2012/5/3 David Woodhouse <[email protected]>:
> On Thu, 2012-05-03 at 19:00 +0200, Arnaud Quette wrote:
>>
>> could you please make the following test:
>> - shutdown the computer and remove it from the UPS load,
>> - restart everything,
>> - stop upsmon,
>> - stop the driver
>> $ upsdrvctl stop
>> - start the driver in debug
>> $ /path/to/blazer_usb -DDDDD -a <devname>
>> - in a separate console, launch some upscmd (load.*, shutdown.* or
>> test.battery.start.*)
>>
>> and send me both the upscmd and driver outputs (compressed or offsite
>> links please!)
>
> http://david.woodhou.se/blazer.txt
> http://david.woodhou.se/control.txt
>
>  19.469011     send: S00R0000
>  19.469093     read: S00R0000
>  19.469151     instcmd: command [load.off] handled
> …
>  43.884598     send: S.5R0000
>  43.884648     read: S.5R0000
>  43.884669     instcmd: command [shutdown.stayoff] handled
> …
>  60.970103     send: Q
>  61.357733     received 22 (22)
>  61.357785     read: UPS No Ack
>  61.745436     received 22 (22)
>  61.745491     read: UPS No Ack
>  62.133141     received 22 (22)
>  62.133190     read: UPS No Ack
>  62.520602     received 22 (22)
>  62.520652     read: UPS No Ack
>  62.908414     received 22 (22)
>  62.908468     read: UPS No Ack
>  63.295998     received 22 (22)
>  63.296017     read: UPS No Ack
>  63.683626     received 22 (22)
>  63.683682     read: UPS No Ack
>  64.071312     received 22 (22)
>  64.071380     read: UPS No Ack
>  64.458913     received 22 (22)
>  64.458966     read: UPS No Ack
>  64.846557     received 22 (22)
>  64.846613     read: UPS No Ack
>  64.846627     instcmd: command [beeper.toggle] handled
> …
>  85.755582     send: S.5R0003
>  85.755624     read: S.5R0003
>  85.755639     instcmd: command [shutdown.return] handled
> …
>  109.496753     send: T10
>  109.496769     read: T10
>  109.496782     instcmd: command [test.battery.start] handled
>
> No obvious reaction from the UPS at all, to any of the commands.

hem, well, I've not much to add!
apart that load.* and shutdown.* may require the UPS to be on battery
to actually work.
at the very least, SxxRxxxx (S for shutdown, R for restart, and xx for
delays), so load.* and shutdown.*, must be implemented.
if this last test fails, you should really get refunded.

cheers young dad ;-)
Arno

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to