Citeren Spiros Ioannou <[email protected]>:

1) new way to initialize model, firmware etc. variables, the strok way
failed because some vars had spaces. (e.g. model "Liebert NX")

Thanks for this patch. I adopted this idea and committed a slightly modified version to the development version.

2) new multipliers for: frequency, nominal power. I get correct readings
now, before I had 500 Hz, and 200VA and now it's ok for me. Test with your
models.

I would like to get some upsc output (latest development version, no patches) from Liebert NX and GXT2 owners before committing this. I'm not quite sure we got everything right now. Check *all* returned values from the upsc output if they are reasonable. If not, provide the debug output (-DDD) as well to see the raw output from the UPS.

3) added battery temperature

Committed, thanks.

4) removed battery.charge. BATTERY_CAPACITY != charge, BATTERY_CAPACITY
means how much the battery has lost its original energy capacity from aging.

Same as the above.

Note that we prefer to break up patches to contain only a single modification. So it would have been better to break up this change in four patches, each changing one of the above.

I also noticed you changed the 'ups.temperature' to 'ambient.temperature'. Note that this change requires an external sensor to be attached to the UPS, otherwise we consider this to be the device (UPS) temperature.

Best regards, Arjen
--
Please keep list traffic on the list


_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev

Reply via email to