Hi David, 2012/4/27 David Woodhouse <[email protected]>: > http://www.zigor.com/uk/index.php/en/products/upssystems/danubioseries > > Ships with UPSilon 2000 software, and appears to work with blazer_usb to > a certain extent with the following config: > > [danubio] > driver = blazer_usb > langid_fix = 0x409 > port = stupidly, I seem to have to set this even though it's ignored > vendorid=0001 > productid=0000 > > Yes, vendor 0001, device 0000. > > idVendor 0x0001 Fry's Electronics > idProduct 0x0000 > bcdDevice 1.00 > iManufacturer 1 > iProduct 2 > iSerial 0 > > > I get meaningful output from upsc (and yes, it was on battery at this > point): > > battery.voltage: 38.70 > battery.voltage.nominal: 36.0 > beeper.status: enabled > device.mfr: > device.model: 2000VA UPS > device.type: ups > driver.name: blazer_usb > driver.parameter.langid_fix: 0x409 > driver.parameter.pollinterval: 2 > driver.parameter.port: foo > driver.parameter.productid: 0000 > driver.parameter.vendorid: 0001 > driver.version: 2.6.3 > driver.version.internal: 0.04 > input.current.nominal: 8.7 > input.frequency: 0.0 > input.frequency.nominal: 50 > input.voltage: 0.0 > input.voltage.fault: 0.0 > input.voltage.nominal: 230 > output.voltage: 227.0 > ups.delay.shutdown: 30 > ups.delay.start: 180 > ups.firmware: VER 40643U > ups.load: 3 > ups.mfr: > ups.model: 2000VA UPS > ups.productid: 0000 > ups.status: OB > ups.temperature: 28.0 > ups.type: offline / line interactive > ups.vendorid: 0001 > > However, none of the commands listed by upscmd actually seem to do > anything. I can't make it shut down, and even beeper.toggle doesn't seem > to do anything (whether it's on battery or not). > > [root@shinybook upsilon]# upscmd -l danubio > Instant commands supported on UPS [danubio]: > > beeper.toggle - Toggle the UPS beeper > load.off - Turn off the load immediately > load.on - Turn on the load immediately > shutdown.return - Turn off the load and return when power is back > shutdown.stayoff - Turn off the load and remain off > shutdown.stop - Stop a shutdown in progress > test.battery.start - Start a battery test > test.battery.start.deep - Start a deep battery test > test.battery.start.quick - Start a quick battery test > test.battery.stop - Stop the battery test
thanks for your report. part of the above command, and standard behavior, shutdown.* and load.* should at least be supported. could you please make the following test: - shutdown the computer and remove it from the UPS load, - restart everything, - stop upsmon, - stop the driver $ upsdrvctl stop - start the driver in debug $ /path/to/blazer_usb -DDDDD -a <devname> - in a separate console, launch some upscmd (load.*, shutdown.* or test.battery.start.*) and send me both the upscmd and driver outputs (compressed or offsite links please!) Testing the shutdown procedure is also welcome. cheers, Arnaud _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev