When running 'sudo upsmon -c fsd' UPS turns off then back on after a delay
as expected. But when power is disconnected and the command is ran, the UPS
turns off but still turns back on again.

Changing 'ondelay' to -1 or 0 does not change the behavior.

How can I get the UPS load to stay turned off if there is no power? Or am I
misunderstanding how to test this functionality?

------------------------------

OS - Raspbian GNU/Linux 10 (buster)
Kernel - 4.19.75-v7+
Nut version - 2.7.4-8
Installation method - From package
UPS - Tripp Lite SMART1500LCD

------------------------------

# /etc/nut/ups.conf

pollinterval = 1

[ups]
driver = usbhid-ups
port = auto
desc = "Tripp Lite SMART1500LCD"
vendorid = 09ae
productid = 2012
ondelay = -1

------------------------------

# /etc/udev/rules.d/62-nut-usbups.rules

SUBSYSTEM!="usb", GOTO="nut-usbups_rules_end"

# TrippLite
#  e.g. TrippLite SMART1500LCD - usbhid-ups
ACTION=="add|change", SUBSYSTEM=="usb|usb_device",
SUBSYSTEMS=="usb|usb_device", ATTR{idVendor}=="09ae",
ATTR{idProduct}=="2012", MODE="664", GROUP="nut", RUN+="/sbin/upsdrvctl
stop; /sbin/upsdrvctl start"

LABEL="nut-usbups_rules_end"

------------------------------

pi@rpi:~ $ upsc ups
Init SSL without certificate database
battery.charge: 100
battery.runtime: 3840
battery.type: PbAC
battery.voltage: 27.1
battery.voltage.nominal: 24.0
device.mfr: Tripp Lite
device.model: Tripp Lite UPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: -1
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 1
driver.parameter.port: auto
driver.parameter.productid: 2012
driver.parameter.synchronous: no
driver.parameter.vendorid: 09ae
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 59.8
input.voltage: 112.5
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage: 112.4
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 30
ups.load: 0
ups.mfr: Tripp Lite
ups.model: Tripp Lite UPS
ups.power: 0.0
ups.power.nominal: 1500
ups.productid: 2012
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0

------------------------------

pi@rpi:~ $ sudo /lib/nut/usbhid-ups -DD -a ups -k
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000     debug level is '2'
   0.002923     upsdrv_initups...
   0.005450     Checking device (09AE/2012) (001/008)
   0.019895     - VendorID: 09ae
   0.021024     - ProductID: 2012
   0.022095     - Manufacturer: Tripp Lite
   0.023168     - Product: Tripp Lite UPS
   0.024250     - Serial Number: unknown
   0.025317     - Bus: 001
   0.026336     - Device release number: 0009
   0.027369     Trying to match device
   0.028705     Device matches
   0.029857     failed to claim USB device: could not claim interface 0:
Device or resource busy
   0.032021     detached kernel driver from USB device...
   0.034740     HID descriptor length 662
   0.126921     Report Descriptor size = 662
   0.129599     Using subdriver: TrippLite HID 0.82
   0.130871     74 HID objects found
   0.133557     Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID:
0x28, Offset: 0, Size: 8, Value: 2
   0.134289     Path: UPS.PowerSummary.iSerialNumber, Type: Feature,
ReportID: 0x29, Offset: 0, Size: 8, Value: 3
   0.136294     Path: UPS.PowerSummary.iManufacturer, Type: Feature,
ReportID: 0x2b, Offset: 0, Size: 8, Value: 1
   0.137040     Path: UPS.PowerSummary.ffff00d9, Type: Feature, ReportID:
0xc0, Offset: 0, Size: 8, Value: 5
   0.139052     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature,
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.141063     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.141916     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
   0.143923     Path: UPS.PowerSummary.CapacityMode, Type: Feature,
ReportID: 0x33, Offset: 0, Size: 8, Value: 2
   0.145915     Path: UPS.PowerSummary.Rechargeable, Type: Feature,
ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
   0.147923     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input,
ReportID: 0x35, Offset: 0, Size: 16, Value: 3840
   0.148173     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x35, Offset: 0, Size: 16, Value: 3840
   0.149052     Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.149220     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.151294     Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature,
ReportID: 0x37, Offset: 0, Size: 8, Value: 100
   0.153295     Path: UPS.PowerSummary.DesignCapacity, Type: Feature,
ReportID: 0x36, Offset: 0, Size: 8, Value: 100
   0.155302     Path: UPS.PowerSummary.PresentStatus.Voltage, Type:
Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 1125
   0.157295     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent,
Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.157466     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
   0.157681     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 2, Size: 1, Value: 1
   0.158004     Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
   0.158537     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
   0.158938     Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.159316     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.159654     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.159998     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent,
Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.160316     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
   0.160643     Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
   0.161050     Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
   0.161590     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
   0.162056     Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.162285     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.162686     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.165063     Path: UPS.BatterySystem.Battery.ConfigVoltage, Type:
Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 24
   0.165929     Path: UPS.BatterySystem.Battery.PresentStatus.Charging,
Type: Feature, ReportID: 0x23, Offset: 0, Size: 1, Value: 1
   0.166098     Path: UPS.BatterySystem.Battery.PresentStatus.Discharging,
Type: Feature, ReportID: 0x23, Offset: 1, Size: 1, Value: 0
   0.166336     Path:
UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature,
ReportID: 0x23, Offset: 2, Size: 1, Value: 0
   0.168422     Path: UPS.BatterySystem.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 0
   0.170429     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID:
0x01, Offset: 0, Size: 8, Value: 120
   0.172417     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID:
0x02, Offset: 0, Size: 8, Value: 60
   0.174421     Path: UPS.Flow.ConfigApparentPower, Type: Feature,
ReportID: 0x03, Offset: 0, Size: 16, Value: 1500
   0.176420     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.178432     Path: UPS.OutletSystem.Outlet.ffff00bc, Type: Feature,
ReportID: 0xe0, Offset: 0, Size: 16, Value: 0
   0.180429     Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature,
ReportID: 0x51, Offset: 0, Size: 8, Value: 0
   0.182421     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.184422     Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature,
ReportID: 0xb6, Offset: 0, Size: 8, Value: 1
   0.186429     Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type:
Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 8210
   0.188432     Path: UPS.TLCustom.[1].ffff00df, Type: Feature, ReportID:
0x9f, Offset: 0, Size: 32, Value: 3
   0.190439     Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID:
0x96, Offset: 0, Size: 8, Value: 255
   0.192393     refresh_report_buffer: expected 5 bytes, but got 2 instead
   0.192571     Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID:
0xb4, Offset: 0, Size: 32, Value: 255
   0.194518     refresh_report_buffer: expected 5 bytes, but got 2 instead
   0.194696     Path: UPS.ffff0015.[1].ffff00d3, Type: Feature, ReportID:
0xb5, Offset: 0, Size: 32, Value: 255
   0.196934     Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID:
0x97, Offset: 0, Size: 16, Value: 255
   0.197763     Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID:
0x98, Offset: 0, Size: 8, Value: 255
   0.199686     Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID:
0x99, Offset: 0, Size: 16, Value: 255
   0.200527     Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID:
0x9b, Offset: 0, Size: 16, Value: 3
   0.202435     Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID:
0xc2, Offset: 0, Size: 32, Value: 11
   0.204391     libusb_get_report: could not claim interface 0: Device or
resource busy
   0.204547     Can't retrieve Report c1: Device or resource busy
   0.204984     Path: UPS.ffff0015.[1].ffff00d8, Type: Feature, ReportID:
0xc1, Offset: 0, Size: 32
   0.207063     Path: UPS.ffff0015.[1].ffff00d7, Type: Feature, ReportID:
0xc3, Offset: 0, Size: 32, Value: 1
   0.207896     libusb_get_report: could not claim interface 0: Device or
resource busy
   0.208048     Can't retrieve Report 9a: Device or resource busy
   0.208339     Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID:
0x9a, Offset: 0, Size: 32
   0.210434     Path: UPS.ffff0015.[1].CommunicationVersion, Type: Feature,
ReportID: 0x59, Offset: 0, Size: 32, Value: 4
   0.212429     Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 263
   0.214426     Path: UPS.PowerConverter.Input.Voltage, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 112.5
   0.216425     Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 59.8
   0.218426     Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 112.4
   0.220433     Path: UPS.PowerConverter.Output.ActivePower, Type: Feature,
ReportID: 0x47, Offset: 0, Size: 16, Value: 0
   0.222423     Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange,
Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.222594     Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.222833     Path: UPS.PowerConverter.PresentStatus.Boost, Type:
Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.223449     Path: UPS.PowerConverter.PresentStatus.Overload, Type:
Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.223707     Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature,
ReportID: 0x22, Offset: 5, Size: 1, Value: 0
   0.223927     Path: UPS.PowerConverter.PresentStatus.OverTemperature,
Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.224405     Path: UPS.PowerConverter.PresentStatus.InternalFailure,
Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.224726     Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.226683     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type:
Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.227422     Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
   0.227656     Report descriptor retrieved (Reportlen = 662)
   0.227813     Found HID device
   0.227999     Detected a UPS: Tripp Lite /Tripp Lite UPS
   0.228695     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.229285     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x35, Offset: 0, Size: 16, Value: 3840
   0.229798     Path: UPS.BatterySystem.Battery.ConfigVoltage, Type:
Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 24
   0.230176     Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 263
   0.230514     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
   0.233641     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.233898     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type:
Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.234177     Path: UPS.BatterySystem.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 0
   0.234533     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.234899     Path: UPS.Flow.ConfigApparentPower, Type: Feature,
ReportID: 0x03, Offset: 0, Size: 16, Value: 1500
   0.235361     Path: UPS.PowerConverter.Output.ActivePower, Type: Feature,
ReportID: 0x47, Offset: 0, Size: 16, Value: 0
   0.235781     Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
   0.236148     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.236631     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent,
Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.236905     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
   0.237127     Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.237528     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.237866     Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
   0.238339     Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
   0.238680     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 7, Size:1, Value: 0
   0.239026     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 4, Size:1, Value: 0
   0.239555     Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange,
Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.239774     Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.240222     Path: UPS.PowerConverter.PresentStatus.Boost, Type:
Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.240606     Path: UPS.PowerConverter.PresentStatus.Overload, Type:
Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.241013     Path: UPS.PowerConverter.PresentStatus.OverTemperature,
Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.241395     Path: UPS.PowerConverter.PresentStatus.InternalFailure,
Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.241731     Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.242083     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature,
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.242538     Path: UPS.PowerConverter.Input.Voltage, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 112.5
   0.242862     Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 59.8
   0.243516     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID:
0x01, Offset: 0, Size: 8, Value: 120
   0.243880     Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 112.4
   0.244299     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID:
0x02, Offset: 0, Size: 8, Value: 60
   0.244685     Path: UPS.BatterySystem.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 0
   0.244975     Path: UPS.BatterySystem.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 0
   0.245549     Path: UPS.BatterySystem.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 0
   0.245890     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.246349     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.246684     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type:
Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.246864     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.247177     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.247607     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.247935     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.248426     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.248761     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.249099     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.249790     find_nut_info: unknown info type: load.on.delay
   0.249969     find_nut_info: unknown info type: load.on.delay
   0.250269     Initiating UPS shutdown
   0.250505     upsdrv_shutdown...
   0.250795     instcmd(shutdown.return, [NULL])
   0.251176     find_nut_info: unknown info type: shutdown.return
   0.251447     instcmd(load.on.delay, [NULL])
   0.251795     find_nut_info: unknown info type: load.on.delay
   0.251985     instcmd: info element unavailable load.on.delay

   0.252371     instcmd(shutdown.reboot, [NULL])
   0.254665     upsdrv_cleanup...

------------------------------

pi@rpi:~ $ upscmd -l ups
Instant commands supported on UPS [ups]:

beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
reset.watchdog - Reset watchdog timer
shutdown.reboot - Shut down the load briefly while rebooting the UPS
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to