Thank you for the info. I'll update one of the Linux machines and see if it 
improves. 


On Thu, Feb 16, 2023, at 1:01 AM, Jim Klimov wrote:
> That is a message from NUT 2.7.4 and older, emitted as snmp-ups driver tries 
> to guess the vendor that matches a device (by extended sub-trees) or see if 
> it has to fall back to IETF data tree, if `mibs=...` were not specified.
> 
> Current versions should not post that as a sort-of-drastic situation.
> 
> Jim
> 
> 
> On Thu, Feb 16, 2023, 02:16 Brad Tarver via Nut-upsdev 
> <[email protected]> wrote:
>> Hello all,
>> 
>> Thank you in advance for a great FOSS project. Also, thank you for reading 
>> my question.
>> 
>> I have a CyberPower OR1500LCDRTXL2U with an RMCARD205. There are a handful 
>> of devices plugged into the UPS.
>> 
>> I received a message today saying to send upsc output to NUT developers 
>> after this message: "No matching MIB found for sysOID 
>> '.1.3.6.1.4.1.3808.1.1.1'"
>> 
>> root@delta:/etc/nut# systemctl status nut-driver.service 
>> Feb 15 17:47:52 delta upsdrvctl[519]: No matching MIB found for sysOID 
>> '.1.3.6.1.4.1.3808.1.1.1'!
>> Feb 15 17:47:52 delta upsdrvctl[519]: Please report it to NUT developers, 
>> with an 'upsc' output for your device.
>> Feb 15 17:47:52 delta upsdrvctl[519]: Going back to the classic MIB 
>> detection method.
>> Feb 15 17:47:52 delta upsdrvctl[519]: Detected OR1500LCDRTXL2U on host 
>> 172.16.20.30 (mib: cyberpower 0.1)
>> Feb 15 17:47:52 delta upsdrvctl[519]: [network-ups] unhandled ASN 0x5 
>> received from .1.3.6.1.4.1.3808.1.1.1.2.2.2.0
>> Feb 15 17:47:52 delta snmp-ups[576]: Startup successful
>> 
>> UPS.CONF
>> ========
>> maxretry = 3
>> [network-ups]
>> driver = snmp-ups
>> port = 172.16.20.30
>> snmp_version = v2c
>> community = cybernut
>> pollfreq = 15
>> desc = "CyperPower OR1500LCDRTXL2U"
>> 
>> 
>> UPSC OUTPUT
>> ========
>> root@delta:/etc/nut# upsc network-ups@localhost
>> Init SSL without certificate database
>> battery.runtime: 262800.00
>> battery.runtime.elapsed: 0.00
>> device.mfr: CYBERPOWER
>> device.model: OR1500LCDRTXL2U
>> device.serial: REDACTED SERIAL NUMBER
>> device.type: ups
>> driver.name: snmp-ups
>> driver.parameter.pollfreq: 15
>> driver.parameter.pollinterval: 2
>> driver.parameter.port: 172.16.20.30
>> driver.parameter.snmp_version: v2c
>> driver.parameter.synchronous: no
>> driver.version: 2.7.4
>> driver.version.data: cyberpower MIB 0.1
>> driver.version.internal: 0.97
>> ups.firmware: BF02018B7V11
>> ups.mfr: CYBERPOWER
>> ups.model: OR1500LCDRTXL2U
>> ups.serial: REDACTED SERIAL NUMBER
>> ups.status: OL
>> 
>> SNMPWALK
>> ========
>> root@delta:/etc/nut# snmpwalk -c cybernut -v 2c 172.16.20.30
>>  
_______________________________________________
Nut-upsdev mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to