Hi 2011/11/11 Kiss Gabor (Bitman) <[email protected]>
> Dear folks, > > According to mge-mib.c (NUT 2.6.2) LB condition > is gained from variable .1.3.6.1.4.1.705.1.5.14.0 (i.e. > upsmgBatteryLowBattery.0). > > The test device of me does not set this variable to yes(1) > even if runtime drops below the preconfigured limit. > I complained about this at Schneider Electric. > They replied that low battery status is indicated by > .1.3.6.1.4.1.705.1.5.14.0 (upsmgBatteryLowCondition.0). > copy/paste error: you probably meant 1.3.6.1.4.1.705.1.5.16.0 > My measurements confirm this statement. > At least in case of NMC 66074, firmware version "GF". > > Note: variable descriptions in MGE MIB file are quite poor. > I can imagine that some programmers of SE/APC are > also confused by them and some devices use > upsmgBatteryLowBattery while others use upsmgBatteryLowCondition > to signal LB status. > Also consider the historical side, back a few years ago, with part of MGE being sold to (or going with ; like myself) Eaton, while the other was merged with APC... That said, I've added and committed the above OID with the standard lowbatt mapping (1 = LB, 2 = <not LB>) Can you please test the trunk, r3318? Note that I've not yet had time to consider your other (XML/HTTP) mail, but it indeed seems like a bug... cheers, Arnaud -- Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ Debian Developer - http://www.debian.org Free Software Developer - http://arnaud.quette.free.fr/
_______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev