Below the answers: > This is the same as https://github.com/networkupstools/nut/issues/254 , right?
Yes, this UPS is the same. > Does battery.runtime only get updated when on battery power, or is this with > a different load? > battery.runtime.low: 59940 > battery.temperature: 00 Yes, this time time is updated on battery power, This is a dynamic counter that changes with a different load. > Is this fixed at 0, or is there a temperature option? In this case, this UPS doesn't have a temperature sensor, therefore this value is equal zero. > battery.voltage: 163.4 > device.mfr: NHS Sistemas de Energia > device.model: Laser Senoidal 5000VA > device.type: ups > driver.name: gamatronic > driver.parameter.pollinterval: 20 > driver.parameter.port: /dev/ttyACM2 > driver.version: 2.6.3 > driver.version.internal: 0.02 > input.frequency: 59.9 > input.transfer.high: 144 > input.transfer.low: 096 > input.voltage: 127.6 > input.voltage.nominal: 120 > output.current: 0.0 > output.frequency: 60.0 > output.voltage: 119.1 > ups.firmware: LSPWM(15).55 > ups.id: ny7bd8723tbecabc > ups.load: 000 > ups.mfr: NHS Sistemas de Energia > ups.model: Laser Senoidal 5000VA > ups.power.nominal: 05000 > ups.status: OL > > > > Below the "upsc" command when the UPS is on battery without input (input bad): > > > battery.charge: 100 > battery.current: 0.0 > battery.date: 12292015 > battery.runtime: 00076 > battery.runtime.low: 59940 > This seems rather high. This variable is supposed to represent the runtime > [in seconds] below which the UPS will signal "LB", but this capture only > shows "OB". > battery.temperature: 00 > battery.voltage: 155.9 > device.mfr: NHS Sistemas de Energia > device.model: Laser Senoidal 5000VA > device.type: ups > driver.name: gamatronic > driver.parameter.pollinterval: 20 > driver.parameter.port: /dev/ttyACM2 > driver.version: 2.6.3 > driver.version.internal: 0.02 > input.frequency: 0.0 > input.transfer.high: 144 > input.transfer.low: 096 > input.voltage: 0.0 > input.voltage.nominal: 120 > output.current: 0.0 > output.frequency: 60.0 > output.voltage: 119.7 > ups.alarm: Input Bad > ups.firmware: LSPWM(15).55 > ups.id: ny7bd8723tbecabc > ups.load: 000 > ups.mfr: NHS Sistemas de Energia > ups.model: Laser Senoidal 5000VA > ups.power.nominal: 05000 > ups.status: ALARM OB This value is high because we don't have a load in the output of the UPS, therefore, with this load the time until the UPS achieve the low battery status is 59940 seconds. Best Regards. ----------------------------------------------------------- Thiago Wiezbicki NHS Sistemas de Energia Av. Juscelino Kubitschek de Oliveira, 5270 Cidade Industrial - Curitiba - PR Fone/Fax: +55 41 2141-9262 http://www.nhs.com.br _______________________________________________ Nut-upsdev mailing list Nut-upsdev@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev