Hello. Battery, battery, battery. I am only thinking at worn batteries. I recently had the same symptoms with an hp/eaton g3 1500va. One of the 3 batteries was reading a healthy 12.8v, but when put under load it would quickly drain. I would measure each battery and test them under load, like with a car headlight bulb switched on both fillaments.
On Thu, 23 Apr 2020, 16:54 Marc Franquesa, <[email protected]> wrote: > Hi, recently I observed that during a power outage, my NUT setup doesn't > shutdown properly. Indeed it never reaches the LowBattery state to notify > and initiate shutdown on clients. Reviewing my setup and logs I think I'm > facing multiple problems and I'm unable to point to real root cause. > > First, let me focus on my scenario and current setup: > > In normal status (ONLINE, fully charged) my UPS runtime is about > 20minutes, this is some of the relevant info: > > Charge 100% > Charge Low 20% > Runtime 20m37s > Type PbAc > Manufacturer EATON > Model Ellipse > ECO 1200 > Serial 000000000 > Power 25VA > Frequency Nominal 50Hz > Voltage 230.0V > Voltage Nominal 230V > Delay Shutdown 25s > Delay Start 40s > Firmware 02 > Load 23% > Power Nominal 1200VA > Status OL > > During a power outage it used to last for about 15 minutes and then > initiate the shutdown. however reviewing the logs of my systems: > > Apr 19 12:04:23 - OnBattery > Apr 19 12:10:21 - Power from UPS cut, all systems got suddenly powered off > (no graceful shutdown) > Apr 19 12:16:46 - Power restored, UPS feeds power again to the systems and > they boot up. > > So this indicated the UPS only lasted about 6 minutes. > > Also I have 2 UPS: > - UPSdevice, which is the real UPS > - HeartBeat : virtual dummy device to monitor proper NUT communication > (see http://rogerprice.org/NUT/NUT.html#HEARTBEAT). > > Looking at the logs when the event starts: > > Apr 19 12:04:23 laney upsmon[756]: UPS [email protected]: On > battery. > Apr 19 12:04:23 laney upssched[797]: New timer: onbattwarn (30 seconds) > Apr 19 12:04:53 laney upssched[797]: Event: onbattwarn > Apr 19 12:08:24 laney upsmon[756]: UPS [email protected]: On > battery. > Apr 19 12:08:24 laney upssched[797]: Cancelling timer: heartbeat-failure > > UPSdevice uses timer "onbattwarn", while HeartBeat is using a separated > timer "heartbeat-failure". So I supose that when heartbeat cancels the > 'heartbeat-failure' the onbattwarn timer is still running. > > The second concern is quickly spotted: > > Apr 19 12:09:19 laney usbhid-ups[703]: libusb_get_interrupt: error > submitting URB: No such device > Apr 19 12:09:24 laney upsd[753]: Data for UPS [UPSdevice] is stale - check > driver > Apr 19 12:09:26 laney upsd[753]: UPS [UPSdevice] data is no longer stale > > Seems that during the 'onbattwarn' event, NUT lost communcaiton with the > UPS for about 6 secs? this is really quick to trigger any 'COMM_BAD' evebt > so no notifcation regarding this is sent, just the logs. > > However as stated above on the logs, just 1 min later (12:10:21) power is > totally lost even from UPS, no trace of LowBattery events, comm errors or > so. A part from a email message that upssched sent me (although no logs of > the event appears), this email reports: > > Power ups UPSdevice battery-low notification > UPS: [email protected] > Notice type: LOWBATT > Message: battery-low > Sun, 19 Apr 2020 12:10:27 +0200 > > Charge 73% > Charge Low 20% > Runtime 15m52s > Type PbAc > Manufacturer EATON > Model Ellipse > ECO 1200 > Serial 000000000 > Type Ups > Power 25VA > Frequency Nominal 50Hz > Voltage 230.0V > Voltage Nominal 230V > Delay Shutdown 20s > Delay Start 30s > Firmware 02 > Load 21% > Power Nominal 1200VA > Status FSD > ALARM OB LB > > So, indeed was in LowBattery and FSD shutdown, however note that the > current charge was 73% >> 20% low battery, so why it set LB when there were > enough battery to run? Is this a comm problem, device issue, driver ? > > So mainly my concerns questions are: > A) Can upsched introduce some race-conditions making a timer cancel cancel > other timers not related ? > B) May my UPS be faulting or just some USB driver issue? > > Any other hint, information or idea is welcomed. > > Regards > _______________________________________________ > Nut-upsuser mailing list > [email protected] > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser