On Mon, Nov 15, 2010 at 11:11 AM, Drew <[email protected]> wrote:
> Good morning,
>
> I just had the chance this morning to get my linux box tied into our
> network and talking to the UPS. I can now confirm that in NUT v2.4.3
> snmp-ups (ietf) works with the Liebert Intellislot Web Card for the
> GXT2 family of UPS'.

Drew,

Have you had a chance to test the "low battery" status (or the "on
battery" status)?

Also, what does "upscmd -l workups" return?

Thanks!

> upsc output:
> tux ~ # upsc work...@localhost
> battery.charge: 100.00
> battery.runtime: 2760.00
> battery.runtime.low: 5
> battery.voltage: 54.60
> device.mfr: Liebert Corporation
> device.model: GXT2-1500RT120
> device.serial: The DAWSON Group
> device.type: ups
> driver.name: snmp-ups
> driver.parameter.mibs: auto
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: 192.168.1.10
> driver.version: 2.4.3
> driver.version.internal: 0.47 (mib: ietf 1.3)
> input.frequency: 60.00
> input.phases: 1.00
> input.quality: 0.00
> input.voltage: 117.00
> output.current: 6.60
> output.frequency: 60.00
> output.phases: 1.00
> output.voltage: 120.00
> ups.firmware: GXT2-00797V01
> ups.firmware.aux: 5.000.0
> ups.mfr: Liebert Corporation
> ups.model: GXT2-1500RT120
> ups.serial: The DAWSON Group
> ups.status: OL
>
> All parameters are correct and match exactly against what is shown by
> the intellislot's web status page.
>
> --
> Drew
>
> "Nothing in life is to be feared. It is only to be understood."
> --Marie Curie
>
> _______________________________________________
> Nut-upsdev mailing list
> [email protected]
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>



-- 
- Charles Lepple