On a test shutdown of an APC Back-UPS RS1500 upsc was run periodically to follow the UPS discharge, it showed these values:
battery.low 120 battery.charge.low 10 As it turned out, the battery.charge.low was encountered first and the system shut down there. However, considering the rate at which the charge was falling at the end I would much rather have had it shutdown sooner than it did. Is there a place in the upsmon.conf (or elsewhere) file where one may enter something like: OVERRIDE_BATTERY_CHARGE_LOW 20 OVERRIDE_BATTERY.LOW 240 ??? Note, I'm not trying to schedule the shutdown at a particular time, just change the limits for when the UPS is considered to be "out of juice". Thank you, David Mathog [EMAIL PROTECTED] Manager, Sequence Analysis Facility, Biology Division, Caltech _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev