Hallo list,
I encounter following problem using the liebert-esp2 driver with my
Liebert GXT2-3000RT230:
I use a standard serial cable with all pins connected, not a cable with
only pins 2,3,5 connected as mentioned in the ups-manual.
The UPS uses pins 4 and 6 in a special way (Pin 4(DTR) asserted
invokes the shutdown timer when ups is on battery, pin 6 to
ground-->any-mode shutdown).
Is it possible to make DTR continously non-asserted or must I cut the
wire or build a custom cable?
Since the DTR signal is continously asserted, the ups will shutdown 120
seconds after a powerfail, even if the power gets restored in this time.
I tried stty commands with no luck, i also tried to add
"ser_set_dtr(upsfd, 0);" into upsdrv_initups() without success.
thanks for help or tips,
Paul
some information:
statserial:
Device: /dev/ttyS4
Signal Pin Pin Direction Status Full
Name (25) (9) (computer) Name
----- --- --- --------- ------ -----
FG 1 - - - Frame Ground
TxD 2 3 out - Transmit Data
RxD 3 2 in - Receive Data
RTS 4 7 out 1 Request To Send
CTS 5 8 in 0 Clear To Send
DSR 6 6 in 1 Data Set Ready
GND 7 5 - - Signal Ground
DCD 8 1 in 1 Data Carrier Detect
DTR 20 4 out 1 Data Terminal Ready
RI 22 9 in 0 Ring Indicator
upsc:
battery.current: 0.00
battery.runtime: 3540
battery.runtime.low: 120
battery.temperature: 0.0
battery.voltage: 824.0
battery.voltage.nominal: 828.0
device.mfr: Liebert
device.model: GXT2-3000RT230
device.serial: 0323000167AF491
device.type: ups
driver.name: liebert-esp2
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS4
driver.version: 2.6.2
driver.version.internal: 0.03
input.bypass.current: 0.0
input.bypass.frequency: 50.0
input.bypass.voltage: 229.0
input.frequency: 50.0
input.frequency.nominal: 50.0
input.phases: 1
input.voltage: 229.0
output.current: 2.4
output.frequency: 50.0
output.frequency.nominal: 50.0
output.phases: 1
output.voltage: 230.4
ups.delay.start: 0
ups.firmware: GXT2MR15D-2K3K
ups.load: 17
ups.mfr: Liebert
ups.mfr.date: 15AUG03
ups.model: GXT2-3000RT230
ups.power: 513
ups.power.nominal: 3000
ups.realpower: 366
ups.serial: 0323000167AF491
ups.status: OL
ups.temperature: 39.5
ups.type: online
cat /proc/version
Linux version 3.1.10-1.9-desktop (geeko@buildhost) (gcc version 4.6.2
(SUSE Linux) ) #1 SMP PREEMPT Thu Apr 5 18:48:38 UTC 2012 (4a97ec8)
nut installed with rpm:
Information for package nut:
Name: nut
Version: 2.6.2-31.10
Arch: x86_64
Vendor: obs://build.opensuse.org/hardware
Installed: Yes
Status: up-to-date
Installed Size: 4.4 MiB
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev