Citeren Marco Chiappero <[email protected]>:
I managed to get twice connected at the same time from the same machine to a single UPS using different hostnames, so it's definitely not an IP based check (at least here with 66102 / EC).
Never mind. The alarm messages are not bound to a specific outlet, but are sent to all NSM clients that are connected. Which means that a single connected driver can handle the alarm messages for all outlets. Basically, the NSM subscription allows us to reduce the polling interval to 1 minute or so, without risking high latency for alarms (since they will be pushed from the NMC when they occur).
It looks like the connected clients need to determine themselves (based on the timer values) when to shutdown the host they are running on. Apparently, the decision when to shutdown is made by the NSM client, this is not signaled directly by the NMC.
This means that we can probably just connect to the main outlet and fix the shutdown delay and shutdown timer to the CENTRALIZED configuration without losing anything. One can still override these settings per outlet, by changing values via the NMC web configuration interface. Adding of the NSM alarms can therefor be done without any additional configuration settings, which is preferred for ease of setting things up.