> On a test shutdown of an APC Back-UPS RS1500 upsc was run periodically > to follow the UPS discharge, it showed these values: > > battery.low 120 > battery.charge.low 10 > > As it turned out, the battery.charge.low was encountered first and the > system shut down there. However, considering the rate at which the > charge was falling at the end I would much rather have had it shutdown > sooner than it did. Is there a place in the upsmon.conf (or elsewhere) > file where one may enter something like: > > OVERRIDE_BATTERY_CHARGE_LOW 20 > OVERRIDE_BATTERY.LOW 240 > > ??? > > Note, I'm not trying to schedule the shutdown at a particular time, just > change the limits for when the UPS is considered to be "out of juice".
See 'man 8 upsrw'. If your UPS supports changing this value, it should be listed if you run 'upsrw <upsname>'. Most of the time, if it is possible to change this value, it will be stored in non-volatile memory in the UPS itself, so you only need to do this once. If you have any more questions regarding this, please use the nut-upsuser mailinglist instead. Best regards, Arjen -- Eindhoven - The Netherlands Key fingerprint - 66 4E 03 2C 9D B5 CB 9B 7A FE 7E C1 EE 88 BC 57 _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev