Good morning, I just had the chance this morning to get my linux box tied into our network and talking to the UPS. I can now confirm that in NUT v2.4.3 snmp-ups (ietf) works with the Liebert Intellislot Web Card for the GXT2 family of UPS'.
upsc output: tux ~ # upsc work...@localhost battery.charge: 100.00 battery.runtime: 2760.00 battery.runtime.low: 5 battery.voltage: 54.60 device.mfr: Liebert Corporation device.model: GXT2-1500RT120 device.serial: The DAWSON Group device.type: ups driver.name: snmp-ups driver.parameter.mibs: auto driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: 192.168.1.10 driver.version: 2.4.3 driver.version.internal: 0.47 (mib: ietf 1.3) input.frequency: 60.00 input.phases: 1.00 input.quality: 0.00 input.voltage: 117.00 output.current: 6.60 output.frequency: 60.00 output.phases: 1.00 output.voltage: 120.00 ups.firmware: GXT2-00797V01 ups.firmware.aux: 5.000.0 ups.mfr: Liebert Corporation ups.model: GXT2-1500RT120 ups.serial: The DAWSON Group ups.status: OL All parameters are correct and match exactly against what is shown by the intellislot's web status page. -- Drew "Nothing in life is to be feared. It is only to be understood." --Marie Curie _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev