Hi!
I have CyberPower CyberShield CSN27U12V UPS. This device don't have
usual for UPS interface, just open collector pins. I connected these
pins to GPIO interface on Orange Pi Zero and wrote NUT driver for this
case. Any interest from NUT community to add this driver to regular
build tree?
See driver code in attachment. Code is fully functional, needs cleanup
to match coding guidelines and needs more tests for rules processing
part. Driver reads GPIO line statuses and transforms them to NUT
statuses using short rules description parameter in the form of status
strings and logical operations on line values.
Modris
/* adelsystem_cbi.c - driver for ADELSYSTEM CB/CBI DC-UPS
*
* Copyright (C)
* 2022 Dimitris Economou <[email protected]>
*
* This program is free software; you can redistribute it and/or modify
* it under the terms of the GNU General Public License as published by
* the Free Software Foundation; either version 2 of the License, or
* (at your option) any later version.
*
* This program is distributed in the hope that it will be useful,
* but WITHOUT ANY WARRANTY; without even the implied warranty of
* MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the
* GNU General Public License for more details.
*
*
* You should have received a copy of the GNU General Public License
* along with this program; if not, write to the Free Software
* Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA 02111-1307 USA
*
*/
/*
* code indentation with tabstop=4
*/
#include "main.h"
#include "adelsystem_cbi.h"
#include <modbus.h>
#include <timehead.h>
#define DRIVER_NAME "NUT ADELSYSTEM DC-UPS CB/CBI driver"
#define DRIVER_VERSION "0.01"
/* variables */
static modbus_t *mbctx = NULL; /* modbus memory context */
static devstate_t *dstate = NULL; /* device state context */
static int errcnt = 0; /* modbus access error counter */
static char *device_mfr = DEVICE_MFR; /* device manufacturer */
static char *device_model = DEVICE_MODEL; /* device model */
static char *device_type = DEVICE_TYPE_STRING; /* device type (e.g. UPS, PDU...) */
static int ser_baud_rate = BAUD_RATE; /* serial port baud rate */
static char ser_parity = PARITY; /* serial port parity */
static int ser_data_bit = DATA_BIT; /* serial port data bit */
static int ser_stop_bit = STOP_BIT; /* serial port stop bit */
static int dev_slave_id = MODBUS_SLAVE_ID; /* set device ID to default value */
static uint32_t mod_resp_to_s = MODRESP_TIMEOUT_s; /* set the modbus response time out (s) */
static uint32_t mod_resp_to_us = MODRESP_TIMEOUT_us; /* set the modbus response time out (us) */
static uint32_t mod_byte_to_s = MODBYTE_TIMEOUT_s; /* set the modbus byte time out (us) */
static uint32_t mod_byte_to_us = MODBYTE_TIMEOUT_us; /* set the modbus byte time out (us) */
/* initialize alarm structs */
void alrminit(void);
/* initialize register start address and hex address from register number */
void reginit(void);
/* read registers' memory region */
int read_all_regs(modbus_t *mb, uint16_t *data);
/* get config vars set by -x or defined in ups.conf driver section */
void get_config_vars(void);
/* get device state */
int get_dev_state(devreg_t regindx, devstate_t **dvstat);
/* create a new modbus context based on connection type (serial or TCP) */
modbus_t *modbus_new(const char *port);
/* reconnect upon communication error */
void modbus_reconnect(void);
/* modbus register read function */
int register_read(modbus_t *mb, int addr, regtype_t type, void *data);
/* modbus register write function */
int register_write(modbus_t *mb, int addr, regtype_t type, void *data);
/* instant command triggered by upsd */
int upscmd(const char *cmd, const char *arg);
/* count the time elapsed since start */
long time_elapsed(struct timeval *start);
/* driver description structure */
upsdrv_info_t upsdrv_info = {
DRIVER_NAME,
DRIVER_VERSION,
"Dimitris Economou <[email protected]>\n",
DRV_BETA,
{NULL}
};
/*
* driver functions
*/
/* read configuration variables from ups.conf and connect to ups device */
void upsdrv_initups(void)
{
int rval;
upsdebugx(2, "upsdrv_initups");
dstate = (devstate_t *)xmalloc(sizeof(devstate_t));
alrminit();
reginit();
get_config_vars();
/* open communication port */
mbctx = modbus_new(device_path);
if (mbctx == NULL) {
fatalx(EXIT_FAILURE, "modbus_new_rtu: Unable to open communication port context");
}
/* set slave ID */
rval = modbus_set_slave(mbctx, dev_slave_id);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_slave: Invalid modbus slave ID %d", dev_slave_id);
}
/* connect to modbus device */
if (modbus_connect(mbctx) == -1) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_connect: unable to connect: error(%s)", modbus_strerror(errno));
}
/* set modbus response timeout */
#if (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32) || (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32_cast_timeval_fields)
rval = modbus_set_response_timeout(mbctx, mod_resp_to_s, mod_resp_to_us);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_response_timeout: error(%s)", modbus_strerror(errno));
}
#elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval_numeric_fields)
{
/* Older libmodbus API (with timeval), and we have
* checked at configure time that we can put uint32_t
* into its fields. They are probably "long" on many
* systems as respectively time_t and suseconds_t -
* but that is not guaranteed; for more details see
* https://pubs.opengroup.org/onlinepubs/9699919799/basedefs/sys_time.h.html
*/
struct timeval to;
memset(&to, 0, sizeof(struct timeval));
to.tv_sec = mod_resp_to_s;
to.tv_usec = mod_resp_to_us;
/* void */ modbus_set_response_timeout(mbctx, &to);
}
/* #elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval) // some un-castable type in fields */
#else
# error "Can not use libmodbus API for timeouts"
#endif /* NUT_MODBUS_TIMEOUT_ARG_* */
/* set modbus byte time out */
#if (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32) || (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32_cast_timeval_fields)
rval = modbus_set_byte_timeout(mbctx, mod_byte_to_s, mod_byte_to_us);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_byte_timeout: error(%s)", modbus_strerror(errno));
}
#elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval_numeric_fields)
{ /* see comments above */
struct timeval to;
memset(&to, 0, sizeof(struct timeval));
to.tv_sec = mod_byte_to_s;
to.tv_usec = mod_byte_to_us;
/* void */ modbus_set_byte_timeout(mbctx, &to);
}
/* #elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval) // some un-castable type in fields */
#endif /* NUT_MODBUS_TIMEOUT_ARG_* */
}
/* initialize ups driver information */
void upsdrv_initinfo(void)
{
devstate_t *ds = dstate; /* device state context */
upsdebugx(2, "upsdrv_initinfo");
/* set device information */
dstate_setinfo("device.mfr", "%s", device_mfr);
dstate_setinfo("device.model", "%s", device_model);
dstate_setinfo("device.type", "%s", device_type);
/* read ups model */
get_dev_state(PRDN, &ds);
dstate_setinfo("ups.model", "%s", ds->product.name);
upslogx(LOG_INFO, "ups.model = %s", ds->product.name);
/* register instant commands */
dstate_addcmd("load.off");
/* set callback for instant commands */
upsh.instcmd = upscmd;
}
/* update UPS signal state */
void upsdrv_updateinfo(void)
{
int rval; /* return value */
int i; /* local index */
devstate_t *ds = dstate; /* device state */
upsdebugx(2, "upsdrv_updateinfo");
errcnt = 0; /* initialize error counter to zero */
status_init(); /* initialize ups.status update */
alarm_init(); /* initialize ups.alarm update */
#if READALL_REGS == 1
rval = read_all_regs(mbctx, regs_data);
if (rval == -1) {
errcnt++;
} else {
#endif
/*
* update UPS status regarding MAINS and SHUTDOWN request
* - OL: On line (mains is present)
* - OB: On battery (mains is not present)
*/
rval = get_dev_state(MAIN, &ds);
if (rval == -1) {
errcnt++;
} else {
if (ds->alrm->alrm[MAINS_AVAIL_I].actv) {
status_set("OB");
alarm_set(mains->alrm[MAINS_AVAIL_I].descr);
upslogx(LOG_INFO, "ups.status = OB");
} else {
status_set("OL");
upslogx(LOG_INFO, "ups.status = OL");
}
if (ds->alrm->alrm[SHUTD_REQST_I].actv) {
status_set("FSD");
alarm_set(mains->alrm[SHUTD_REQST_I].descr);
upslogx(LOG_INFO, "ups.status = FSD");
}
}
/*
* update UPS status regarding battery voltage
*/
rval = get_dev_state(BVAL, &ds);
if (rval == -1) {
errcnt++;
} else {
if (ds->alrm->alrm[BVAL_LOALRM_I].actv) {
status_set("LB");
alarm_set(bval->alrm[BVAL_LOALRM_I].descr);
upslogx(LOG_INFO, "ups.status = LB");
}
if (ds->alrm->alrm[BVAL_HIALRM_I].actv) {
status_set("HB");
alarm_set(bval->alrm[BVAL_HIALRM_I].descr);
upslogx(LOG_INFO, "ups.status = HB");
}
if (ds->alrm->alrm[BVAL_BSTSFL_I].actv) {
alarm_set(bval->alrm[BVAL_BSTSFL_I].descr);
upslogx(LOG_INFO, "battery start with battery flat");
}
}
/* get "battery.voltage" */
rval = get_dev_state(BATV, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("battery.voltage", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "battery.voltage = %s", ds->reg.strval);
}
/*
* update UPS status regarding battery charger status
*/
/* get "battery.charger.status" */
rval = get_dev_state(CHRG, &ds);
if (rval == -1) {
errcnt++;
} else {
if (ds->charge.state == CHRG_BULK || ds->charge.state == CHRG_ABSR) {
status_set("CHRG");
upslogx(LOG_INFO, "ups.status = CHRG");
}
dstate_setinfo("battery.charger.status", "%s", ds->charge.info);
upslogx(LOG_DEBUG, "battery.charger.status = %s", ds->charge.info);
}
rval = get_dev_state(PMNG, &ds);
if (rval == -1) {
errcnt++;
} else {
if (ds->power.state == PMNG_BCKUP) {
status_set("DISCHRG");
dstate_setinfo("battery.charger.status", "discharging");
upslogx(LOG_INFO, "ups.status = DISCHRG");
}
if (ds->power.state == PMNG_BOOST) {
status_set("BOOST");
upslogx(LOG_INFO, "ups.status = BOOST");
}
}
/*
* update UPS battery state of charge
*/
rval = get_dev_state(BSOC, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("battery.charge", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "battery.charge = %s", ds->reg.strval);
}
/*
* update UPS AC input state
*/
rval = get_dev_state(VACA, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s is active", ds->alrm->alrm[i].descr);
}
}
}
rval = get_dev_state(VAC, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("input.voltage", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "input.voltage = %s", ds->reg.strval);
}
/*
* update UPS onboard temperature state
*/
rval = get_dev_state(OBTA, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s is active", ds->alrm->alrm[i].descr);
}
}
}
rval = get_dev_state(OTMP, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("ups.temperature", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "ups.temperature = %s", ds->reg.strval);
}
/*
* update UPS battery temperature state
*/
rval = get_dev_state(BSTA, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s alarm is active", ds->alrm->alrm[i].descr);
}
}
}
rval = get_dev_state(BTMP, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("battery.temperature", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "battery.temperature = %s", ds->reg.strval);
}
rval = get_dev_state(TBUF, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("battery.runtime", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "battery.runtime = %s", ds->reg.strval);
}
/*
* update UPS device failure state
*/
rval = get_dev_state(DEVF, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s alarm is active", ds->alrm->alrm[i].descr);
}
}
}
/*
* update UPS SoH and SoC states
*/
rval = get_dev_state(SCSH, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s alarm is active", ds->alrm->alrm[i].descr);
}
}
}
/*
* update UPS battery state
*/
rval = get_dev_state(BSTA, &ds);
if (rval == -1) {
errcnt++;
} else {
for (i = 0; i < ds->alrm->alrm_c; i++) {
if (ds->alrm->alrm[i].actv) {
alarm_set(ds->alrm->alrm[i].descr);
upsdebugx(3, "%s alarm is active", ds->alrm->alrm[i].descr);
}
}
}
/*
* update UPS load status
*/
rval = get_dev_state(LVDC, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("output.voltage", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "output.voltage = %s", ds->reg.strval);
}
rval = get_dev_state(LCUR, &ds);
if (rval == -1) {
errcnt++;
} else {
dstate_setinfo("output.current", "%s", ds->reg.strval);
upslogx(LOG_DEBUG, "output.current = %s", ds->reg.strval);
}
#if READALL_REGS == 1
}
#endif
/* check for communication errors */
if (errcnt == 0) {
alarm_commit();
status_commit();
dstate_dataok();
} else {
upsdebugx(2, "Communication errors: %d", errcnt);
dstate_datastale();
}
}
/* shutdown UPS */
void upsdrv_shutdown(void)
{
int rval;
int cnt = FSD_REPEAT_CNT; /* shutdown repeat counter */
struct timeval start;
long etime;
/* retry sending shutdown command on error */
while ((rval = upscmd("load.off", NULL)) != STAT_INSTCMD_HANDLED && cnt > 0) {
rval = gettimeofday(&start, NULL);
if (rval < 0) {
upslogx(LOG_ERR, "upscmd: gettimeofday: %s", strerror(errno));
}
/* wait for an increasing time interval before sending shutdown command */
while ((etime = time_elapsed(&start)) < ( FSD_REPEAT_INTRV / cnt));
upsdebugx(2, "ERROR: load.off failed, wait for %lims, retries left: %d\n", etime, cnt - 1);
cnt--;
}
switch (rval) {
case STAT_INSTCMD_FAILED:
case STAT_INSTCMD_INVALID:
fatalx(EXIT_FAILURE, "shutdown failed");
case STAT_INSTCMD_UNKNOWN:
fatalx(EXIT_FAILURE, "shutdown not supported");
default:
break;
}
upslogx(LOG_INFO, "shutdown command executed");
}
/* print driver usage info */
void upsdrv_help(void)
{
}
/* list flags and values that you want to receive via -x */
void upsdrv_makevartable(void)
{
addvar(VAR_VALUE, "ser_baud_rate", "serial port baud rate");
addvar(VAR_VALUE, "ser_parity", "serial port parity");
addvar(VAR_VALUE, "ser_data_bit", "serial port data bit");
addvar(VAR_VALUE, "ser_stop_bit", "serial port stop bit");
addvar(VAR_VALUE, "dev_slave_id", "device modbus slave ID");
addvar(VAR_VALUE, "mod_resp_to_s", "modbus response timeout (s)");
addvar(VAR_VALUE, "mod_resp_to_us", "modbus response timeout (us)");
addvar(VAR_VALUE, "mod_byte_to_s", "modbus byte timeout (s)");
addvar(VAR_VALUE, "mod_byte_to_us", "modbus byte timeout (us)");
}
/* close modbus connection and free modbus context allocated memory */
void upsdrv_cleanup(void)
{
if (mbctx != NULL) {
modbus_close(mbctx);
modbus_free(mbctx);
}
if (dstate != NULL) {
free(dstate);
}
}
/*
* driver support functions
*/
/* initialize alarm structs */
void alrminit(void)
{
mains = alloc_alrm_ar(mains_c, sizeof(mains_ar));
alrm_ar_init(mains, mains_ar, mains_c);
vaca = alloc_alrm_ar(vaca_c, sizeof(vaca_ar));
alrm_ar_init(vaca, vaca_ar, vaca_c);
devf = alloc_alrm_ar(devf_c, sizeof(devf_ar));
alrm_ar_init(devf, devf_ar, devf_c);
btsf = alloc_alrm_ar(btsf_c, sizeof(btsf_ar));
alrm_ar_init(btsf, btsf_ar, btsf_c);
bval = alloc_alrm_ar(bval_c, sizeof(bval_ar));
alrm_ar_init(bval, bval_ar, bval_c);
shsc = alloc_alrm_ar(shsc_c, sizeof(shsc_ar));
alrm_ar_init(shsc, shsc_ar, shsc_c);
bsta = alloc_alrm_ar(bsta_c, sizeof(bsta_ar));
alrm_ar_init(bsta, bsta_ar, bsta_c);
obta = alloc_alrm_ar(obta_c, sizeof(obta_ar));
alrm_ar_init(obta, obta_ar, obta_c);
}
/* initialize register start address and hex address from register number */
void reginit(void)
{
int i; /* local index */
for (i = 0; i < MODBUS_NUMOF_REGS; i++) {
int rnum = regs[i].num;
switch (regs[i].type) {
case COIL:
regs[i].saddr = rnum - 1;
regs[i].xaddr = 0x0 + regs[i].num - 1;
break;
case INPUT_B:
rnum -= 10000;
regs[i].saddr = rnum - 1;
regs[i].xaddr = 0x10000 + rnum - 1;
break;
case INPUT_R:
rnum -= 30000;
regs[i].saddr = rnum - 1;
regs[i].xaddr = 0x30000 + rnum - 1;
break;
case HOLDING:
rnum -= 40000;
regs[i].saddr = rnum - 1;
regs[i].xaddr = 0x40000 + rnum - 1;
break;
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic push
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT
# pragma GCC diagnostic ignored "-Wcovered-switch-default"
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE
# pragma GCC diagnostic ignored "-Wunreachable-code"
#endif
/* Older CLANG (e.g. clang-3.4) seems to not support the GCC pragmas above */
#ifdef __clang__
# pragma clang diagnostic push
# pragma clang diagnostic ignored "-Wunreachable-code"
# pragma clang diagnostic ignored "-Wcovered-switch-default"
#endif
/* All enum cases defined as of the time of coding
* have been covered above. Handle later definitions,
* memory corruptions and buggy inputs below...
*/
default:
upslogx(LOG_ERR,
"Invalid register type %d for register %d",
regs[i].type,
regs[i].num
);
upsdebugx(3,
"Invalid register type %d for register %d",
regs[i].type,
regs[i].num
);
#ifdef __clang__
# pragma clang diagnostic pop
#endif
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic pop
#endif
}
upsdebugx(3,
"reginit: num:%d, type: %d saddr: %d, xaddr: 0x%x",
regs[i].num,
regs[i].type,
regs[i].saddr,
regs[i].xaddr
);
}
}
/* read registers' memory region */
int read_all_regs(modbus_t *mb, uint16_t *data)
{
int rval;
/* read all HOLDING registers */
rval = modbus_read_registers(mb, regs[H_REG_STARTIDX].xaddr, MAX_H_REGS, data);
if (rval == -1) {
upslogx(LOG_ERR,
"ERROR:(%s) modbus_read: addr:0x%x, length:%8d, path:%s\n",
modbus_strerror(errno),
regs[H_REG_STARTIDX].xaddr,
MAX_H_REGS,
device_path
);
/* on BROKEN PIPE, INVALID CRC and INVALID DATA error try to reconnect */
if (errno == EPIPE || errno == EMBBADDATA || errno == EMBBADCRC) {
upsdebugx(1, "register_read: error(%s)", modbus_strerror(errno));
modbus_reconnect();
}
}
/* no COIL, INPUT_B or INPUT_R register regions to read */
return rval;
}
/* Read a modbus register */
int register_read(modbus_t *mb, int addr, regtype_t type, void *data)
{
int rval = -1;
/* register bit masks */
uint16_t mask8 = 0x00FF;
uint16_t mask16 = 0xFFFF;
switch (type) {
case COIL:
rval = modbus_read_bits(mb, addr, 1, (uint8_t *)data);
*(uint16_t *)data = *(uint16_t *)data & mask8;
break;
case INPUT_B:
rval = modbus_read_input_bits(mb, addr, 1, (uint8_t *)data);
*(uint16_t *)data = *(uint16_t *)data & mask8;
break;
case INPUT_R:
rval = modbus_read_input_registers(mb, addr, 1, (uint16_t *)data);
*(uint16_t *)data = *(uint16_t *)data & mask16;
break;
case HOLDING:
rval = modbus_read_registers(mb, addr, 1, (uint16_t *)data);
*(uint16_t *)data = *(uint16_t *)data & mask16;
break;
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic push
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT
# pragma GCC diagnostic ignored "-Wcovered-switch-default"
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE
# pragma GCC diagnostic ignored "-Wunreachable-code"
#endif
/* Older CLANG (e.g. clang-3.4) seems to not support the GCC pragmas above */
#ifdef __clang__
# pragma clang diagnostic push
# pragma clang diagnostic ignored "-Wunreachable-code"
# pragma clang diagnostic ignored "-Wcovered-switch-default"
#endif
/* All enum cases defined as of the time of coding
* have been covered above. Handle later definitions,
* memory corruptions and buggy inputs below...
*/
default:
upsdebugx(2,"ERROR: register_read: invalid register type %d\n", type);
break;
#ifdef __clang__
# pragma clang diagnostic pop
#endif
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic pop
#endif
}
if (rval == -1) {
upslogx(LOG_ERR,
"ERROR:(%s) modbus_read: addr:0x%x, type:%8s, path:%s\n",
modbus_strerror(errno),
addr,
(type == COIL) ? "COIL" :
(type == INPUT_B) ? "INPUT_B" :
(type == INPUT_R) ? "INPUT_R" : "HOLDING",
device_path
);
/* on BROKEN PIPE, INVALID CRC and INVALID DATA error try to reconnect */
if (errno == EPIPE || errno == EMBBADDATA || errno == EMBBADCRC) {
upsdebugx(1, "register_read: error(%s)", modbus_strerror(errno));
modbus_reconnect();
}
}
upsdebugx(3, "register addr: 0x%x, register type: %d read: %u",addr, type, *(unsigned int *)data);
return rval;
}
/* write a modbus register */
int register_write(modbus_t *mb, int addr, regtype_t type, void *data)
{
int rval = -1;
/* register bit masks */
uint16_t mask8 = 0x00FF;
uint16_t mask16 = 0xFFFF;
switch (type) {
case COIL:
*(uint16_t *)data = *(uint16_t *)data & mask8;
rval = modbus_write_bit(mb, addr, *(uint8_t *)data);
break;
case HOLDING:
*(uint16_t *)data = *(uint16_t *)data & mask16;
rval = modbus_write_register(mb, addr, *(uint16_t *)data);
break;
case INPUT_B:
case INPUT_R:
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT)
# pragma GCC diagnostic push
# pragma GCC diagnostic ignored "-Wcovered-switch-default"
#endif
/* All enum cases defined as of the time of coding
* have been covered above. Handle later definitions,
* memory corruptions and buggy inputs below...
*/
default:
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT)
# pragma GCC diagnostic pop
#endif
upsdebugx(2,"ERROR: register_write: invalid register type %d\n", type);
break;
}
if (rval == -1) {
upslogx(LOG_ERR,
"ERROR:(%s) modbus_write: addr:0x%x, type:%8s, path:%s\n",
modbus_strerror(errno),
addr,
(type == COIL) ? "COIL" :
(type == INPUT_B) ? "INPUT_B" :
(type == INPUT_R) ? "INPUT_R" : "HOLDING",
device_path
);
/* on BROKEN PIPE error try to reconnect */
if (errno == EPIPE) {
upsdebugx(1, "register_write: error(%s)", modbus_strerror(errno));
modbus_reconnect();
}
}
upsdebugx(3, "register addr: 0x%x, register type: %d read: %u",addr, type, *(unsigned int *)data);
return rval;
}
/* returns the time elapsed since start in milliseconds */
long time_elapsed(struct timeval *start)
{
long rval;
struct timeval end;
rval = gettimeofday(&end, NULL);
if (rval < 0) {
upslogx(LOG_ERR, "time_elapsed: %s", strerror(errno));
}
if (start->tv_usec < end.tv_usec) {
suseconds_t nsec = (end.tv_usec - start->tv_usec) / 1000000 + 1;
end.tv_usec -= 1000000 * nsec;
end.tv_sec += nsec;
}
if (start->tv_usec - end.tv_usec > 1000000) {
suseconds_t nsec = (start->tv_usec - end.tv_usec) / 1000000;
end.tv_usec += 1000000 * nsec;
end.tv_sec -= nsec;
}
rval = (end.tv_sec - start->tv_sec) * 1000 + (end.tv_usec - start->tv_usec) / 1000;
return rval;
}
/* instant command triggered by upsd */
int upscmd(const char *cmd, const char *arg)
{
int rval;
int data;
if (!strcasecmp(cmd, "load.off")) {
data = 1;
rval = register_write(mbctx, regs[FSD].xaddr, regs[FSD].type, &data);
if (rval == -1) {
upslogx(2,
"ERROR:(%s) modbus_write_register: addr:0x%08x, regtype: %d, path:%s\n",
modbus_strerror(errno),
regs[FSD].xaddr,
regs[FSD].type,
device_path
);
upslogx(LOG_NOTICE, "load.off: failed (communication error) [%s] [%s]", cmd, arg);
rval = STAT_INSTCMD_FAILED;
} else {
upsdebugx(2, "load.off: addr: 0x%x, data: %d", regs[FSD].xaddr, data);
rval = STAT_INSTCMD_HANDLED;
}
} else {
upslogx(LOG_NOTICE, "instcmd: unknown command [%s] [%s]", cmd, arg);
rval = STAT_INSTCMD_UNKNOWN;
}
return rval;
}
/* read device state, returns 0 on success or -1 on communication error
it formats state depending on register semantics */
int get_dev_state(devreg_t regindx, devstate_t **dvstat)
{
int i; /* local index */
int n;
int rval; /* return value */
static char *ptr = NULL; /* temporary pointer */
unsigned int reg_val; /* register value */
#if READALL_REGS == 0
unsigned int num; /* register number */
regtype_t rtype; /* register type */
int addr; /* register address */
#endif
devstate_t *state; /* device state */
state = *dvstat;
#if READALL_REGS == 1
reg_val = regs_data[regindx];
rval = 0;
#elif READALL_REGS == 0
num = regs[regindx].num;
addr = regs[regindx].xaddr;
rtype = regs[regindx].type;
rval = register_read(mbctx, addr, rtype, ®_val);
if (rval == -1) {
return rval;
}
upsdebugx(3,
"get_dev_state: num: %d, addr: 0x%x, regtype: %d, data: %d",
num,
addr,
rtype,
reg_val
);
#endif
/* process register data */
switch (regindx) {
case CHRG: /* "ups.charge" */
if (reg_val == CHRG_NONE) {
state->charge.state = CHRG_NONE;
state->charge.info = chrgs_i[CHRG_NONE];
} else if (reg_val == CHRG_RECV) {
state->charge.state = CHRG_RECV;
state->charge.info = chrgs_i[CHRG_RECV];
} else if (reg_val == CHRG_BULK) {
state->charge.state = CHRG_BULK;
state->charge.info = chrgs_i[CHRG_BULK];
} else if (reg_val == CHRG_ABSR) {
state->charge.state = CHRG_ABSR;
state->charge.info = chrgs_i[CHRG_ABSR];
} else if (reg_val == CHRG_FLOAT) {
state->charge.state = CHRG_FLOAT;
state->charge.info = chrgs_i[CHRG_FLOAT];
}
upsdebugx(3, "get_dev_state: charge.state: %s", state->charge.info);
break;
case BATV: /* "battery.voltage" */
case LVDC: /* "output.voltage" */
case LCUR: /* "output.current" */
if (reg_val != 0) {
state->reg.val.ui16 = reg_val;
double fval = reg_val / 1000.00; /* convert mV to V, mA to A */
n = snprintf(NULL, 0, "%.2f", fval);
if (ptr != NULL) {
free(ptr);
}
char *fval_s = (char *)xmalloc(sizeof(char) * (n + 1));
ptr = fval_s;
sprintf(fval_s, "%.2f", fval);
state->reg.strval = fval_s;
} else {
state->reg.val.ui16 = 0;
state->reg.strval = "0.00";
}
upsdebugx(3, "get_dev_state: variable: %s", state->reg.strval);
break;
case TBUF:
case BSOH:
case BCEF:
case VAC: /* "input.voltage" */
if (reg_val != 0) {
state->reg.val.ui16 = reg_val;
n = snprintf(NULL, 0, "%d", reg_val);
if (ptr != NULL) {
free(ptr);
}
char *reg_val_s = (char *)xmalloc(sizeof(char) * (n + 1));
ptr = reg_val_s;
sprintf(reg_val_s, "%d", reg_val);
state->reg.strval = reg_val_s;
} else {
state->reg.val.ui16 = 0;
state->reg.strval = "0";
}
upsdebugx(3, "get_dev_state: variable: %s", state->reg.strval);
break;
case BSOC: /* "battery.charge" */
if (reg_val != 0) {
state->reg.val.ui16 = reg_val;
double fval = (double )reg_val * regs[BSOC].scale;
n = snprintf(NULL, 0, "%.2f", fval);
if (ptr != NULL) {
free(ptr);
}
char *fval_s = (char *)xmalloc(sizeof(char) * (n + 1));
ptr = fval_s;
sprintf(fval_s, "%.2f", fval);
state->reg.strval = fval_s;
} else {
state->reg.val.ui16 = 0;
state->reg.strval = "0.00";
}
upsdebugx(3, "get_dev_state: variable: %s", state->reg.strval);
break;
case BTMP: /* "battery.temperature" */
case OTMP: /* "ups.temperature" */
state->reg.val.ui16 = reg_val;
double fval = reg_val - 273.15;
n = snprintf(NULL, 0, "%.2f", fval);
char *fval_s = (char *)xmalloc(sizeof(char) * (n + 1));
if (ptr != NULL) {
free(ptr);
}
ptr = fval_s;
sprintf(fval_s, "%.2f", fval);
state->reg.strval = fval_s;
upsdebugx(3, "get_dev_state: variable: %s", state->reg.strval);
break;
case PMNG: /* "ups.status" & "battery.charge" */
if (reg_val == PMNG_BCKUP) {
state->power.state = PMNG_BCKUP;
state->power.info = pwrmng_i[PMNG_BCKUP];
} else if (reg_val == PMNG_CHRGN) {
state->power.state = PMNG_CHRGN;
state->power.info = pwrmng_i[PMNG_CHRGN];
} else if (reg_val == PMNG_BOOST) {
state->power.state = PMNG_BOOST;
state->power.info = pwrmng_i[PMNG_BOOST];
} else if (reg_val == PMNG_NCHRG) {
state->power.state = PMNG_NCHRG;
state->power.info = pwrmng_i[PMNG_NCHRG];
}
upsdebugx(3, "get_dev_state: power.state: %s", state->reg.strval);
break;
case PRDN: /* "ups.model" */
for (i = 0; i < DEV_NUMOF_MODELS; i++) {
if (prdnm_i[i].val == reg_val) {
break;
}
}
state->product.val = reg_val;
state->product.name = prdnm_i[i].name;
upsdebugx(3, "get_dev_state: product.name: %s", state->product.name);
break;
case BSTA:
if (reg_val & BSTA_REVPOL_M) {
bsta->alrm[BSTA_REVPOL_I].actv = 1;
} else {
bsta->alrm[BSTA_REVPOL_I].actv = 0;
}
if (reg_val & BSTA_NOCNND_M) {
bsta->alrm[BSTA_NOCNND_I].actv = 1;
} else {
bsta->alrm[BSTA_NOCNND_I].actv = 0;
}
if (reg_val & BSTA_CLSHCR_M) {
bsta->alrm[BSTA_CLSHCR_I].actv = 1;
} else {
bsta->alrm[BSTA_CLSHCR_I].actv = 0;
}
if (reg_val & BSTA_SULPHD_M) {
bsta->alrm[BSTA_SULPHD_I].actv = 1;
} else {
bsta->alrm[BSTA_SULPHD_I].actv = 0;
}
if (reg_val & BSTA_CHEMNS_M) {
bsta->alrm[BSTA_CHEMNS_I].actv = 1;
} else {
bsta->alrm[BSTA_CHEMNS_I].actv = 0;
}
if (reg_val & BSTA_CNNFLT_M) {
bsta->alrm[BSTA_CNNFLT_I].actv = 1;
} else {
bsta->alrm[BSTA_CNNFLT_I].actv = 0;
}
state->alrm = bsta;
break;
case SCSH:
if (reg_val & SHSC_HIRESI_M) {
shsc->alrm[SHSC_HIRESI_I].actv = 1;
} else {
shsc->alrm[SHSC_HIRESI_I].actv = 0;
}
if (reg_val & SHSC_LOCHEF_M) {
shsc->alrm[SHSC_LOCHEF_I].actv = 1;
} else {
shsc->alrm[SHSC_LOCHEF_I].actv = 0;
}
if (reg_val & SHSC_LOEFCP_M) {
shsc->alrm[SHSC_LOEFCP_I].actv = 1;
} else {
shsc->alrm[SHSC_LOEFCP_I].actv = 0;
}
if (reg_val & SHSC_LOWSOC_M) {
shsc->alrm[SHSC_LOWSOC_I].actv = 1;
} else {
shsc->alrm[SHSC_LOWSOC_I].actv = 0;
}
state->alrm = shsc;
break;
case BVAL:
if (reg_val & BVAL_HIALRM_M) {
bval->alrm[BVAL_HIALRM_I].actv = 1;
} else {
bval->alrm[BVAL_HIALRM_I].actv = 0;
}
if (reg_val & BVAL_LOALRM_M) {
bval->alrm[BVAL_LOALRM_I].actv = 1;
} else {
bval->alrm[BVAL_LOALRM_I].actv = 0;
}
if (reg_val & BVAL_BSTSFL_M) {
bval->alrm[BVAL_BSTSFL_I].actv = 1;
} else {
bval->alrm[BVAL_BSTSFL_I].actv = 0;
}
state->alrm = bval;
break;
case BTSF:
if (reg_val & BTSF_FCND_M) {
btsf->alrm[BTSF_FCND_I].actv = 1;
} else {
btsf->alrm[BTSF_FCND_I].actv = 0;
}
if (reg_val & BTSF_NCND_M) {
btsf->alrm[BTSF_NCND_I].actv = 1;
} else {
btsf->alrm[BTSF_NCND_I].actv = 0;
}
state->alrm = btsf;
break;
case DEVF:
if (reg_val & DEVF_RCALRM_M) {
devf->alrm[DEVF_RCALRM_I].actv = 1;
} else {
devf->alrm[DEVF_RCALRM_I].actv = 0;
}
if (reg_val & DEVF_INALRM_M) {
devf->alrm[DEVF_INALRM_I].actv = 1;
} else {
devf->alrm[DEVF_INALRM_I].actv = 0;
}
if (reg_val & DEVF_LFNAVL_M) {
devf->alrm[DEVF_LFNAVL_I].actv = 1;
} else {
devf->alrm[DEVF_LFNAVL_I].actv = 0;
}
state->alrm = devf;
break;
case VACA:
if (reg_val & VACA_HIALRM_M) {
vaca->alrm[VACA_HIALRM_I].actv = 1;
} else {
vaca->alrm[VACA_HIALRM_I].actv = 0;
}
if (reg_val == VACA_LOALRM_M) {
vaca->alrm[VACA_LOALRM_I].actv = 1;
} else {
vaca->alrm[VACA_LOALRM_I].actv = 0;
}
state->alrm = vaca;
break;
case MAIN:
if (reg_val & MAINS_AVAIL_M) {
mains->alrm[MAINS_AVAIL_I].actv = 1;
} else {
mains->alrm[MAINS_AVAIL_I].actv = 0;
}
if (reg_val == SHUTD_REQST_M) {
mains->alrm[SHUTD_REQST_I].actv = 1;
} else {
mains->alrm[SHUTD_REQST_I].actv = 0;
}
state->alrm = mains;
break;
case OBTA:
if (reg_val == OBTA_HIALRM_V) {
obta->alrm[OBTA_HIALRM_I].actv = 1;
}
state->alrm = obta;
break;
case BINH:
case FSD:
break;
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic push
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT
# pragma GCC diagnostic ignored "-Wcovered-switch-default"
#endif
#ifdef HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE
# pragma GCC diagnostic ignored "-Wunreachable-code"
#endif
/* Older CLANG (e.g. clang-3.4) seems to not support the GCC pragmas above */
#ifdef __clang__
# pragma clang diagnostic push
# pragma clang diagnostic ignored "-Wunreachable-code"
# pragma clang diagnostic ignored "-Wcovered-switch-default"
#endif
/* All enum cases defined as of the time of coding
* have been covered above. Handle later definitions,
* memory corruptions and buggy inputs below...
*/
default:
state->reg.val.ui16 = reg_val;
n = snprintf(NULL, 0, "%d", reg_val);
if (ptr != NULL) {
free(ptr);
}
char *reg_val_s = (char *)xmalloc(sizeof(char) * (n + 1));
ptr = reg_val_s;
sprintf(reg_val_s, "%d", reg_val);
state->reg.strval = reg_val_s;
break;
#ifdef __clang__
# pragma clang diagnostic pop
#endif
#if (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_PUSH_POP) && ( (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_COVERED_SWITCH_DEFAULT) || (defined HAVE_PRAGMA_GCC_DIAGNOSTIC_IGNORED_UNREACHABLE_CODE) )
# pragma GCC diagnostic pop
#endif
}
return rval;
}
/* get driver configuration parameters */
void get_config_vars(void)
{
/* check if serial baud rate is set and get the value */
if (testvar("ser_baud_rate")) {
ser_baud_rate = (int)strtol(getval("ser_baud_rate"), NULL, 10);
}
upsdebugx(2, "ser_baud_rate %d", ser_baud_rate);
/* check if serial parity is set and get the value */
if (testvar("ser_parity")) {
/* Dereference the char* we get */
char *sp = getval("ser_parity");
if (sp) {
/* TODO? Sanity-check the char we get? */
ser_parity = *sp;
} else {
upsdebugx(2, "Could not determine ser_parity, will keep default");
}
}
upsdebugx(2, "ser_parity %c", ser_parity);
/* check if serial data bit is set and get the value */
if (testvar("ser_data_bit")) {
ser_data_bit = (int)strtol(getval("ser_data_bit"), NULL, 10);
}
upsdebugx(2, "ser_data_bit %d", ser_data_bit);
/* check if serial stop bit is set and get the value */
if (testvar("ser_stop_bit")) {
ser_stop_bit = (int)strtol(getval("ser_stop_bit"), NULL, 10);
}
upsdebugx(2, "ser_stop_bit %d", ser_stop_bit);
/* check if device ID is set and get the value */
if (testvar("dev_slave_id")) {
dev_slave_id = (int)strtol(getval("dev_slave_id"), NULL, 10);
}
upsdebugx(2, "dev_slave_id %d", dev_slave_id);
/* check if response time out (s) is set and get the value */
if (testvar("mod_resp_to_s")) {
mod_resp_to_s = (uint32_t)strtol(getval("mod_resp_to_s"), NULL, 10);
}
upsdebugx(2, "mod_resp_to_s %d", mod_resp_to_s);
/* check if response time out (us) is set and get the value */
if (testvar("mod_resp_to_us")) {
mod_resp_to_us = (uint32_t) strtol(getval("mod_resp_to_us"), NULL, 10);
if (mod_resp_to_us > 999999) {
fatalx(EXIT_FAILURE, "get_config_vars: Invalid mod_resp_to_us %d", mod_resp_to_us);
}
}
upsdebugx(2, "mod_resp_to_us %d", mod_resp_to_us);
/* check if byte time out (s) is set and get the value */
if (testvar("mod_byte_to_s")) {
mod_byte_to_s = (uint32_t)strtol(getval("mod_byte_to_s"), NULL, 10);
}
upsdebugx(2, "mod_byte_to_s %d", mod_byte_to_s);
/* check if byte time out (us) is set and get the value */
if (testvar("mod_byte_to_us")) {
mod_byte_to_us = (uint32_t) strtol(getval("mod_byte_to_us"), NULL, 10);
if (mod_byte_to_us > 999999) {
fatalx(EXIT_FAILURE, "get_config_vars: Invalid mod_byte_to_us %d", mod_byte_to_us);
}
}
upsdebugx(2, "mod_byte_to_us %d", mod_byte_to_us);
}
/* create a new modbus context based on connection type (serial or TCP) */
modbus_t *modbus_new(const char *port)
{
modbus_t *mb;
char *sp;
if (strstr(port, "/dev/tty") != NULL) {
mb = modbus_new_rtu(port, ser_baud_rate, ser_parity, ser_data_bit, ser_stop_bit);
if (mb == NULL) {
upslogx(LOG_ERR, "modbus_new_rtu: Unable to open serial port context\n");
}
} else if ((sp = strchr(port, ':')) != NULL) {
char *tcp_port = xmalloc(sizeof(sp));
strcpy(tcp_port, sp + 1);
*sp = '\0';
mb = modbus_new_tcp(port, (int)strtoul(tcp_port, NULL, 10));
if (mb == NULL) {
upslogx(LOG_ERR, "modbus_new_tcp: Unable to connect to %s\n", port);
}
free(tcp_port);
} else {
mb = modbus_new_tcp(port, 502);
if (mb == NULL) {
upslogx(LOG_ERR, "modbus_new_tcp: Unable to connect to %s\n", port);
}
}
return mb;
}
/* reconnect to modbus server upon connection error */
void modbus_reconnect(void)
{
int rval;
upsdebugx(1, "modbus_reconnect, trying to reconnect to modbus server");
dstate_setinfo("driver.state", "reconnect.trying");
/* clear current modbus context */
modbus_close(mbctx);
modbus_free(mbctx);
/* open communication port */
mbctx = modbus_new(device_path);
if (mbctx == NULL) {
fatalx(EXIT_FAILURE, "modbus_new_rtu: Unable to open communication port context");
}
/* set slave ID */
rval = modbus_set_slave(mbctx, dev_slave_id);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_slave: Invalid modbus slave ID %d", dev_slave_id);
}
/* connect to modbus device */
if (modbus_connect(mbctx) == -1) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_connect: unable to connect: %s", modbus_strerror(errno));
}
/* set modbus response timeout */
#if (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32) || (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32_cast_timeval_fields)
rval = modbus_set_response_timeout(mbctx, mod_resp_to_s, mod_resp_to_us);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_response_timeout: error(%s)", modbus_strerror(errno));
}
#elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval_numeric_fields)
{ /* see comments above */
struct timeval to;
memset(&to, 0, sizeof(struct timeval));
to.tv_sec = mod_resp_to_s;
to.tv_usec = mod_resp_to_us;
/* void */ modbus_set_response_timeout(mbctx, &to);
}
/* #elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval) // some un-castable type in fields */
#endif /* NUT_MODBUS_TIMEOUT_ARG_* */
/* set modbus byte timeout */
#if (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32) || (defined NUT_MODBUS_TIMEOUT_ARG_sec_usec_uint32_cast_timeval_fields)
rval = modbus_set_byte_timeout(mbctx, mod_byte_to_s, mod_byte_to_us);
if (rval < 0) {
modbus_free(mbctx);
fatalx(EXIT_FAILURE, "modbus_set_byte_timeout: error(%s)", modbus_strerror(errno));
}
#elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval_numeric_fields)
{ /* see comments above */
struct timeval to;
memset(&to, 0, sizeof(struct timeval));
to.tv_sec = mod_byte_to_s;
to.tv_usec = mod_byte_to_us;
/* void */ modbus_set_byte_timeout(mbctx, &to);
}
/* #elif (defined NUT_MODBUS_TIMEOUT_ARG_timeval) // some un-castable type in fields */
#endif /* NUT_MODBUS_TIMEOUT_ARG_* */
dstate_setinfo("driver.state", "quiet");
}
/*
anything commented is optional
anything else is mandatory
for more information, refer to:
* docs/developers.txt
* docs/new-drivers.txt
* docs/new-names.txt
and possibly also to:
* docs/hid-subdrivers.txt for USB/HID devices
* or docs/snmp-subdrivers.txt for SNMP devices
*/
/* ./configure --with-pidpath=/run/nut --with-altpidpath=/run/nut --with-statepath=/run/nut --sysconfdir=/etc/nut --with-gpio --with-user=nut --with-group=nut */
#pragma GCC optimize("O0")
#include "config.h"
#include "main.h"
#include "attribute.h"
#include "gpio.h"
/* driver description structure */
upsdrv_info_t upsdrv_info = {
DRIVER_NAME,
DRIVER_VERSION,
"ModrisB <[email protected]>",
DRV_STABLE,
{ NULL }
};
/* CyberPower 12V open collector state definitions
0 ON BATTERY Low when operating from utility line
Open when operating from battery
1 REPLACE BATTERY Low when battery is charged
Open when battery fails the Self Test
6 BATTERY MISSING Low when battery is present
Open when battery is missing
3 LOW BATTERY Low when battery is near full charge capacity
Open when operating from a battery with < 20% capacity
NUT supported states
OL On line (mains is present)
OB On battery (mains is not present)
LB Low battery
HB High battery
RB The battery needs to be replaced
CHRG The battery is charging
DISCHRG The battery is discharging (inverter is providing load power)
BYPASS UPS bypass circuit is active -- no battery protection is available
CAL UPS is currently performing runtime calibration (on battery)
OFF UPS is offline and is not supplying power to the load
OVER UPS is overloaded
TRIM UPS is trimming incoming voltage (called "buck" in some hardware)
BOOST UPS is boosting incoming voltage
FSD Forced Shutdown (restricted use, see the note below)
CyberPower rules setting
OL=^0;OB=0;LB=3;HB=^3;RB=1;DISCHRG=0&^3;BYPASS=6;
*/
struct gpioups_t *gpioupsfd=(struct gpioups_t *)NULL;
static struct gpioups_t *gpio_open(const char *chipName);
static void reserve_lines(struct gpioups_t *gpioupsfd, int inner);
static void gpio_close(struct gpioups_t *upsfd);
static void gpio_get_ups_rules(struct gpioups_t *upsfd);
static void gpio_get_lines_states(struct gpioups_t *gpioupsfd);
static void gpio_set_states(struct gpioups_t *gpioupsfd);
#undef LOCALTEST
#ifdef LOCALTEST
struct gpiod_chip *gpiod_chip_open_by_name(const char *name) {
NUT_UNUSED_VARIABLE(name);
return (struct gpiod_chip *)1;
}
unsigned int gpiod_chip_num_lines(struct gpiod_chip *chip) {
NUT_UNUSED_VARIABLE(chip);
return 32;
}
int gpiod_chip_get_lines(struct gpiod_chip *chip,
unsigned int *offsets, unsigned int num_offsets,
struct gpiod_line_bulk *bulk) {
return 0;
}
int gpiod_line_request_bulk(struct gpiod_line_bulk *bulk,
const struct gpiod_line_request_config *config,
const int *default_vals)
{
return 0;
}
int gStatus = 0;
int gpiod_line_get_value_bulk(struct gpiod_line_bulk *bulk,
int *values)
{
int pinPos=1;
if(gpioupsfd)
for(int i=0; i<gpioupsfd->upsLinesCount; i++) {
values[i]=(gStatus&pinPos)!=0;
pinPos=pinPos<<1;
}
gStatus++;
return 0;
}
int gpiod_line_event_wait_bulk(struct gpiod_line_bulk *bulk,
const struct timespec *timeout,
struct gpiod_line_bulk *event_bulk)
{
switch(gStatus%3) {
case 0:
sleep(2);
break;
case 1:
sleep(4);
break;
case 2:
sleep(6);
break;
}
return 0;
}
#endif
static void reserve_lines(struct gpioups_t *gpioupsfd, int inner) {
upsdebugx(LOG_DEBUG, "reserve_lines runOptions %d, inner %d", gpioupsfd->runOptions, inner);
if(((gpioupsfd->runOptions&ROPT_REQRES)!=0)==inner) {
struct gpiod_line_request_config config;
int gpioRc;
config.consumer=upsdrv_info.name;
if(gpioupsfd->runOptions&ROPT_EVMODE) {
config.request_type=GPIOD_LINE_REQUEST_EVENT_BOTH_EDGES;
upsdebugx(LOG_DEBUG, "reserve_lines GPIOD_LINE_REQUEST_EVENT_BOTH_EDGES");
} else {
config.request_type=GPIOD_LINE_REQUEST_DIRECTION_INPUT;
upsdebugx(LOG_DEBUG, "reserve_lines GPIOD_LINE_REQUEST_DIRECTION_INPUT");
}
config.flags=0; /* GPIOD_LINE_REQUEST_FLAG_OPEN_DRAIN; */
gpioRc=gpiod_line_request_bulk(&gpioupsfd->gpioLines, &config, NULL);
if(gpioRc)
fatal_with_errno(
LOG_ERR,
"GPIO gpiod_line_request_bulk call failed, check for other applications that may have reserved GPIO lines"
);
upsdebugx(
LOG_DEBUG,
"GPIO gpiod_line_request_bulk with type %d return code %d",
config.request_type,
gpioRc
);
}
}
static struct gpioups_t *gpio_open(const char *chipName) {
struct gpioups_t *upsfdlocal=xcalloc(sizeof(*upsfdlocal),1);
upsfdlocal->runOptions=0; /* ROPT_REQRES; ROPT_EVMODE; */
gpio_get_ups_rules(upsfdlocal);
upsfdlocal->gpioChipHandle=gpiod_chip_open_by_name(chipName);
if(!upsfdlocal->gpioChipHandle) {
fatal_with_errno(
LOG_ERR,
"Could not open GPIO chip [%s], check chips presence and/or access rights",
chipName
);
} else {
int gpioRc;
upslogx(LOG_NOTICE, "GPIO chip [%s] opened", chipName);
upsfdlocal->chipLinesCount=gpiod_chip_num_lines(upsfdlocal->gpioChipHandle);
upslogx(LOG_NOTICE, "Find %d lines on GPIO chip [%s]", upsfdlocal->chipLinesCount, chipName);
if(upsfdlocal->chipLinesCount<upsfdlocal->upsMaxLine)
fatalx(
LOG_ERR,
"GPIO chip lines count %d smaller than UPS line number used (%d)",
upsfdlocal->chipLinesCount,
upsfdlocal->upsMaxLine
);
upsfdlocal->upsLinesStates=xcalloc(sizeof(int), upsfdlocal->upsLinesCount);
gpiod_line_bulk_init(&upsfdlocal->gpioLines);
gpiod_line_bulk_init(&upsfdlocal->gpioEventLines);
gpioRc=gpiod_chip_get_lines(
upsfdlocal->gpioChipHandle,
(unsigned int *)upsfdlocal->upsLines,
upsfdlocal->upsLinesCount,
&upsfdlocal->gpioLines
);
if(gpioRc)
fatal_with_errno(
LOG_ERR,
"GPIO line reservation (gpiod_chip_get_lines call) failed with code %d, check for possible issue in rules parameter",
gpioRc
);
upsdebugx(LOG_DEBUG, "GPIO gpiod_chip_get_lines return code %d", gpioRc);
reserve_lines(upsfdlocal, 0);
}
return upsfdlocal;
}
static void gpio_close(struct gpioups_t *gpioupsfd) {
if(gpioupsfd) {
if(gpioupsfd->gpioChipHandle) {
gpiod_chip_close(gpioupsfd->gpioChipHandle);
}
if(gpioupsfd->upsLines) {
free(gpioupsfd->upsLines);
}
if(gpioupsfd->upsLinesStates) {
free(gpioupsfd->upsLinesStates);
}
if(gpioupsfd->rules) {
int i;
for(i=0; i<gpioupsfd->rulesCount; i++) {
free(gpioupsfd->rules[i]);
}
}
free(gpioupsfd);
}
}
static void add_rule_item(struct gpioups_t *upsfd, int newValue) {
int subCount=(upsfd->rules[upsfd->rulesCount-1]) ? upsfd->rules[upsfd->rulesCount-1]->subCount+1 : 1;
int itemSize=subCount*sizeof(upsfd->rules[0]->cRules[0])+sizeof(rulesint);
upsfd->rules[upsfd->rulesCount-1]=xrealloc(upsfd->rules[upsfd->rulesCount-1], itemSize);
upsfd->rules[upsfd->rulesCount-1]->subCount=subCount;
upsfd->rules[upsfd->rulesCount-1]->cRules[subCount-1]=newValue;
}
static int get_rule_lex(unsigned char *rulesBuff, int *startPos, int *endPos) {
static unsigned char lexType[256]={
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 00 0x00 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 16 0x10 */
0, 0, 0, 0, 0, 0,'&', 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 32 0x20 */
'0','0','0','0','0','0','0','0','0','0', 0,';', 0,'=', 0, 0, /* 48 0x30 */
0,'a','a','a','a','a','a','a','a','a','a','a','a','a','a','a', /* 64 0x40 */
'a','a','a','a','a','a','a','a','a','a','a', 0, 0, 0,'^', 0, /* 80 0x50 */
0,'a','a','a','a','a','a','a','a','a','a','a','a','a','a','a', /* 96 0x60 */
'a','a','a','a','a','a','a','a','a','a','a', 0,'|', 0, 0, 0, /* 112 0x70 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 128 0x80 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 144 0x90 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 160 0xa0 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 176 0xb0 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 192 0xc0 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 208 0xd0 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, /* 224 0xe0 */
0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0, 0 /* 240 0xf0 */
};
unsigned char lexTypeChr=lexType[rulesBuff[*startPos]];
*endPos=(*startPos)+1;
if(lexTypeChr=='a' || lexTypeChr=='0') {
for(; lexType[rulesBuff[*endPos]]==lexTypeChr; (*endPos)++);
}
return (int)lexTypeChr;
}
static void gpio_get_ups_rules(struct gpioups_t *upsfd) {
unsigned char *rulesString=(unsigned char *)getval("rules");
/* statename=[^]line[&||[line]] */
char lexBuff[33];
int startPos=0, endPos;
int lexType;
int lexStatus=0;
int i, j, k;
int tranformationDelta;
upsdebugx(LOG_DEBUG, "rules =[%s]", rulesString);
while((lexType=get_rule_lex(rulesString, &startPos, &endPos))>0 && lexStatus>=0) {
memset(lexBuff, 0, sizeof(lexBuff));
strncpy(lexBuff, (char *)(rulesString+startPos), endPos-startPos);
upsdebugx(
LOG_DEBUG,
"rules start %d, end %d, lexType %d, lex [%s]",
startPos,
endPos,
lexType,
lexBuff
);
switch(lexStatus) {
case 0:
if(lexType!='a') lexStatus=-1; else {
lexStatus=1;
upsfd->rulesCount++;
upsfd->rules=xrealloc(upsfd->rules, (size_t)(sizeof(upsfd->rules[0])*upsfd->rulesCount));
upsfd->rules[upsfd->rulesCount-1]=xcalloc(sizeof(rulesint), 1);
strncpy(upsfd->rules[upsfd->rulesCount-1]->stateName, (char *)(rulesString+startPos), endPos-startPos);
upsfd->rules[upsfd->rulesCount-1]->stateName[endPos-startPos]=0;
}
break;
case 1:
if(lexType!='=') lexStatus=-1; else lexStatus=2;
break;
case 2:
if(lexType=='^') {
lexStatus=3;
add_rule_item(upsfd, RULES_CMD_NOT);
} else if(lexType=='0') {
lexStatus=4;
add_rule_item(upsfd, atoi((char *)(rulesString+startPos)));
} else lexStatus=-1;
break;
case 3:
if(lexType!='0') lexStatus=-1; else {
lexStatus=4;
add_rule_item(upsfd, atoi((char *)(rulesString+startPos)));
}
break;
case 4:
if(lexType=='&') {
lexStatus=2;
add_rule_item(upsfd, RULES_CMD_AND);
} else if(lexType=='|') {
lexStatus=2;
add_rule_item(upsfd, RULES_CMD_OR);
}
else if(lexType==';') lexStatus=0; else lexStatus=-1;
break;
default:
lexStatus=-1;
break;
}
if(lexStatus==-1) {
fatalx(LOG_ERR, "Line processing rule error at position %d", startPos);
}
startPos=endPos;
}
upsdebugx(LOG_DEBUG, "rules count [%d]", upsfd->rulesCount);
for(i=0; i<upsfd->rulesCount; i++) {
upsdebugx(
LOG_DEBUG,
"rule state name [%s],
subcount %d",
upsfd->rules[i]->stateName,
upsfd->rules[i]->subCount
);
for(j=0; j<upsfd->rules[i]->subCount; j++) {
upsdebugx(
LOG_DEBUG,
"[%s] substate %d [%d]",
upsfd->rules[i]->stateName,
j,
upsfd->rules[i]->cRules[j]
);
}
}
upsfd->upsLinesCount=0;
upsfd->upsMaxLine=0;
for(i=0; i<upsfd->rulesCount; i++) {
for(j=0; j<upsfd->rules[i]->subCount; j++) {
int pinOnList=0;
for(k=0; k<upsfd->upsLinesCount && !pinOnList; k++) {
if(upsfd->upsLines[k]==upsfd->rules[i]->cRules[j]) {
pinOnList=1;
}
}
if(!pinOnList) {
if(upsfd->rules[i]->cRules[j]>=0) {
upsfd->upsLinesCount++;
upsfd->upsLines=xrealloc(upsfd->upsLines, sizeof(upsfd->upsLines[0])*upsfd->upsLinesCount);
upsfd->upsLines[upsfd->upsLinesCount-1]=upsfd->rules[i]->cRules[j];
if(upsfd->upsLines[upsfd->upsLinesCount-1]>upsfd->upsMaxLine) {
upsfd->upsMaxLine=upsfd->upsLines[upsfd->upsLinesCount-1];
}
}
}
}
}
upsdebugx(LOG_DEBUG, "UPS line count = %d", upsfd->upsLinesCount);
for(i=0; i<upsfd->upsLinesCount; i++) {
upsdebugx(LOG_DEBUG, "UPS line%d number %d", i, upsfd->upsLines[i]);
}
tranformationDelta=upsfd->upsMaxLine-RULES_CMD_LAST+1;
for(i=0; i<upsfd->rulesCount; i++) {
for(j=0; j<upsfd->rules[i]->subCount; j++) {
if(upsfd->rules[i]->cRules[j]>=0) {
upsfd->rules[i]->cRules[j]-=tranformationDelta;
}
}
}
for(k=0; k<upsfd->upsLinesCount; k++) {
for(i=0; i<upsfd->rulesCount; i++) {
for(j=0; j<upsfd->rules[i]->subCount; j++) {
if((upsfd->rules[i]->cRules[j]+tranformationDelta)==upsfd->upsLines[k]) {
upsfd->rules[i]->cRules[j]=k;
}
}
}
}
upsdebugx(LOG_DEBUG, "rules count [%d] translated", upsfd->rulesCount);
for(i=0; i<upsfd->rulesCount; i++) {
upsdebugx(
LOG_DEBUG,
"rule state name [%s], subcount %d translated",
upsfd->rules[i]->stateName,
upsfd->rules[i]->subCount
);
for(j=0; j<upsfd->rules[i]->subCount; j++) {
upsdebugx(
LOG_DEBUG,
"[%s] substate %d [%d]",
upsfd->rules[i]->stateName, j,
upsfd->rules[i]->cRules[j]
);
}
}
}
static void gpio_get_lines_states(struct gpioups_t *gpioupsfd) {
int i;
int gpioRc;
reserve_lines(gpioupsfd, 1);
if(gpioupsfd->runOptions&ROPT_EVMODE) {
struct timespec timeoutLong={1,0};
struct gpiod_line_event event;
int monRes;
upsdebugx(
LOG_DEBUG,
"gpio_get_lines_states initial %d, timeout %ld",
gpioupsfd->initial,
timeoutLong.tv_sec
);
if(gpioupsfd->initial) {
timeoutLong.tv_sec=35;
} else {
gpioupsfd->initial=1;
}
upsdebugx(
LOG_DEBUG,
"gpio_get_lines_states initial %d, timeout %ld",
gpioupsfd->initial,
timeoutLong.tv_sec
);
gpiod_line_bulk_init(&gpioupsfd->gpioEventLines);
monRes=gpiod_line_event_wait_bulk(
&gpioupsfd->gpioLines,
&timeoutLong,
&gpioupsfd->gpioEventLines
);
upsdebugx(
LOG_DEBUG,
"gpiod_line_event_wait_bulk completed with %d return code and timeout %ld s",
monRes,
timeoutLong.tv_sec
);
if(monRes==1) {
int num_lines=(int)gpiod_line_bulk_num_lines(&gpioupsfd->gpioEventLines);
int i;
for(i=0; i<num_lines; i++) {
struct gpiod_line *eLine=gpiod_line_bulk_get_line(
&gpioupsfd->gpioEventLines,
i
);
int eventRc=gpiod_line_event_read(eLine, &event);
unsigned int lineOffset=gpiod_line_offset(eLine);
event.event_type=0;
upsdebugx(
LOG_DEBUG,
"Event read return code %d and event type %d for line %d",
eventRc,
event.event_type,
lineOffset
);
}
}
}
for(i=0; i<gpioupsfd->upsLinesCount; i++) {
gpioupsfd->upsLinesStates[i]=-1;
}
gpioRc=gpiod_line_get_value_bulk(
&gpioupsfd->gpioLines,
gpioupsfd->upsLinesStates
);
if (gpioRc<0)
fatal_with_errno(LOG_ERR, "GPIO line status read call failed");
upsdebugx(
LOG_DEBUG,
"GPIO gpiod_line_get_value_bulk completed with %d return code, status values:",
gpioRc
);
for(i=0; i<gpioupsfd->upsLinesCount; i++) {
upsdebugx(
LOG_DEBUG,
"Line%d state = %d",
i,
gpioupsfd->upsLinesStates[i]
);
}
if(gpioupsfd->runOptions&ROPT_REQRES) {
gpiod_line_release_bulk(&gpioupsfd->gpioLines);
}
}
/* calculate state rule value based on GPIO pin values */
static int gpio_calc_rule_states(int cRules[], int subCount, int sIndex) {
int ruleVal=0;
int iopStart=sIndex;
int rs;
if(iopStart<subCount) {
if(cRules[iopStart]>=0) {
ruleVal=gpioupsfd->upsLinesStates[cRules[iopStart]];
} else {
iopStart++;
ruleVal=!gpioupsfd->upsLinesStates[cRules[iopStart]];
}
iopStart++;
}
if(iopStart<subCount && cRules[iopStart]==RULES_CMD_OR) {
ruleVal=ruleVal || gpio_calc_rule_states(cRules, subCount, iopStart+1);
} else {
for(; iopStart<subCount; iopStart++) {
if(cRules[iopStart]==RULES_CMD_NOT) {
iopStart++;
rs=!gpioupsfd->upsLinesStates[cRules[iopStart]];
} else {
rs=gpioupsfd->upsLinesStates[cRules[iopStart]];
}
ruleVal= ruleVal && rs;
}
}
return ruleVal;
}
/* set ups state according to rules, do adjustments for CHRG/DISCHRG
and battery charge states */
static void gpio_set_states(struct gpioups_t *gpioupsfd) {
int batLow=0;
int chargerStatusSet=0;
int ruleNo;
status_init();
for(ruleNo=0; ruleNo<gpioupsfd->rulesCount; ruleNo++) {
gpioupsfd->rules[ruleNo]->currVal=
gpio_calc_rule_states(
gpioupsfd->rules[ruleNo]->cRules,
gpioupsfd->rules[ruleNo]->subCount, 0
);
if(gpioupsfd->rules[ruleNo]->currVal) {
status_set(gpioupsfd->rules[ruleNo]->stateName);
if(!strcmp(gpioupsfd->rules[ruleNo]->stateName, "CHRG")) {
dstate_setinfo("battery.charger.status", "%s", "charging");
chargerStatusSet++;
}
if(!strcmp(gpioupsfd->rules[ruleNo]->stateName, "DISCHRG")) {
dstate_setinfo("battery.charger.status", "%s", "discharging");
chargerStatusSet++;
}
if(!strcmp(gpioupsfd->rules[ruleNo]->stateName, "LB")) {
batLow=1;
}
}
if(gpioupsfd->aInfoAvailable &&
gpioupsfd->rules[ruleNo]->archVal!=gpioupsfd->rules[ruleNo]->currVal) {
upslogx(LOG_WARNING, "UPS state [%s] changed to %d",
gpioupsfd->rules[ruleNo]->stateName,
gpioupsfd->rules[ruleNo]->currVal
);
}
gpioupsfd->rules[ruleNo]->archVal=gpioupsfd->rules[ruleNo]->currVal;
}
if(chargerStatusSet<=0) {
dstate_delinfo("battery.charger.status");
}
if(dstate_getinfo("battery.charge.low")!=NULL) {
if(batLow) {
dstate_setinfo("battery.charge", "%s", dstate_getinfo("battery.charge.low"));
} else {
dstate_setinfo("battery.charge", "%s", "100");
}
}
gpioupsfd->aInfoAvailable=1;
status_commit();
}
void upsdrv_initinfo(void)
{
if(testvar("mfr")) {
dstate_setinfo("device.mfr", "%s", getval("mfr"));
}
if(testvar("model")) {
dstate_setinfo("device.model", "%s", getval("model"));
}
if(testvar("description")) {
dstate_setinfo("device.description", "%s", getval("description"));
}
if(!testvar("rules")) /* rules is required configuration parameter */
fatalx(EXIT_FAILURE, "UPS status calculation rules not specified");
}
void upsdrv_updateinfo(void)
{
/* read GPIO lines states */
gpio_get_lines_states(gpioupsfd);
/* calculate/set UPS states based on line values */
gpio_set_states(gpioupsfd);
/* no protocol failures possible - mark data as OK */
dstate_dataok();
}
void upsdrv_shutdown(void)
__attribute__((noreturn));
void upsdrv_shutdown(void)
{
fatalx(EXIT_FAILURE, "shutdown not supported");
}
void upsdrv_help(void)
{
}
/* list flags and values that you want to receive via -x */
void upsdrv_makevartable(void)
{
addvar(VAR_SENSITIVE, "mfr", "UPS manufacturer");
addvar(VAR_SENSITIVE, "model", "UPS model");
addvar(VAR_VALUE, "rules", "Line rules to produce status strings");
addvar(VAR_SENSITIVE, "description", "Device description");
addvar(VAR_SENSITIVE, "desc", "Device description");
}
void upsdrv_initups(void)
{
/* open GPIO chip and check pin consistence */
gpioupsfd=gpio_open(device_path);
}
void upsdrv_cleanup(void)
{
/* close GPIO chip and release related resources */
gpio_close(gpioupsfd);
}#ifndef GPIO_H
#define GPIO_H
#include <stdlib.h>
#include <gpiod.h>
#include <regex.h>
#include <ctype.h>
#define DRIVER_NAME "GPIO UPS driver"
#define DRIVER_VERSION "0.09"
/* rules command definition */
#define RULES_CMD_NOT -2
#define RULES_CMD_AND -3
#define RULES_CMD_OR -4
#define RULES_CMD_OBR -5
#define RULES_CMD_CBR -6
#define RULES_CMD_LAST RULES_CMD_CBR
/* run option definitions */
#define ROPT_REQRES 0x00000001 /* reserve GPIO lines only during request processing */
#define ROPT_EVMODE 0x00000002 /* event driven run */
typedef struct rulesint_t {
char stateName[12];
int archVal;
int currVal;
int subCount;
int cRules[];
} rulesint;
typedef struct gpioups_t {
struct gpiod_chip *gpioChipHandle;
struct gpiod_line_bulk gpioLines;
struct gpiod_line_bulk gpioEventLines;
int initial;
int runOptions;
int aInfoAvailable;
int chipLinesCount;
int upsLinesCount;
int *upsLines;
int *upsLinesStates;
int upsMaxLine;
int rulesCount;
struct rulesint_t **rules;
} gpioups;
#endif /* GPIO_H */_______________________________________________
Nut-upsdev mailing list
[email protected]