On Thu, 23 Apr 2020, Marc Franquesa wrote:
...this email reports:Power ups UPSdevice battery-low notification UPS: [email protected] Notice type: LOWBATT Message: battery-low Sun, 19 Apr 2020 12:10:27 +0200 Charge 73% Charge Low 20% Runtime 15m52s ... Delay Shutdown 20s Delay Start 30s Firmware 02 Load 21% Power Nominal 1200VA Status FSD ALARM OB LB
Assuming the battery is ok, then how long does it take this system to shut down? Is a Delay Shutdown of only 20 sec enough?
So, indeed was in LowBattery and FSD shutdown, however note that the current charge was 73% >> 20% low battery, so why it set LB when there were enough battery to run? Is this a comm problem, device issue, driver ?
System administrators sometimes use the command upsrw -s battery.charge.low=75 -u <upsuser> -p <sekret> <myups> to speed up NUT testing. Do you have such a command lurking somewhere?
A) Can upsched introduce some race-conditions making a timer cancel cancel other timers not related ?
The upssched timers operate independently of one another. Unless you have strange logic in upssched-cmd the heartbeat timers should not affect any other timer. If you are shutting down on LB, then why do you need timers in upssched (apart from the heartbeart)?
Roger
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser