Cyber Power Systems CP1000PFCLCD

= upsc output =

attached


= Shutdown results =

I experienced a genuine power outage shortly after setup. The 1 master system and the 1 slave system both shutdown successfully. The master shutdown before the slave (*not* a bug report; I may not have this configured correctly yet). The UPS was not powered off by the master. I don't know if the UPS supports that, or if I have that setup correctly either.

The shutdown command coincided with the UPS's own notion of "critical battery" (and associated beeping), which is about 2 minutes runtime remaining (I have about 36 minutes at my typical load). I don't think the UPS's critical level is adjustable.


= Product link =

http://www.cyberpowersystems.com/products/ups-systems/adaptive-sinewave-series/CP1000PFCLCD.html
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2220
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP1000PFCLCD
device.model: CRDA103-461
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.35
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 121.0
input.voltage.nominal: 120
output.voltage: 137.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 16
ups.mfr: CP1000PFCLCD
ups.model: CRDA103-461
ups.productid: 0501
ups.realpower.nominal: 600
ups.serial: CPS
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764