> tables of the world. The other problem is network failures always seem
> to come from "unexpected" issues. I always love it when I get an outage
> report from my ISP's or datacenter and they say an "unexpected issue"
> or "unforseen issue" caused the problem.
> 
> 
> Dylan
> -----Original Message-----
> From: Dan Snyder [mailto:[email protected]]
> Sent: Monday, August 24, 2009 8:39 AM
> To: Ken Gilmour
> Cc: NANOG list
> Subject: Re: Data Center testing
> 
> We have done power tests before and had no problem.  I guess I am
> looking for someone who does testing of the network equipment outside
> of just power tests.  We had an outage due to a configuration mistake
> that became apparent when a switch failed.  It didn't cause a problem
> however when we did a power test for the whole data center.
> 
> -Dan
> 
> 
> On Mon, Aug 24, 2009 at 9:31 AM, Ken Gilmour <[email protected]>
> wrote:
> 
> > I know Peer1 in vancouver reguarly send out notifications of
> > "non-impacting" generator load testing, like monthly. Also InterXion
> > in Dublin, Ireland have occasionally sent me notification that there
> > was a power outage of less than a minute however their backup
> > successfully took the load.
> >
> > I only remember one complete outage in Peer1 a few years ago... Never
> > seen any outage in InterXion Dublin.
> >
> > Also I don't ever remember any power failure at AiNet (Deepak will
> > probably elaborate)
> >
> > 2009/8/24 Dan Snyder <[email protected]>:
> > > Does any one know of any data centers that do failure testing of
> > > their networking equipment regularly? I mean to verify that
> > > everything fails over properly after changes have been made over
> > > time.  Is there any best practice guides for doing this?
> > >
> > > Thanks,
> > > Dan
> > >
> >
> 


Reply via email to