Dear All, Our software engineers checking your questions and will reply next week.
Sincerely yours -- Alexey Morozov distribution manager -----Original Message----- From: Arjen de Korte [mailto:[email protected]] Sent: Tuesday, November 10, 2009 11:58 AM To: Morozov Alexey Cc: Alexander Gordeev; [email protected] Subject: Re: [Nut-upsdev] Powercom support and sponsorship Citeren Morozov Alexey <[email protected]>: > Kindly please work out in detail your questions. 1) Value too large for defined data type Feature reports 0x11 (UPS.PowerSummary.ConfigVoltage), 0x19 (UPS.Battery.ConfigVoltage), 0x1c (UPS.Input.ConfigVoltage) and 0x20 (UPS.Output.ConfigVoltage) should return an 8 bit (1 byte) value according to the report descriptor. When we retrieve them, we get more than that (probably two bytes, but the actual value can't be reported). Either the report descriptor needs to be fixed, or reading the feature report should return the correct amount of data. -> NUT won't be able to read nominal input-, output- and battery voltage Input reports 0x0a (UPS.PowerSummary.RemainingCapacity) and 0x15 (UPS.Battery.Test) both return 2 bytes while the report descriptor says these should be 8 bit (1 byte), the same as the the corresponding feature reports. -> NUT won't be able to use these reports 2) Erroneous value retrieved for report Reports 0x12, 0x1a, 0x1d and 0x21 all return '212' as value. I very much doubt that UPS.PowerSummary.Voltage, UPS.Battery.Voltage, UPS.Input.Voltage and UPS.Output.Voltage are the same (since these should be measured values). -> NUT won't read the input-, output- and battery voltage 3) Suspicious value read The input report and feature report 0x0e (UPS.PowerSummary.RunTimeToEmpty) don't match (0x0e 0x64 0x10 and 0x0e 0x80 0x09 respectively). While technically not wrong, it is doubtful that this really is the case. Looking at the values read in the input reports, there might be an issue with ordering of data: [0a] 0c 10 (expected 64) [0e] 64 10 (expected 80 09) [15] 80 09 (expected 01) [14] 01 09 (expected 0c 10) Looking at the actual and expected values, it looks like the data for the input reports is outputed with the next input report. Also, the number of bytes returned in the reports seems to be fixed at 2, while this should depend on the actual size of the reports (1 byte for 0x0a and 0x15 and 2 bytes for 0x0e and 0x14). There is a small chance that this could be an issue with libusb, USB controller and/or operating system, so for the moment I would call this suspicious only. Alexander, could you post what you're using right now? Is this a *BSD or a Linux system? -> NUT only uses input reports as a trigger to read feature reports, so if the number of bytes is correct, there would be no issue. Best regards, Arjen PS It would be helpful if I could have a Powercom unit too for debugging the above. -- Please keep list traffic on the list _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
