Charles,

Here is the output:

ugen1.3: <USB UPS PPC> at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON

  bLength = 0x0012
  bDescriptorType = 0x0001
  bcdUSB = 0x0200
  bDeviceClass = 0x0000
  bDeviceSubClass = 0x0000
  bDeviceProtocol = 0x0000
  bMaxPacketSize0 = 0x0008
  idVendor = 0x06da
  idProduct = 0x0005
  bcdDevice = 0x0003
  iManufacturer = 0x0003  <PPC>
  iProduct = 0x0001  <USB UPS>
  iSerialNumber = 0x0000  <no string>
  bNumConfigurations = 0x0001

I am running all the ups programs as root, i.e. "ps -aux" shows:

root 39901 0.0 0.0 22388 3860 ?? Is 12:57AM 0:00.00 /usr/local/bin/upslog -s UPSonic@localhost -l /var/log/ups.log -i 300 -u root root 39976 0.0 0.0 22392 3804 ?? Is 12:57AM 0:00.00 /usr/local/sbin/upsmon -u root localhost root 39978 0.0 0.0 22392 3900 ?? S 12:57AM 0:00.01 /usr/local/sbin/upsmon -u root localhost

The /var/log/ups.log does not have much in it either that
makes sense....maybe I need a utility to decode it?
Sample lines from the is file are:

20140131 103652 NA NA NA [NA] NA NA
20140131 103914 NA NA NA [NA] NA NA
20140131 103914 NA NA NA [NA] NA NA
20140131 104414 NA NA NA [NA] NA NA
20140131 104914 NA NA NA [NA] NA NA
20140131 105221 NA NA NA [NA] NA NA
20140131 105221 NA NA NA [NA] NA NA
20140131 105721 NA NA NA [NA] NA NA
20140131 110221 NA NA NA [NA] NA NA
20140131 110330 NA NA NA [NA] NA NA
20140131 110330 NA NA NA [NA] NA NA
20140131 110631 NA NA NA [NA] NA NA
20140131 110631 NA NA NA [NA] NA NA
20140131 110923 NA NA NA [NA] NA NA
20140131 110923 NA NA NA [NA] NA NA
20140131 111323 NA NA NA [NA] NA NA
20140204 092035 NA NA NA [NA] NA NA
20140204 092045 NA NA NA [NA] NA NA
20140204 092045 NA NA NA [NA] NA NA
20140204 092545 NA NA NA [NA] NA NA



On 2/3/14, 8:39 PM, Charles Lepple wrote:
On Feb 3, 2014, at 9:05 PM, Chris Duffy wrote:

Thx for the info Charles.

Here is what I am seeing from
'usbconfig list'
[...]
ugen1.3: <USB UPS PPC> at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON


The last line I guess is key.

Unfortunately, it is not very unique: the vendor can pick the string "USB UPS PPC", but the drivers match on the numeric IDs. Try 'usbconfig -d ugen1.3 dump_device_desc'

I did try all the diff combinations from the chart below
to no avail.....

"no avail" is not one of our error messages... I just checked :-)

What was the error message from blazer_usb?

and they are using a USB cable/port.....

see below.

Thx for any leads.

Chris


On 1/31/14, 6:17 PM, Charles Lepple wrote:
On Jan 31, 2014, at 3:14 PM, Chris Duffy wrote:

The current one I am looking is support for:

*Upsonic Commercial UPS CXR 2000 - 2000VA/1200W - Rack/Tower*

What seems to be supported in Freebsd is:

Small clarification: the hardware compatibility list isn't broken down by operating system (theoretically, the drivers should work on any POSIX system, with additional dependencies for USB).


CXR1000
        blazer_ser
LAN Saver 600
        genericups upstype=0
Power Guardian
        genericups upstype=7
PrOffice 650
USB     blazer_usb
DS-800
USB     blazer_usb



we tried these but not much luck according to my customer.
Has anyone got this one to work on Freebsd and
what is needed for the config?

In general, permissions on device nodes aren't set up automatically in FreeBSD. In particular, the USB nodes aren't writable by the default system username for NUT (uucp), so you probably will need to make a change to devd.conf.

Given the usbconfig output above, you will either need to run the driver as root ("-u root" on the command line) or change the permissions ("chown uucp /dev/usb/1.3.*"). The /dev filesystem is volatile, so this will reset itself on the next boot.

--
Charles Lepple
clepple@gmail





_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to