On 2/20/2014 6:55 AM, Charles Lepple wrote:
On Feb 19, 2014, at 12:50 PM, Ted Mittelstaedt wrote:
Worse, however, is if there's a power failure right near the end of
the 2-days-off cycle. That happened to me last week - it was a
short duration 15 second loss - and the upscode2 driver decided it
needed to issue a forced shutdown.
Very likely this was because upscode2 had decided the batteries
were dangerously low discharged. But they were NOT discharged and
easily kept the servers up and online.
As far as I can tell, the upscode2 driver does not use the battery
voltage to determine when to shut down - it uses one of the UPS
status bits from the STAT or STMF responses.
Really! I was afraid of that. With this blip, this is what
upslog was showing:
20140212 032546 65.9 119.30 60.9 [OL] NA NA
20140212 032626 62.8 119.10 55.5 [FSD OL] NA NA
20140212 043722 NA NA NA [WAIT] NA NA
20140212 044222 67.7 118.90 54.4 [OL] NA NA
20140212 044722 65.9 119.20 52.4 [OL] NA NA
The blip obviously took place between 3:25:46 and
3:26:26, I was lucky that upslog caught it then. You
can see the calculated state of charge going to 62.8% so
the battery voltage probably hit 48 volts at that time -
and I'm assuming the UPS considered the batteries in imminent
danger of failing - I guess - even though they weren't.
I did a battery replacement on this UPS about 8 months ago,
I wonder if the batteries I used have a slightly lower run
voltage than what the UPS was calibrated for?
What I don't understand exactly is why FSD and OL were _both_
showing in the status?
That's forced shutdown, I believe and online at the same time?!?
We have a few other drivers that calculate a cosmetic
state-of-charge, and off the top of my head, the drivers have
parameters to adjust for the variations in voltages sensed by the
UPS. That's certainly a possible improvement for this driver, but I
don't think it is going to fix the internal UPS determination of
whether the battery is low.
Well, do you think my patch logic makes sense? From the looks of
it the upscode2 protocol is obsolete and was not used by many
UPSes (and most likely most of those are being retired) and
more modern UPSes have their own logic to calculate battery state
of charge that is much better than having the driver do it. But
this may help someone else who is dealing with one of these.
is there anyway to delay how long NUT reacts to an FSD from the
driver? Since with a little blip like this lasting less than a
minute, my preference is to NOT shut any of the servers down but
to let it ride.
I also suggest the following patch to upslog.c (little line wrapping there)
--- upslog.c.orig 2012-07-31 10:38:58.000000000 -0700
+++ upslog.c 2014-02-20 09:23:14.000000000 -0800
@@ -50,6 +50,7 @@
static flist_t *fhead = NULL;
#define DEFAULT_LOGFORMAT "%TIME @Y@m@d @H@M@S% %VAR battery.charge% " \
+ "%VAR battery.voltage% %VAR output.current% " \
"%VAR input.voltage% %VAR ups.load% [%VAR ups.status%] " \
"%VAR ups.temperature% %VAR input.frequency%"
Mainly because the only real indicator of true battery health with this
UPS is the voltage off the battery bank.
Ted
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev