On Jun 10, 2019, at 2:32 PM, Marc Finns wrote: > > Hello, I read all FAQ and other sources but I could not find this situation, > so I thought of asking the experts. > I successfully configured a Raspberry NUT server to control my UPS that > powers several devices (NUC with ESXI VMs, Synology NAS etc). > All works well in principle, but I have the following behaviours that I could > not find described anywhere. > • When power returns after the system has shuts down because of battery > flat, all restarts immediately. However, as soon as NUT server reboots, it > switches the UPS to battery till it dies – even if line is present
This is FAQ #49: https://networkupstools.org/docs/FAQ.html#_my_ups_powers_up_immediately_after_a_power_failure_instead_of_waiting_for_the_batteries_to_recharge > • If power returns after the system has started the shutdown sequence, > the UPS does not return to AC mode and stays on battery till it dies. This is FAQ #51: https://networkupstools.org/docs/FAQ.html#_the_power_came_back_during_the_shutdown_but_before_the_ups_power_off_now_the_ups_does_not_reboot_and_my_computer_stays_off_how_can_i_fix_that These are subtle edge cases, but apparently a lot of entry-level UPS models omit the interface to control these two situations. As mentioned in both of the FAQ explanations, you can work around this in software, or you can sell the UPS to someone who annoys you, and look for one that provides the "battery.charge.restart" NUT variable (Minimum battery level for UPS restart after power-off) and the "shutdown.return" instant command. In both cases, we have tried to collect NUT variable dumps and command listings from NUT users here: https://networkupstools.org/ddl/ Note that this information is best-effort, and sometimes vendors change the underlying firmware without changing the model name. There is no substitute for testing when it comes to shutdown procedures, unfortunately. (If you get an error from the mailing list about the message size, please try turning off HTML posting, and gzip any log files.) > > Therefore, behaviour (1) creates a dangerous endless loop where power > returns, all boots, after 30 sec power is brutally cut, and so on. The net > result is that I already killed a disk. > Please note: I never had this behaviour when I used the Synology as network > UPS server. > Is anyone having the same / having a suggestion? > Thanks a million. Marc. > > Hardware: Raspberry PI > OS name and version: Raspbian (Linux raspberrypi 4.19.42-v7+ #1219 SMP Tue > May 14 21:20:58 BST 2019 armv7l GNU/Linux) > NUT version 2.7.4 installed from repo > UPS: APS Back-UPS RS 550G > Driver configuration: > [ups] > driver = usbhid-ups > port = auto > desc = "Back-UPS RS 550G" > ignorelb > override.battery.charge.low = 20 > override.battery.runtime.low = 200 > pollfreq = 15 > > Output of /lib/nut/usbhid-ups -DD -a ups > Network UPS Tools - Generic HID driver 0.41 (2.7.4) > USB communication driver 0.33 > 0.000000 debug level is '2' > 0.004536 upsdrv_initups... > 0.006506 Checking device (051D/0002) (001/004) > 0.009744 - VendorID: 051d > 0.009826 - ProductID: 0002 > 0.010240 - Manufacturer: American Power Conversion > 0.010866 - Product: Back-UPS RS 550G FW:857.L5 .I USB FW:L5 > 0.011214 - Serial Number: 3B1547X04970 > 0.011271 - Bus: 001 > 0.011768 - Device release number: 0090 > 0.011822 Trying to match device > 0.012248 Device matches > 0.013822 HID descriptor length 1134 > 0.016761 Report Descriptor size = 1134 > 0.019750 Using subdriver: APC HID 0.96 > 0.019824 112 HID objects found > 0.020801 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, > Offset: 0, Size: 8, Value: 2 > 0.021529 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: > 0x02, Offset: 0, Size: 8, Value: 3 > 0.022404 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, > ReportID: 0x03, Offset: 0, Size: 8, Value: 4 > 0.023913 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, > ReportID: 0x04, Offset: 0, Size: 8, Value: 1 > 0.025154 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: > 0x05, Offset: 0, Size: 8, Value: 1 > 0.026405 Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, > Offset: 0, Size: 8, Value: 1 > 0.027244 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, > Offset: 0, Size: 8, Value: 1 > 0.028082 Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: > 0x06, Offset: 8, Size: 8, Value: 0 > 0.028965 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: > 0x06, Offset: 8, Size: 8, Value: 0 > 0.029785 Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: > 0x06, Offset: 16, Size: 8, Value: 8 > 0.030618 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: > 0x06, Offset: 16, Size: 8, Value: 8 > 0.031914 Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, > ReportID: 0x07, Offset: 0, Size: 16, Value: 18290 > 0.033288 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: > 0x08, Offset: 0, Size: 16, Value: 12 > 0.034536 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x09, > Offset: 0, Size: 16, Value: 12.59 > 0.035776 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: > 0x0a, Offset: 0, Size: 8, Value: 1 > 0.037025 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: > 0x0b, Offset: 0, Size: 8, Value: 2 > 0.038282 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, > ReportID: 0x0c, Offset: 0, Size: 8, Value: 18 > 0.039169 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, > ReportID: 0x0c, Offset: 0, Size: 8, Value: 18 > 0.040008 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: > 0x0c, Offset: 8, Size: 16, Value: 262 > 0.040842 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: > 0x0c, Offset: 8, Size: 16, Value: 262 > 0.042150 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: > 0x0d, Offset: 0, Size: 8, Value: 100 > 0.043790 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, > ReportID: 0x0e, Offset: 0, Size: 8, Value: 100 > 0.045030 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, > ReportID: 0x0f, Offset: 0, Size: 8, Value: 50 > 0.046289 Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, > ReportID: 0x10, Offset: 0, Size: 8, Value: 1 > 0.047658 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, > ReportID: 0x11, Offset: 0, Size: 8, Value: 10 > 0.048905 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, > ReportID: 0x12, Offset: 0, Size: 8, Value: 1 > 0.050153 Path: UPS.PowerSummary.ACPresent, Type: Input, ReportID: 0x13, > Offset: 0, Size: 8, Value: 1 > 0.050693 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: > 0x13, Offset: 0, Size: 8, Value: 1 > 0.051529 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: > Input, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 > 0.051760 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: > Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 > 0.052150 Path: UPS.PowerSummary.ShutdownImminent, Type: Input, ReportID: > 0x14, Offset: 8, Size: 8, Value: 0 > 0.052536 Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, > ReportID: 0x14, Offset: 8, Size: 8, Value: 0 > 0.053409 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, > ReportID: 0x15, Offset: 0, Size: 16, Value: -1 > 0.054039 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, > ReportID: 0x16, Offset: 0, Size: 1, Value: 1 > 0.054279 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, > ReportID: 0x16, Offset: 0, Size: 1, Value: 1 > 0.054497 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, > ReportID: 0x16, Offset: 1, Size: 1, Value: 0 > 0.054959 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: > Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 > 0.055360 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, > ReportID: 0x16, Offset: 2, Size: 1, Value: 1 > 0.055752 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, > ReportID: 0x16, Offset: 2, Size: 1, Value: 1 > 0.056148 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: > Input, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 > 0.056541 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: > Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 > 0.056957 Path: > UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, > ReportID: 0x16, Offset: 4, Size: 1, Value: 0 > 0.057713 Path: > UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, > ReportID: 0x16, Offset: 4, Size: 1, Value: 0 > 0.059206 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: > Input, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 > 0.059435 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: > Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 > 0.059909 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, > Type: Input, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 > 0.060331 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, > Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 > 0.060733 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: > Input, ReportID: 0x16, Offset: 7, Size: 1, Value: 0 > 0.060957 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: > Feature, ReportID: 0x16, Offset: 7, Size: 1, Value: 0 > 0.061353 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: > Input, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 > 0.061752 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: > Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 > 0.062147 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, > ReportID: 0x16, Offset: 9, Size: 1, Value: 0 > 0.062550 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, > ReportID: 0x16, Offset: 9, Size: 1, Value: 0 > 0.063188 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: > Input, ReportID: 0x16, Offset: 10, Size: 1, Value: 0 > 0.063408 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: > Feature, ReportID: 0x16, Offset: 10, Size: 1, Value: 0 > 0.064299 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, > ReportID: 0x17, Offset: 0, Size: 16, Value: 120 > 0.065154 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.065791 Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: > 0x1c, Offset: 0, Size: 24, Value: 599297 > 0.066410 Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: > 0x20, Offset: 0, Size: 16, Value: 19752 > 0.067027 Path: UPS.Battery.Test, Type: Input, ReportID: 0x21, Offset: 0, > Size: 8, Value: 6 > 0.067247 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: > 0, Size: 8, Value: 6 > 0.067906 Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID: > 0x22, Offset: 0, Size: 8, Value: 18 > 0.068533 Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: > 0x23, Offset: 0, Size: 16, Value: 262 > 0.069157 Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID: > 0x24, Offset: 0, Size: 16, Value: 120 > 0.069783 Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, > Offset: 0, Size: 16, Value: 12 > 0.070424 Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, > Offset: 0, Size: 16, Value: 12.59 > 0.071043 Path: UPS.Battery.ff860024, Type: Feature, ReportID: 0x27, > Offset: 0, Size: 16, Value: 247 > 0.071667 Path: UPS.Battery.ff860018, Type: Feature, ReportID: 0x28, > Offset: 0, Size: 32, Value: -1.34135e+09 > 0.072280 Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, > Offset: 0, Size: 8, Value: 230 > 0.072912 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: > 0, Size: 16, Value: 235 > 0.073536 Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: > 0x32, Offset: 0, Size: 16, Value: 176 > 0.074160 Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: > 0x33, Offset: 0, Size: 16, Value: 282 > 0.074783 Path: UPS.Input.ff860024, Type: Feature, ReportID: 0x34, > Offset: 0, Size: 16, Value: 128 > 0.075399 Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, > Offset: 0, Size: 8, Value: 1 > 0.076023 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: > 0x36, Offset: 0, Size: 8, Value: 0 > 0.076649 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: > Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 > 0.077279 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: > Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 > 0.077902 Path: UPS.APCGeneralCollection.DelayBeforeShutdown, Type: > Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: -1 > 0.078529 Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: > 0x50, Offset: 0, Size: 8, Value: 26 > 0.079478 Path: UPS.PowerConverter.ff860024, Type: Feature, ReportID: > 0x51, Offset: 0, Size: 8, Value: 226 > 0.080454 Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, > ReportID: 0x52, Offset: 0, Size: 16, Value: 330 > 0.081163 Path: UPS.ff860001.ff860023, Type: Feature, ReportID: 0x60, > Offset: 0, Size: 16, Value: 0 > 0.081788 Path: UPS.ff860001.ff860026, Type: Feature, ReportID: 0x61, > Offset: 0, Size: 8, Value: 138 > 0.082900 Path: UPS.ff860001.ff860025, Type: Feature, ReportID: 0x62, > Offset: 0, Size: 32, Value: 5.0463e+07 > 0.083531 Path: UPS.iProduct, Type: Feature, ReportID: 0x7f, Offset: 0, > Size: 8, Value: 5 > 0.084150 Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, ReportID: > 0x7e, Offset: 0, Size: 8, Value: 7 > 0.084774 Path: UPS.iSerialNumber, Type: Feature, ReportID: 0x7d, Offset: > 0, Size: 8, Value: 3 > 0.085397 Path: UPS.iManufacturer, Type: Feature, ReportID: 0x7c, Offset: > 0, Size: 8, Value: 1 > 0.086029 Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, > Offset: 0, Size: 16, Value: 18290 > 0.086659 Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: > 0x7a, Offset: 0, Size: 1, Value: 1 > 0.086916 Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: > 0x7a, Offset: 1, Size: 1, Value: 0 > 0.087155 Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: > 0x7a, Offset: 2, Size: 1, Value: 1 > 0.087368 Path: UPS.PresentStatus.BatteryPresent, Type: Feature, > ReportID: 0x7a, Offset: 3, Size: 1, Value: 1 > 0.087585 Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: > Feature, ReportID: 0x7a, Offset: 4, Size: 1, Value: 0 > 0.087804 Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, > ReportID: 0x7a, Offset: 5, Size: 1, Value: 0 > 0.088017 Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: > Feature, ReportID: 0x7a, Offset: 6, Size: 1, Value: 0 > 0.088231 Path: UPS.PresentStatus.CommunicationLost, Type: Feature, > ReportID: 0x7a, Offset: 7, Size: 1, Value: 0 > 0.088447 Path: UPS.PresentStatus.NeedReplacement, Type: Feature, > ReportID: 0x7a, Offset: 8, Size: 1, Value: 0 > 0.088668 Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: > 0x7a, Offset: 9, Size: 1, Value: 0 > 0.088887 Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, > ReportID: 0x7a, Offset: 10, Size: 1, Value: 0 > 0.089537 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: > 0, Size: 8, Value: 0 > 0.090152 Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x78, > Offset: 0, Size: 8, Value: 1 > 0.090785 Path: UPS.ff860029, Type: Feature, ReportID: 0x75, Offset: 0, > Size: 16, Value: 98 > 0.092051 Path: UPS.ff86002a, Type: Feature, ReportID: 0x74, Offset: 0, > Size: 32, Value: 3.0318e+08 > 0.092948 Path: UPS.ff860090.ff860091, Type: Feature, ReportID: 0x8c, > Offset: 0, Size: 8, Value: 1 > 0.093576 Path: UPS.ff860090.ff860092, Type: Feature, ReportID: 0x8d, > Offset: 0, Size: 8, Value: 25 > 0.094305 Path: UPS.ff860090.ff860093, Type: Feature, ReportID: 0x8e, > Offset: 0, Size: 8, Value: 36 > 0.094758 Path: UPS.ff860090.ff860094, Type: Feature, ReportID: 0x8f, > Offset: 0, Size: 8, Value: 0 > 0.095293 Path: UPS.ff860090.ff860095, Type: Feature, ReportID: 0x90, > Offset: 0, Size: 8, Value: 1 > 0.095763 Path: UPS.ff860090.ff860096, Type: Feature, ReportID: 0x91, > Offset: 0, Size: 16, Value: 4 > 0.096259 Path: UPS.ff860090.ff860097, Type: Feature, ReportID: 0x92, > Offset: 0, Size: 16, Value: 4 > 0.096757 Path: UPS.00000000.ff000055, Type: Feature, ReportID: 0x80, > Offset: 0, Size: 8, Value: 0 > 0.096884 Report descriptor retrieved (Reportlen = 1134) > 0.096919 Found HID device > 0.096954 Detected a UPS: American Power Conversion/Back-UPS RS 550G > FW:857.L5 .I USB FW:L5 > 0.097057 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, > ReportID: 0x0c, Offset: 0, Size: 8, Value: 18 > 0.097169 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, > ReportID: 0x0f, Offset: 0, Size: 8, Value: 50 > 0.097273 Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: > 0x23, Offset: 0, Size: 16, Value: 262 > 0.097423 Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, > Offset: 0, Size: 16, Value: 12.59 > 0.097553 Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, > Offset: 0, Size: 16, Value: 12 > 0.097676 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, > ReportID: 0x03, Offset: 0, Size: 8, Value: 4 > 0.098542 Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: > 0x20, Offset: 0, Size: 16, Value: 19752 > 0.098659 Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: > 0x1c, Offset: 0, Size: 24, Value: 599297 > 0.098762 Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: > 0x50, Offset: 0, Size: 8, Value: 26 > 0.098951 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, > ReportID: 0x15, Offset: 0, Size: 16, Value: -1 > 0.099201 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: > Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 > 0.099280 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: > 0, Size: 8, Value: 6 > 0.099361 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.099448 Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, > Offset: 0, Size: 16, Value: 18290 > 0.099551 Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, > ReportID: 0x52, Offset: 0, Size: 16, Value: 330 > 0.099663 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, > ReportID: 0x16, Offset: 2, Size: 1, Value: 1 > 0.099740 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: > Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 > 0.099817 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, > ReportID: 0x16, Offset: 0, Size: 1, Value: 1 > 0.099889 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: > Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 > 0.099964 Path: > UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, > ReportID: 0x16, Offset: 4, Size: 1, Value: 0 > 0.100036 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, > ReportID: 0x16, Offset: 9, Size: 1, Value: 0 > 0.100118 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: > Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 > 0.100193 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, > Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 > 0.100274 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: > Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 > 0.100346 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, > Offset: 0, Size: 8, Value: 1 > 0.100415 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: > 0x06, Offset: 8, Size: 8, Value: 0 > 0.100485 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: > 0x13, Offset: 0, Size: 8, Value: 1 > 0.100555 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: > Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 > 0.100621 Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, > ReportID: 0x14, Offset: 8, Size: 8, Value: 0 > 0.100685 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: > 0x06, Offset: 16, Size: 8, Value: 8 > 0.100754 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: > 0x36, Offset: 0, Size: 8, Value: 0 > 0.100829 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: > 0x36, Offset: 0, Size: 8, Value: 0 > 0.100898 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: > 0, Size: 16, Value: 235 > 0.100980 Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, > Offset: 0, Size: 8, Value: 230 > 0.101103 Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: > 0x32, Offset: 0, Size: 16, Value: 176 > 0.101197 Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: > 0x33, Offset: 0, Size: 16, Value: 282 > 0.101277 Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, > Offset: 0, Size: 8, Value: 1 > 0.101492 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: > 0, Size: 8, Value: 6 > 0.101581 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: > 0, Size: 8, Value: 6 > 0.101668 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: > 0, Size: 8, Value: 6 > 0.101735 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: > 0, Size: 8, Value: 0 > 0.101803 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: > 0, Size: 8, Value: 0 > 0.101914 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, > ReportID: 0x15, Offset: 0, Size: 16, Value: -1 > 0.102004 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, > ReportID: 0x15, Offset: 0, Size: 16, Value: -1 > 0.102169 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: > Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 > 0.102249 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: > Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 > 0.102311 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: > Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 > 0.102403 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.102478 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.102556 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.102625 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.102696 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, > ReportID: 0x18, Offset: 0, Size: 8, Value: 1 > 0.102831 find_nut_info: unknown info type: load.on.delay > 0.102880 find_nut_info: unknown info type: load.on.delay > 0.102946 upsdrv_initinfo... > 0.102995 upsdrv_updateinfo... > 0.103404 Got 2 HID objects... > 0.103475 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, > ReportID: 0x0c, Offset: 0, Size: 8, Value: 18 > 0.103552 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: > 0x0c, Offset: 8, Size: 16, Value: 262 > 0.103596 Quick update... _______________________________________________ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser