On Feb 19, 2014, at 12:50 PM, Ted Mittelstaedt wrote: > Worse, however, is if there's a power failure right near the end > of the 2-days-off cycle. That happened to me last week - it was a > short duration 15 second loss - and the upscode2 driver decided it needed to > issue a forced shutdown. > > Very likely this was because upscode2 had decided the batteries > were dangerously low discharged. But they were NOT discharged and > easily kept the servers up and online.
As far as I can tell, the upscode2 driver does not use the battery voltage to determine when to shut down - it uses one of the UPS status bits from the STAT or STMF responses. We have a few other drivers that calculate a cosmetic state-of-charge, and off the top of my head, the drivers have parameters to adjust for the variations in voltages sensed by the UPS. That's certainly a possible improvement for this driver, but I don't think it is going to fix the internal UPS determination of whether the battery is low. -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev