All,
I have built and installed nut from git on Archlinux. It uses the usbhid
driver. Beginning a couple of years ago, nut begin failing to run on Archlinux
without 'tweaking' or 'fudging' the install. There are two primary problems:
(1) upsdrvctl cannot be launched normally i.e. (/usr/sbin/upsdrvctl start)
without failing to connect:
Dec 14 02:24:39 phoinix systemd[1]: Starting Network UPS Tools - power device
driver controller...
Dec 14 02:24:39 phoinix systemd[1]: nut-driver.service: control process exited,
code=exited status=1
Dec 14 02:24:39 phoinix systemd[1]: Failed to start Network UPS Tools - power
device driver controller.
Dec 14 02:24:39 phoinix systemd[1]: Dependency failed for Network UPS Tools -
power devices information server.
Dec 14 02:24:39 phoinix systemd[1]: Unit nut-driver.service entered failed
state.
Dec 14 02:24:39 phoinix upsdrvctl[28629]: Network UPS Tools - Generic HID driver
0.38 (2.7.1-signed-9-g6fb35b3)
Dec 14 02:24:39 phoinix upsdrvctl[28629]: USB communication driver 0.32
Dec 14 02:24:39 phoinix upsdrvctl[28629]: No matching HID UPS found
Dec 14 02:24:39 phoinix upsdrvctl[28629]: Driver failed to start (exit status=1)
lsusb shows:
Bus 004 Device 002: ID 0764:0501 Cyber Power System, Inc. CP1500 AVR UPS
Fudging the options for upsdrvctl and limiting the start to one ups allows
upsdrvctl to find the ups device and works:
/usr/sbin/upsdrvctl -u root start phoinix_ups
(both -u root and the ups name are required before it will find the device)
(2) Starting upsdrvctl this way creates a problem with the GID of the files
created in /var/state/ups causing upsd to fail to connect to the ups device (at
least it starts without failing - in 2.6.x it would not start):
[02:47 phoinix:/var/state] # l ups
total 16
-rw-r--r-- 1 root root 6 Dec 14 02:36 upsd.pid
-rw-rw---- 1 root root 0 Dec 14 02:36 usbhid-ups-phoinix_ups
-rw-r--r-- 1 root root 6 Dec 14 02:36 usbhid-ups-phoinix_ups.pid
However, manually changing group ownership to root:nut and setting the setuid
and setgid bits allows upsd to start normally and preserves the setting across
reboot:
[02:47 phoinix:/var/state] # l ups
total 16
drwsrws--- 2 root nut 4096 Dec 14 02:36 .
drwxr-xr-x 3 root root 4096 Dec 14 02:06 ..
-rw-r--r-- 1 root nut 6 Dec 14 02:36 upsd.pid
srw-rw---- 1 root nut 0 Dec 14 02:36 usbhid-ups-phoinix_ups
-rw-r--r-- 1 root nut 6 Dec 14 02:36 usbhid-ups-phoinix_ups.pid
But these are still kludges to get nut to start and run properly. Why doesn't
"upsdrvctl start" allow nut to find the UPS when it can find it without a
problem with the options "-u root start <upsname>"? Second why doesn't nut
create the .pid files and the usbhid file with root:nut ownership?
These problems have been around a while. I used nut for a long time before
these problems popped up, and I would like to help get them solved. I know the
hotplugging, etc. causes problems, but it is hard to understand how it used to
work just fine and now doesn't. Let me know what else I can send, and I'm happy
to do it. The configure options used building nut were:
./autogen.sh
./configure \
--without-wrap \
--with-user=ups \
--with-group=nut \
--with-usb \
--with-cgi \
--prefix=/usr \
--sbindir=/usr/bin \
--datadir=/usr/share/ups \
--with-drvpath=/usr/bin \
--sysconfdir=/etc/ups \
--with-udev-dir=/usr/lib/udev \
--with-systemdsystemunitdir=/lib/systemd/system \
--with-cgipath=/srv/http/cgi-bin/nut \
--with-htmlpath=/srv/http/htdocs/nut
With the "fudges" it works:
03:15 phoinix:~/pkg/bld/network-ups-tools-git> upsc phoinix_ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1050
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 13.5
battery.voltage.nominal: 12
device.mfr: CPS
device.model: UPS CP1000AVRLCD
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/hiddev0
driver.version: 2.7.1-signed-9-g6fb35b3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 140
input.transfer.low: 90
input.voltage: 121.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 26
ups.mfr: CPS
ups.model: UPS CP1000AVRLCD
ups.productid: 0501
ups.realpower.nominal: 88
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764
--
David C. Rankin, J.D.,P.E.
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev