On Jun 11, 2019, at 1:37 AM, Marc Finns wrote:
> 
> Thanks for the reply. However these two FAQ are unfortunately not describing 
> the situation. 
> - The first issue is that NUT switches off the UPS upon reboot on low battery 
> (not that it dies because of low battery)
> - The second issue is that the UPS does not recognise being online again (not 
> that the PC does not restart)

My apologies, I misinterpreted "UPS does not return to AC mode" as the UPS AC 
output, and did not carefully read the first issue.

However, I still maintain that there are a few features missing from this class 
of UPS (or they are mapped to proprietary APC HID usages). It is possible that 
the Synology shutdown strategy is using a different command.

With the devices powered from something other than the UPS under test, can you 
grab a log from something like "/lib/nut/usbhid-ups -DDD -a ups -k 2>&1 | tee 
/tmp/APC_Back-UPS_RS_550G_shutdown.txt"? The usbhid-ups driver selects one of 
several shutdown commands, and I think we will need at least 3x -D to see that 
logic in the debug output. Please gzip the log before emailing
_______________________________________________