I wasn't clear. 

battery.runtime.low is not a counter, but a value estimated in seconds that is 
decreasing conforming the battery is discharging. It's mean: How much time (in 
seconds) will be necessary until the battery achieve the depleted status ( 
http://www.networkupstools.org/protocols/sec.html#Estimated_Minutes ) . If the 
UPS don't have a load, this value will be higher than the value when the UPS 
have 100% of load. 

The battery.run.low is not related with battery.runtime this is important 
explain. Battery.runtime will count in seconds 
(http://www.networkupstools.org/protocols/sec.html#Seconds_on_Battery) how much 
time the UPS is in the Battery status and doesn't depend of load or other 
parameter as battery.run.low depends.

battery.run.low is a dynamic timer, initially without a load in UPS it will be 
a high seconds estimator. It will change dynamically conforms I can increase 
the UPS load or not. It's a value calculated from the UPS to notice the User 
how much time he have until the UPs battery achieve the depleted status.

The battery.run.low can be higher than battery.runtime, do you agree?


----------------------------------------------------------- 
Thiago Wiezbicki 
NHS Sistemas de Energia 
Av. Juscelino Kubitschek de Oliveira, 5270 
Cidade Industrial - Curitiba - PR 
Fone/Fax: +55 41 2141-9262 
http://www.nhs.com.br

----- Mensagem original -----
De: "Charles Lepple" <[email protected]>
Para: "Thiago Wiezbicki - NHS" <[email protected]>
Cc: "nut-upsdev" <[email protected]>
Enviadas: Sábado, 9 de janeiro de 2016 19:41:09
Assunto: Re: [Nut-upsdev] [HCL] NHS Laser Senoidal 5000VA supported by 
gamatronic

On Jan 8, 2016, at 7:09 AM, Thiago Wiezbicki - NHS 
<[email protected]> wrote:
> 
>>> battery.runtime: 00076
>>> battery.runtime.low: 59940
>> 
>> This seems rather high. This variable is supposed to represent the runtime 
>> [in seconds] below which the UPS will signal "LB", but this capture only 
>> shows "OB".
> 
> This value is high because we don't have a load in the output of the UPS, 
> therefore, with this load the time until the UPS achieve the low battery 
> status is 59940 seconds.

I admit that the documentation is not clear that battery.runtime.low should be 
a configuration value, rather than a counter.

However, I am still confused as to why the runtime.low number is larger than 
runtime (which would be the time until the battery is completely empty, versus 
just low).

Since this might be hard to work around with the current driver, we can put a 
note in the DDL, but at this point I don't know what the note should say.

-- 
Charles Lepple
clepple@gmail