Arnaud' the original reason for this was due to having multiple communication channels to the UPS. It is possible for the non-NUT channel to start a UPS delayed shutdown that the NUT master and slaves need to know about. Charles suggested using FSD rather than OB LB to avoid confusing messages about a low battery in the log when there isn't a low battery. Upsmon still does the work, I think, it is just that the driver is setting the flag for upsmon to act on rather than upsmon seeing OB LB and doing the same thing. Can the rules be adjusted?

Bill

At 03:44 AM 2/28/2012, Arnaud Quette wrote:
Hi Billy,

switching back this thread to -upsdev

2012/2/27 William R. Elliot <[email protected]>:
> I have been able to set the 'FSD' from the driver and it is picked up by
> upsmon.  That gives me the functionality that I was asked to put in the
> driver. If that is against the rules then I'll make an adjustment when the
> allowed method is defined.  :-)

yup, that's against the tables of the law ;-p
more seriously, the right way to do this is to set the status to "OB
LB", which will trigger upsmon to add FSD.
the reason is that, in master / slave(s) setup, this allows upsmon to
do the job, and notify slaves.

so, as long as you just catch something that implies the FSD status
using "OB LB", everything is fine.

don't hesitate to post your patch on -upsdev to get feedback and
adjustment request, which is needed before we can merge your contrib.

cheers,
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
--
Conseiller Municipal - Saint Bernard du Touvet