I see, so you kept the load.on.delay command but removed the check to see if it was handled. Did you do the same thing for the shutdown.stayoff logic?
https://github.com/networkupstools/nut/blob/master/drivers/usbhid-ups.c#L562 This might be a dumb question but did this require you to recompile the kernel? These types of changes are way beyond my depth. Thank you for the direction! On Thu, Jan 2, 2020, 11:38 AM Ken Olum <[email protected]> wrote: > Hi, Layne. I had a similar problem with my Tripp-Lite BCPERS450. You > can see the previous correspondence by searching for > > site:alioth-lists.debian.net/pipermail/nut-upsuser BCPERS450 shutdown > > with Google. > > In particular, I fixed (well, worked around) the problem, as I wrote in > > https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-March/011082.html > > I've been running with this code for nearly 2 years now, and it seems to > work. So maybe it could be adopted into the source in some way. > > Ken >
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser