On Jan 31, 2010, at 8:49 PM, chance fulton wrote:

If there is anything else you want done with this I am available to test
most days.

I did not have time to capture the poweroff event, as it would take me
an hour or so to kill the ups without making too much noise :)


Added secondary load around 60
Power fail at 123
return power at 182

Load removed at 240

Hope this helps.


I can let it run much longer if required, I only stopped it for the sake
of the list.

Thanks, I'll look at the events later.

I'm still confused by the output - it says it's r2300, but in that version, it shouldn't say "Unknown input voltage range: 0x02" because that is one of the cases that it is decoding in the switch statement in decode_v(). Are you sure the tripplite_usb driver is being rebuilt properly?

If any of the other folks on the list want to take a look at this, I'd be happy to have another set of eyes on the problem.

- Charles

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev