Don,
Thanks for this information. The max equipment width of 21.25" is
what I was looking to verify and several sources are in agreement. Your
assistance is greatly appreciated.
Thx,
Joe
-----Original Message-----
From: Don Robert House [mailto:[email protected]]
Sent: Friday, February 21, 2003 2:29 AM
To: Joe Finlayson; Ed Hickey
Cc: [email protected]; [email protected]
Subject: RE: Equipment dimensions for 23" Rack
Importance: High
Joe and Ed,
I took careful measurements today. 23" is the distance between the
far ends of the mounting ears on the sides of the equipment. The
maximum width of the equipment itself is 21 1/4 inches. The center
of the mounting holes on one side to the center of the holes on the
other side is 22 1/4". The inside opening width is 21 1/2" and the
outside width measurement of the network rack is 26". The standard
heights for "23 inch" network equipment racks are 7 foot, 9 foot, and
11 foot 6 inches.
I hope this is somewhat helpful to you. I will continue to look for
appropriate documentation.
Don
--
Don R. House,
Technical Representative
From - Sat Feb 22 07:52:00 2003
Return-Path: <[email protected]>
Received: from mtiwgwc14.worldnet.att.net ([127.0.0.1])
by mtiwgwc14.worldnet.att.net
(InterMail vM.5.01.05.12 201-253-122-126-112-20020820) with ESMTP
id
<20030221073622.jwjy22738.mtiwgwc14.worldnet.att....@mtiwgwc14.worldnet.att.net>
for <[email protected]>;
Fri, 21 Feb 2003 07:36:22 +0000
Received: from theworld.com (pcls1.std.com[199.172.62.103])
by mtiwgwc14.worldnet.att.net (mtiwgwc14) with ESMTP
id <2003022107362101400kiicme>; Fri, 21 Feb 2003 07:36:21 +0000
Received: from europe.std.com (europe.std.com [199.172.62.20])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id CAA23959;
Fri, 21 Feb 2003 02:35:52 -0500
Received: (from daemon@localhost)
by europe.std.com (8.9.3/8.9.3) id CAA22383
for nebs-outgoing; Fri, 21 Feb 2003 02:32:08 -0500 (EST)
Received: from TheWorld.com (pcls4.std.com [199.172.62.106])
by europe.std.com (8.9.3/8.9.3) with ESMTP id CAA22078
for <[email protected]>; Fri, 21 Feb 2003 02:29:33 -0500 (EST)
Received: from smtp2.abac.com (smtp2.abac.com [216.55.128.11])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id CAA20095
for <[email protected]>; Fri, 21 Feb 2003 02:29:28 -0500
Received: from [216.55.130.181] (216-55-130-181.dialup.tnt01.san-diego.abac.net
[216.55.130.181])
by smtp2.abac.com (Postfix) with ESMTP
id AB1AF369BA4; Thu, 20 Feb 2003 23:29:25 -0800 (PST)
Mime-Version: 1.0
X-Sender: (Unverified)
Message-Id: <p05200f1cba7b82e81da1@[216.55.130.181]>
In-Reply-To: <[email protected]>
References: <[email protected]>
X-Priority: 2 (High)
List-Post: [email protected]
Date: Thu, 20 Feb 2003 23:29:21 -0800
To: Joe Finlayson <[email protected]>, Ed Hickey <[email protected]>
From: Don Robert House <[email protected]>
Subject: RE: Equipment dimensions for 23" Rack
Cc: [email protected], [email protected]
Content-Type: text/plain; charset="us-ascii" ; format="flowed"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]
X-Mozilla-Status: a011
X-Mozilla-Status2: 00000000
X-UIDL: <p05200f1cba7b82e81da1@[216.55.130.181]>
Joe and Ed,
I took careful measurements today. 23" is the distance between the
far ends of the mounting ears on the sides of the equipment. The
maximum width of the equipment itself is 21 1/4 inches. The center
of the mounting holes on one side to the center of the holes on the
other side is 22 1/4". The inside opening width is 21 1/2" and the
outside width measurement of the network rack is 26". The standard
heights for "23 inch" network equipment racks are 7 foot, 9 foot, and
11 foot 6 inches.
I hope this is somewhat helpful to you. I will continue to look for
appropriate documentation.
Don
--
Don R. House,
Technical Representative
From - Wed Feb 19 03:30:55 2003
Return-Path: <[email protected]>
Received: from mtiwgwc15.worldnet.att.net ([127.0.0.1])
by mtiwgwc15.worldnet.att.net
(InterMail vM.5.01.05.12 201-253-122-126-112-20020820) with ESMTP
id
<20030219071745.dree304.mtiwgwc15.worldnet.att....@mtiwgwc15.worldnet.att.net>
for <[email protected]>;
Wed, 19 Feb 2003 07:17:45 +0000
Received: from theworld.com (pcls4.std.com[199.172.62.106])
by mtiwgwc15.worldnet.att.net (mtiwgwc15) with ESMTP
id <2003021907174401500d18m1e>; Wed, 19 Feb 2003 07:17:44 +0000
Received: from europe.std.com (europe.std.com [199.172.62.20])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id CAA30761;
Wed, 19 Feb 2003 02:16:20 -0500
Received: (from daemon@localhost)
by europe.std.com (8.9.3/8.9.3) id CAA19622
for nebs-outgoing; Wed, 19 Feb 2003 02:13:25 -0500 (EST)
Received: from TheWorld.com (pcls1.std.com [199.172.62.103])
by europe.std.com (8.9.3/8.9.3) with ESMTP id CAA18932
for <[email protected]>; Wed, 19 Feb 2003 02:09:01 -0500 (EST)
Received: from smtp2.abac.com (smtp2.abac.com [216.55.128.11])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id CAA23535
for <[email protected]>; Wed, 19 Feb 2003 02:08:56 -0500
Received: from [216.55.130.239] (216-55-130-239.dialup.tnt01.san-diego.abac.net
[216.55.130.239])
by smtp2.abac.com (Postfix) with ESMTP
id 7AC41369331; Tue, 18 Feb 2003 23:08:53 -0800 (PST)
Mime-Version: 1.0
X-Sender: (Unverified)
Message-Id: <p05200f0cba78d99b1f90@[216.55.130.239]>
In-Reply-To: <[email protected]>
References: <[email protected]>
X-Priority: 2 (High)
List-Post: [email protected]
Date: Tue, 18 Feb 2003 23:08:48 -0800
To: Joe Finlayson <[email protected]>,
"'Don Robert House'" <[email protected]>,
Ed Hickey <[email protected]>
From: Don Robert House <[email protected]>
Subject: RE: Equipment dimensions for 23" Rack
Cc: [email protected]
Content-Type: text/plain; charset="us-ascii" ; format="flowed"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]
X-Mozilla-Status: a011
X-Mozilla-Status2: 00000000
X-UIDL: <p05200f0cba78d99b1f90@[216.55.130.239]>
Joe,
It is my belief that the 23" is the nominal distance for the mounting
hole spacing on the equipment "ears". The inside width of the
flanges being a minimum of 500mm and the outer width dimensions of
the flanges being 600 mm. The second set of requirements show the
inside and outside dimensions for a power lineup.
I have seven Zone 4 network relay racks at our museum from Newton,
AT&T and Hendry. They are all exactly the same with the same
measurements. These racks house a DDS STC Hub and End Office. The
equipment is designed to "just fit" into the racks. I will get out
my tape measure and send you what I find out. I will then try to
match the data with the proper specification. I am sorry I was not
more helpful the first time around.
Don
Curator - NADCOMM
North American Data Communications Museum
640 "C" Street
San Diego, CA 92101
(619) 235-8222
(619) 235-8220 FAX
At 11:24 AM -0500 2/18/2003, Joe Finlayson wrote:
>Don,
>
> I reviewed Section 3 previously and don't see where they address the
>19" and 23" racks, only the "desired" NEBS 2000 Framework Criteria for 600mm
>and 750mm racks. Am I missing something here?
>
> R3-15 [57] The width of the flange aperture (the width of the open
>space between the uprights) shall be 500 mm, +2 mm/-0 mm for the 600-mm wide
>frameworks, or 650 mm, +2 mm/-0 mm wide for 750-mm wide frameworks.
>
> 500mm = 19.7" and 650mm = 25.6".
>
> This is nowhere near the "equipment width" dimensions of 19" and 23"
>C.O. equipment.
>
>Thx,
>
>
>Joe
>
>-----Original Message-----
>From: Don Robert House [mailto:[email protected]]
>Sent: Monday, February 17, 2003 10:42 PM
>To: Joe Finlayson; Ed Hickey
>Cc: [email protected]
>Subject: Re: Equipment dimensions for 23" Rack
>
>
>Joe and Ed,
>I think section 3 of GR-63 (Geometric Requirements) is what you are
>looking for. Think metric.
>Don
>
>
>
>At 10:01 AM -0500 2/17/2003, Joe Finlayson wrote:
>>Would anyone be able to provide the maximum width dimensions for
>>C.O. equipment destined for a 23" rack? I perused through GR-63 and only
>>found rack dimensions. A reference to the corresponding Telcordia spec
>>would helpful as well.
>>
>>Thx,
>>
>>Joe
>>
>>*********************************
>>Joe Finlayson
>>Manager, Compliance Engineering
>>Telica, Inc.
>>734 Forest Street, Bldg. G, Suite 100
>>Marlboro, MA 01752
>>Tel: (508) 804-8212
>>Fax: (508) 480-0922
> >Email: [email protected]
> >Web: www.telica.com
>
>
>--
>Don R. House,
>Technical Representative
--
Don R. House,
Technical Representative
From - Wed Feb 19 03:28:07 2003
Return-Path: <[email protected]>
Received: from mtiwgwc16.worldnet.att.net ([127.0.0.1])
by mtiwgwc16.worldnet.att.net
(InterMail vM.5.01.05.12 201-253-122-126-112-20020820) with ESMTP
id
<20030218163603.hyqt2030.mtiwgwc16.worldnet.att....@mtiwgwc16.worldnet.att.net>
for <[email protected]>;
Tue, 18 Feb 2003 16:36:03 +0000
Received: from theworld.com (pcls2.std.com[199.172.62.104])
by mtiwgwc16.worldnet.att.net (mtiwgwc16) with ESMTP
id <2003021816355401600h1sj5e>; Tue, 18 Feb 2003 16:35:54 +0000
Received: from europe.std.com (europe.std.com [199.172.62.20])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id LAA27714;
Tue, 18 Feb 2003 11:35:16 -0500
Received: (from daemon@localhost)
by europe.std.com (8.9.3/8.9.3) id LAA16696
for nebs-outgoing; Tue, 18 Feb 2003 11:33:31 -0500 (EST)
Received: from TheWorld.com (pcls2.std.com [199.172.62.104])
by europe.std.com (8.9.3/8.9.3) with ESMTP id LAA15640
for <[email protected]>; Tue, 18 Feb 2003 11:28:37 -0500 (EST)
Received: from wench.telica.com ([4.19.224.196])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id LAA16768
for <[email protected]>; Tue, 18 Feb 2003 11:28:36 -0500
Received: by wench.telica.com with Internet Mail Service (5.5.2653.19)
id <ZPPPG1HQ>; Tue, 18 Feb 2003 11:24:24 -0500
Message-ID: <[email protected]>
From: Joe Finlayson <[email protected]>
To: "'Don Robert House'" <[email protected]>,
Ed Hickey
<[email protected]>
Cc: [email protected]
Subject: RE: Equipment dimensions for 23" Rack
List-Post: [email protected]
Date: Tue, 18 Feb 2003 11:24:20 -0500
MIME-Version: 1.0
X-Mailer: Internet Mail Service (5.5.2653.19)
Content-Type: text/plain;
charset="iso-8859-1"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]
X-Mozilla-Status: 8011
X-Mozilla-Status2: 00000000
X-UIDL: <[email protected]>
Don,
I reviewed Section 3 previously and don't see where they address the
19" and 23" racks, only the "desired" NEBS 2000 Framework Criteria for 600mm
and 750mm racks. Am I missing something here?
R3-15 [57] The width of the flange aperture (the width of the open
space between the uprights) shall be 500 mm, +2 mm/-0 mm for the 600-mm wide
frameworks, or 650 mm, +2 mm/-0 mm wide for 750-mm wide frameworks.
500mm = 19.7" and 650mm = 25.6".
This is nowhere near the "equipment width" dimensions of 19" and 23"
C.O. equipment.
Thx,
Joe
-----Original Message-----
From: Don Robert House [mailto:[email protected]]
Sent: Monday, February 17, 2003 10:42 PM
To: Joe Finlayson; Ed Hickey
Cc: [email protected]
Subject: Re: Equipment dimensions for 23" Rack
Joe and Ed,
I think section 3 of GR-63 (Geometric Requirements) is what you are
looking for. Think metric.
Don
At 10:01 AM -0500 2/17/2003, Joe Finlayson wrote:
>Would anyone be able to provide the maximum width dimensions for
>C.O. equipment destined for a 23" rack? I perused through GR-63 and only
>found rack dimensions. A reference to the corresponding Telcordia spec
>would helpful as well.
>
>Thx,
>
>Joe
>
>*********************************
>Joe Finlayson
>Manager, Compliance Engineering
>Telica, Inc.
>734 Forest Street, Bldg. G, Suite 100
>Marlboro, MA 01752
>Tel: (508) 804-8212
>Fax: (508) 480-0922
>Email: [email protected]
>Web: www.telica.com
--
Don R. House,
Technical Representative
From - Wed Feb 19 03:27:01 2003
Return-Path: <[email protected]>
Received: from mtiwmhc14.worldnet.att.net ([127.0.0.1])
by mtiwmhc14.worldnet.att.net
(InterMail vM.5.01.05.12 201-253-122-126-112-20020820) with ESMTP
id
<20030218035133.vexh9415.mtiwmhc14.worldnet.att....@mtiwmhc14.worldnet.att.net>
for <[email protected]>;
Tue, 18 Feb 2003 03:51:33 +0000
Received: from theworld.com (pcls2.std.com[199.172.62.104])
by mtiwmhc14.worldnet.att.net (mtiwmhc14) with ESMTP
id <2003021803513211400b4snqe>; Tue, 18 Feb 2003 03:51:32 +0000
Received: from europe.std.com (europe.std.com [199.172.62.20])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id WAA29922;
Mon, 17 Feb 2003 22:50:20 -0500
Received: (from daemon@localhost)
by europe.std.com (8.9.3/8.9.3) id WAA10119
for nebs-outgoing; Mon, 17 Feb 2003 22:47:25 -0500 (EST)
Received: from TheWorld.com (pcls4.std.com [199.172.62.106])
by europe.std.com (8.9.3/8.9.3) with ESMTP id WAA09135
for <[email protected]>; Mon, 17 Feb 2003 22:43:09 -0500 (EST)
Received: from smtp2.abac.com (smtp2.abac.com [216.55.128.11])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id WAA21706
for <[email protected]>; Mon, 17 Feb 2003 22:43:03 -0500
Received: from [216.55.130.133] (216-55-130-133.dialup.tnt01.san-diego.abac.net
[216.55.130.133])
by smtp2.abac.com (Postfix) with ESMTP
id 7DA27369664; Mon, 17 Feb 2003 19:43:01 -0800 (PST)
Mime-Version: 1.0
X-Sender: (Unverified)
Message-Id: <p05200f01ba775a9e4981@[64.24.59.48]>
In-Reply-To: <[email protected]>
References: <[email protected]>
List-Post: [email protected]
Date: Mon, 17 Feb 2003 19:41:30 -0800
To: Joe Finlayson <[email protected]>, Ed Hickey <[email protected]>
From: Don Robert House <[email protected]>
Subject: Re: Equipment dimensions for 23" Rack
Cc: [email protected]
Content-Type: text/plain; charset="us-ascii" ; format="flowed"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]
X-Mozilla-Status: 8011
X-Mozilla-Status2: 00000000
X-UIDL: <p05200f01ba775a9e4981@[64.24.59.48]>
Joe and Ed,
I think section 3 of GR-63 (Geometric Requirements) is what you are
looking for. Think metric.
Don
At 10:01 AM -0500 2/17/2003, Joe Finlayson wrote:
>Would anyone be able to provide the maximum width dimensions for
>C.O. equipment destined for a 23" rack? I perused through GR-63 and only
>found rack dimensions. A reference to the corresponding Telcordia spec
>would helpful as well.
>
>Thx,
>
>Joe
>
>*********************************
>Joe Finlayson
>Manager, Compliance Engineering
>Telica, Inc.
>734 Forest Street, Bldg. G, Suite 100
>Marlboro, MA 01752
>Tel: (508) 804-8212
>Fax: (508) 480-0922
>Email: [email protected]
>Web: www.telica.com
--
Don R. House,
Technical Representative
From - Wed Feb 19 03:26:02 2003
Return-Path: <[email protected]>
Received: from mtiwgwc12.worldnet.att.net ([127.0.0.1])
by mtiwgwc12.worldnet.att.net
(InterMail vM.5.01.05.12 201-253-122-126-112-20020820) with ESMTP
id
<20030217151608.naui9890.mtiwgwc12.worldnet.att....@mtiwgwc12.worldnet.att.net>
for <[email protected]>;
Mon, 17 Feb 2003 15:16:08 +0000
Received: from theworld.com (pcls3.std.com[199.172.62.105])
by mtiwgwc12.worldnet.att.net (mtiwgwc12) with ESMTP
id <20030217151608012004eltve>; Mon, 17 Feb 2003 15:16:08 +0000
Received: from europe.std.com (europe.std.com [199.172.62.20])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id KAA07127;
Mon, 17 Feb 2003 10:14:59 -0500
Received: (from daemon@localhost)
by europe.std.com (8.9.3/8.9.3) id KAA27598
for nebs-outgoing; Mon, 17 Feb 2003 10:12:10 -0500 (EST)
Received: from TheWorld.com (pcls1.std.com [199.172.62.103])
by europe.std.com (8.9.3/8.9.3) with ESMTP id KAA26732
for <[email protected]>; Mon, 17 Feb 2003 10:05:26 -0500 (EST)
Received: from wench.telica.com ([4.19.224.196])
by TheWorld.com (8.9.3/8.9.3) with ESMTP id KAA09650
for <[email protected]>; Mon, 17 Feb 2003 10:05:25 -0500
Received: by wench.telica.com with Internet Mail Service (5.5.2653.19)
id <ZPPPGBL0>; Mon, 17 Feb 2003 10:01:20 -0500
Message-ID: <[email protected]>
From: Joe Finlayson <[email protected]>
To: "'NEBS Newsgroup'" <[email protected]>
Subject: Equipment width dimensions for 23" Rack
List-Post: [email protected]
Date: Mon, 17 Feb 2003 10:01:17 -0500
MIME-Version: 1.0
X-Mailer: Internet Mail Service (5.5.2653.19)
Content-Type: text/plain;
charset="iso-8859-1"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]
X-Mozilla-Status: 8001
X-Mozilla-Status2: 00000000
X-UIDL: <[email protected]>
Would anyone be able to provide the maximum width dimensions for
C.O. equipment destined for a 23" rack? I perused through GR-63 and only
found rack dimensions. A reference to the corresponding Telcordia spec
would helpful as well.
Thx,
Joe
*********************************
<<...OLE_Obj...>>
Joe Finlayson
Manager, Compliance Engineering
Telica, Inc.
734 Forest Street, Bldg. G, Suite 100
Marlboro, MA 01752
Tel: (508) 804-8212
Fax: (508) 480-0922
Email: [email protected]
Web: www.telica.com