Dear Arnaud,

> > That said, I've added and committed the above OID with the standard lowbatt
> > mapping (1 = LB, 2 = <not LB>)
> > Can you please test the trunk, r3318?

Do you mean this?
http://trac.networkupstools.org/projects/nut/changeset/3318/trunk/drivers/mge-mib.c

> Thanks.
> I'll do in a week or so.
> Unfortunately at this moment I'm quite busy.

I added your new line to version 2.4.1 mgemib.h.
(I have this source prepared on my disk, that was the laziest way
to test your patch. :)

The result is a bit strange:
ups.status: OL OL

More detailed log follows. (Relevant raw SNMP vars and upsc output)

MG-SNMP-UPS-MIB::upsmgConfigLowBatteryTime.0 = INTEGER: 180
MG-SNMP-UPS-MIB::upsmgBatteryRemainingTime.0 = INTEGER: 2791
MG-SNMP-UPS-MIB::upsmgBatteryLowBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgBatteryLowCondition.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputOnBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputOnByPass.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputUtilityOff.0 = INTEGER: no(2)
battery.runtime: 2791.00
ups.status: OL OL

MG-SNMP-UPS-MIB::upsmgConfigLowBatteryTime.0 = INTEGER: 180
MG-SNMP-UPS-MIB::upsmgBatteryRemainingTime.0 = INTEGER: 7430
MG-SNMP-UPS-MIB::upsmgBatteryLowBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgBatteryLowCondition.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputOnBattery.0 = INTEGER: yes(1)
MG-SNMP-UPS-MIB::upsmgOutputOnByPass.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputUtilityOff.0 = INTEGER: yes(1)
battery.runtime: 7430.00
ups.status: OB OB

MG-SNMP-UPS-MIB::upsmgConfigLowBatteryTime.0 = INTEGER: 9999
MG-SNMP-UPS-MIB::upsmgBatteryRemainingTime.0 = INTEGER: 7430
MG-SNMP-UPS-MIB::upsmgBatteryLowBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgBatteryLowCondition.0 = INTEGER: yes(1)
MG-SNMP-UPS-MIB::upsmgOutputOnBattery.0 = INTEGER: yes(1)
MG-SNMP-UPS-MIB::upsmgOutputOnByPass.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputUtilityOff.0 = INTEGER: yes(1)
battery.runtime: 7430.00
ups.status: OB LB OB

MG-SNMP-UPS-MIB::upsmgConfigLowBatteryTime.0 = INTEGER: 9999
MG-SNMP-UPS-MIB::upsmgBatteryRemainingTime.0 = INTEGER: 2791
MG-SNMP-UPS-MIB::upsmgBatteryLowBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgBatteryLowCondition.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputOnBattery.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputOnByPass.0 = INTEGER: no(2)
MG-SNMP-UPS-MIB::upsmgOutputUtilityOff.0 = INTEGER: no(2)
battery.runtime: 2791.00
ups.status: OL OL

Is this what you expected?
Or should I compile a version 2.6.2 driver?

(The test UPS is available in this week only. Please reply soon.)

Regards

Gabor

-- 
A mug of beer, please. Shaken, not stirred.

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to