Here is another XS model:
[root@sampson log]# upsrw apc@localhost
[input.sensitivity]
Input power sensitivity
Type: STRING
Value: medium
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 139
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 88
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20
[root@sampson log]# upsc apc@localhost
battery.charge: 100
battery.charge.low: 15
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2017/04/26
battery.runtime: 2154
battery.runtime.low: 300
battery.type: PbAc
battery.voltage: 27.2
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Back-UPS XS 1300G
device.serial: 4B1717P20965
device.type: ups
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.serial: 4B1717P20965
driver.parameter.vendorid: 051d
driver.version: 2.6.5
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
input.sensitivity: medium
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 116.0
input.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 864.L9 .D
ups.firmware.aux: L9
ups.load: 16
ups.mfr: American Power Conversion
ups.mfr.date: 2017/04/26
ups.model: Back-UPS XS 1300G
ups.productid: 0002
ups.realpower.nominal: 780
ups.serial: 4B1717P20965
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d
On Wed, Jan 2, 2019 at 9:08 AM, Charles Lepple <[email protected]>
wrote:
Given that we don't have a Back-UPS NS in the compatibility list, and
that you have two of the three categories of information on the list
already, would you mind if we added this to the DDL? The output of
upsrw would be useful for completeness. Also, if you know any of the
values from upsc are incorrect, we can note that. For instance, I'm
assuming that "battery.date" is incorrect, and the real dates are
under "battery.mfr.date" and "ups.mfr.date". Other reports:
http://new.networkupstools.org/ddl/APC/
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser