Arjen de Korte ha scritto:
Citeren Marco Chiappero <[email protected]>:
Never mind. The alarm messages are not bound to a specific outlet, but
are sent to all NSM clients that are connected.
The NMC will send some alarm messages rather than others depending on
the outlet the client system it is attached to.
For example, if I remember correctly, I've seen a computer connected to
a programmable outlet receiving both
System.Outlet[1|2].RunTimeToShutdown and System.RunTimeToShutdown
messages, while a client on the main outlet receiving only the latter.
Which means that a
single connected driver can handle the alarm messages for all outlets.
Well, alarm messages are host specific. That said, I can't understand
why we should need to read messages for outlets we are not even using...
Is there a reason for connecting a single host to many outlets of a
single ups?
Basically, the NSM subscription allows us to reduce the polling interval
to 1 minute or so, without risking high latency for alarms (since they
will be pushed from the NMC when they occur).
We still need a small polling interval if we want to keep things easy
and use a non blocking read from the socket. However this implies more
"work" on the client side only.
It looks like the connected clients need to determine themselves (based
on the timer values) when to shutdown the host they are running on.
Apparently, the decision when to shutdown is made by the NSM client,
this is not signaled directly by the NMC.
As far as I can say here, with my firmware revision, it doesn't work
like that. The client provides its own shutdown settings (local or
centralized - if centralized it needs to retrieve them before
subscription), then the NMC does calculations and commands shutdown with
an alarm (level 3) containing the
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit=1 object.
The only degree of freedom (and decision) in the clients lies in
performing a specific action rather than another (or no action at all)
upon reception of a certain alarm message. Clients are "stupid", as it
should be.
This means that we can probably just connect to the main outlet and fix
the shutdown delay and shutdown timer to the CENTRALIZED configuration
without losing anything. One can still override these settings per
outlet, by changing values via the NMC web configuration interface.
Adding of the NSM alarms can therefor be done without any additional
configuration settings, which is preferred for ease of setting things up.
Honestly, I can't see what are you trying to do, things are already
really simple.
You specify a (low) polling interval (suggested), a ups address
(mandatory) and an outlet (mandatory).
Now:
- No shutdown parameters specified (= need to find some valid) -> read
the config.xml page from the ups containing the CENTRALIED ones -> offer
them during subscription.
- One or more parameters specified (shutdown timer is mandatory) (=
using LOCAL settings) -> offer them during subscription.
Then the NMC will use those to specifically notify a host (for every
single host subscribed) its own right time to go down.
(UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit=1 = LB state
for that host).