Now tackling sending the UPS commands to have it turn off and back on (with 
some delay), I'm just putting this out there to make sure I'm on the right 
track.  I want to design this to be as close as possible to "industry 
standard", or at least concensus.

Looking through the other HU_TYPE_CMDs out there, it seems that most UPSs use 
"UPS.PowerSummary.DelayBeforeShutdown" for load.off.delay, and 
"UPS.PowerSummary.DelayBeforeStartup" for load.on.delay.  Belkin appears to use 
custom codes (reserved for vendors), which I know I could do, but guess I don't 
see the reason for doing so yet.

So basically, when someone uses load.off.delay as a command to the UPS, then 
the value they pass through is how many seconds they want the UPS to wait 
before disconnecting the power to the CPU.  That is the time in which you HOPE 
the system shuts down successfully.

You also (can) pass in load.on.delay, which should be a value larger than 
load.off.delay.  That tells the UPS that even if wall power comes back, do not 
switch on the UPS load until X seconds have passed.  This makes sure the system 
has fully shut down, and power is removed...before it is applied again.  This 
ensures that the system will startup again.

Have I got the right idea?  It seems like those two commands will take care of 
most I need to have the UPS do.