On 7/4/23 12:13, Karl Schmidt wrote:


On 7/4/23 05:31AM, Jim Klimov wrote:
Hello, thanks for the report and trying to wrap my head around it.

On a side note, it seems you've reported the same(?) UPS a couple of decades ago? ;)
https://networkupstools.org/networkupstools-master.github.io/ddl/Exide/NetUPS_SE_PRC2400a.html 
<https://networkupstools.org/networkupstools-master.github.io/ddl/Exide/NetUPS_SE_PRC2400a.html> 
=> 
https://github.com/networkupstools/nut-ddl/blob/master/Exide/Exide__NetUPS_SE_PRC2400a__upscode2__2.0.2__01.dev
 
<https://github.com/networkupstools/nut-ddl/blob/master/Exide/Exide__NetUPS_SE_PRC2400a__upscode2__2.0.2__01.dev>
 => https://alioth-lists.debian.net/pipermail/nut-upsuser/2005-July/000030.html 
<https://alioth-lists.debian.net/pipermail/nut-upsuser/2005-July/000030.html>

two decades? Seems like a few weeks..  <grin>

To be clear - it has worked all that time - I would get hickups, where it would complain about a communication error - once in a while.  It did work.

udev has ben playing tidly-winks with manhole covers since early buster, and debian currently has a udev bug that won't be fixed before trixie. Check to see if you are suffering from the bug, that ftdi serial SHOULD show up in /dev/serial/ both in by-id and in by-path subdirs. But the bug kills the by-id, so if it is detected, you should have a /dev/serial/by-path. That should in a roundabout way, hit /dev/ttyUSBsomething. If that is the case, try the by-path output format to address the non-working ttyUSB#, and get back to us of course. The by-id is by far the most definite way because if the adapter has a serial number, it becomes part of the unique address to the device. The usb# is not the final say. /dev/serial/by-id will contain a nominally 24 digit serial number hard coded into the chip at bondout time.

Its currently being a major pita in the 3d printer world.

So to me there are a few issues that pop up from this recent message:

1) Do I understand correctly that in the topmost "screenshot" with debug verbosity "2" the driver only proceeds to report the `tcgetattr()` error and exits, while the runs at greater verbosity they lived longer at least (seems they also actually worked)?

No - the clip at the top is directed to the symlink. Now I'm just trying to get /dev/ttyUSB0 to work as a first step.

* Did you check if this is linked to verbosity level (something broken about debugging methods - these were refactored between 2.7.4 and 2.8.0), * ...or to just running it several times - e.g. a competing driver instance or some other program held the device node, but was killed off during/before retries? * Namely, there was a bug related to that debug-method refactor, and the fix mentions `upscode2` specifically among the places it could pop up: https://github.com/networkupstools/nut/pull/1495 <https://github.com/networkupstools/nut/pull/1495> ** if this is it - running the packaged build at debug verbosity 3 or more may be an option; otherwise a custom build either from debian sources of your package + patch equivalent for the PR, or just of the current NUT master: e.g. https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests <https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests> may help

2) I suppose the udev rule above was hand-crafted? NUT sources do not mention a "6001" (productId), and the "0403" (vendorId) is mentioned in a `nutdrv_siemens_sitop` driver which was added in NUT 2.8.0 release.

The 6001-id is a ftdi USB to serial adapter - Rule was to keep the port from changing names. (I should have pointed that out)..

The rule appears works - other than the symlink - creates with the right group and mask - the symlink no longer works? (probably a udev bug?).

For the symlink :
# stty -a -F /dev/ttyUSB-nut
stty: /dev/ttyUSB-nut: Operation not permitted

# ll /dev/ttyUSB-nut
lrwxrwxrwx 1 root root 15 2023-07-03 20:20 /dev/ttyUSB-nut -> bus/usb/001/010

So the symlink that udev creates, points to the bus device rather than /dev/ttyUSB0 ??  I think probably a seperate udev puzzle?




* Asking because one of the changes introduced by 2.8.0 was a change from "rules" to "hwdb" format in https://github.com/networkupstools/nut/pull/1342/files <https://github.com/networkupstools/nut/pull/1342/files> - however as I'm revisiting it now, I am having second thoughts: the changed file was about UPower not UDev - both subsystems are from FreeDesktop project, but not sure if the similarities don't end there. * Originally was going to suggest that the NUT "udev rules" are replaced by "udev hwdb" (format change leading to a more optimized use of binary database under the systemd hood), but not fully sure this is actually the case at the moment. * Anyway, wondering if your rule is honored or ignored by systemd after the OS upgrade - this may depend on config file location and naming. At least, would for HWDB override mechanism: https://www.freedesktop.org/software/systemd/man/hwdb.html <https://www.freedesktop.org/software/systemd/man/hwdb.html> * ...and/or if it conflicts with something due to also-use of some same SUBSYSTEM (not listed in your snapshot)...

Hope this helps,
Jim Klimov

On Tue, Jul 4, 2023 at 5:08 AM Karl Schmidt <[email protected] <mailto:[email protected]>> wrote:

    Upgraded to Debian bookworm - working nut system stopped working.

    nut-server:   Installed: 2.8.0-7


    Trying :

    /usr/lib/nut/upscode2 -a malaysia -DD
    Network UPS Tools - UPScode II UPS driver 0.90 (2.8.0)
    Warning: This is an experimental driver.
    Some features may not function correctly.

         0.000000     [D1] debug level is '2'
         0.002302     tcgetattr(/dev/ttyUSB-nut): Inappropriate ioctl for device

    Looks like two problems  - the udev rule isn't working any more?
    ATTRS{idVendor}=="0403", ATTRS{idProduct}=="6001", ATTRS{serial}=="AJV9MKOY", SYMLINK+="ttyUSB-nut",GROUP = "nut",
    MODE="0666"


    So I tried going straight to the device:
    /usr/lib/nut/upscode2 -a malaysia -DDDD

    This returns the following after a bit (Looks like it likes UPTP)..


    ] upscsend: 'UPTP'
         1.857813     [D3] upscrecv: Empty line
         1.921764     [D3] upscrecv: 5 bytes: 'NNAME'
         2.097563     [D3] upscrecv: 20 bytes:        'UPS 2400 VA FW -0026'
         2.097593     [D2] Got value: NNAME UPS 2400 VA FW -0026

    So it IS talking to the UPS - but something above my knowledge is going wrong?




    Here is a longer output tail..

    /usr/lib/nut/upscode2 -a malaysia -DDDD
    Network UPS Tools - UPScode II UPS driver 0.90 (2.8.0)
    Warning: This is an experimental driver.
    Some features may not function correctly.

         0.000000     [D1] debug level is '4'
         0.002995     [D1] input_timeout = 2 Sec
         0.003002     [D1] output_pace = 200 uSec
         0.003007     [D1] full_update_timer = 60 Sec
         0.003011     [D1] use_crlf = 0
         0.003016     [D1] use_pre_lf = 0
         0.004308     [D3] upscsend: 'UPCL'
         0.217722     [D3] upscrecv: Empty line
         0.265688     [D3] upscrecv: 4 bytes: 'UPSS'
         0.265717     [D2] Supports command: UPSS
         0.313620     [D3] upscrecv: 4 bytes: 'UPDS'
         0.313649     [D2] Supports command: UPDS
         0.361570     [D3] upscrecv: 4 bytes: 'UPDV'
         0.361599     [D2] Supports command: UPDV
         0.409520     [D3] upscrecv: 4 bytes: 'UPTP'
         0.409549     [D2] Supports command: UPTP
         0.457471     [D3] upscrecv: 4 bytes: 'UPSN'
         0.457500     [D2] Supports command: UPSN
         0.505436     [D3] upscrecv: 4 bytes: 'UPPN'
         0.505465     [D2] Supports command: UPPN
         0.569393     [D3] upscrecv: 4 bytes: 'UPSD'
         0.569421     [D2] Supports command: UPSD
         0.569437     [D1] setvar: ups.delay.shutdown UPSD
         0.617343     [D3] upscrecv: 4 bytes: 'UPCD'
         0.617372     [D2] Supports command: UPCD
         0.617387     [D1] setvar: ups.delay.reboot UPCD
         0.665290     [D3] upscrecv: 4 bytes: 'UPPC'
         0.665319     [D2] Supports command: UPPC
         0.665334     [D1] instcmd: shutdown.reboot UPPC
         0.713264     [D3] upscrecv: 4 bytes: 'UPPU'
         0.713293     [D2] Supports command: UPPU
         0.713307     [D1] instcmd: shutdown.stop UPPU
         0.761218     [D3] upscrecv: 4 bytes: 'UPIS'
         0.761247     [D2] Supports command: UPIS
         0.761262     [D1] instcmd: test.panel.start UPIS
         0.809167     [D3] upscrecv: 4 bytes: 'UP??'
         0.809197     [D2] Supports command: UP??
         0.857112     [D3] upscrecv: 4 bytes: 'UPEA'
         0.857141     [D2] Supports command: UPEA
         0.905089     [D3] upscrecv: 4 bytes: 'UPDA'
         0.905119     [D2] Supports command: UPDA
         0.953091     [D3] upscrecv: 4 bytes: 'UPCL'
         0.953120     [D2] Supports command: UPCL
         0.953135     [D2] Request value: UPCD 0000
         0.954763     [D3] upscsend: 'UPCD'
         0.956318     [D3] upscsend: '0000'
         2.958427     [D3] upscrecv: Timeout
         4.960535     [D3] upscrecv: Timeout
         4.960566     [D2] Got value:
         4.960580     Bad response to UPCD 0000:
         4.960596     dstate_setflags: base variable (ups.delay.reboot) does not exist          4.960609     dstate_setaux: base variable (ups.delay.reboot) does not exist
         4.960624     [D2] Request value: UPSD 0000
         4.962217     [D3] upscsend: 'UPSD'
         4.963805     [D3] upscsend: '0000'
         5.089317     [D3] upscrecv: Empty line
         5.201214     [D3] upscrecv: 4 bytes: 'ACSD'
         5.313141     [D3] upscrecv: 3 bytes: '000'
         5.313177     [D2] Got value: ACSD 000
         5.313221     [D2] Request value: UPTP ""
         5.314826     [D3] upscsend: 'UPTP'
         5.512984     [D3] upscrecv: Empty line
         5.560909     [D3] upscrecv: 5 bytes: 'NNAME'
         5.752764     [D3] upscrecv: 20 bytes:        'UPS 2400 VA FW -0026'
         5.752794     [D2] Got value: NNAME UPS 2400 VA FW -0026
         5.752817     [D2] Request value: UPSN 0
         5.754297     [D3] upscsend: 'UPSN'
         5.754904     [D3] upscsend: '0'
         5.856693     [D3] upscrecv: Empty line
         5.904642     [D3] upscrecv: 4 bytes: 'ACSN'
         6.080517     [D3] upscrecv: 20 bytes:        'LR204A996      '
         6.080547     [D2] Got value: ACSN LR204A996
         6.082104     [D3] upscsend: 'UPDA'
         6.082125     [D1] Setvar: ups.delay.shutdown 10
         6.082140     [D2] Request value: UPSD 10
         6.083732     [D3] upscsend: 'UPSD'
         6.084665     [D3] upscsend: '10'
         8.086750     [D3] upscrecv: Timeout
        10.088837     [D3] upscrecv: Timeout
        10.088870     [D2] Got value:
        10.088885     Bad response to UPSD 10:
        10.088899     [D1] Setvar: ups.delay.reboot 60
        10.088914     [D2] Request value: UPCD 60
        10.090447     [D3] upscsend: 'UPCD'
        10.091381     [D3] upscsend: '60'
        10.216917     [D3] upscrecv: Empty line
        10.664514     [D3] upscrecv: 4 bytes: 'ACCD'
        10.776416     [D3] upscrecv: 3 bytes: '060'
        10.776446     [D2] Got value: ACCD 060
        10.778032     [D3] upscsend: 'UPDS'
        10.879313     [D3] upscrecv: Empty line
        10.927264     [D3] upscrecv: 4 bytes: 'STOK'
        10.975240     [D3] upscrecv: 2 bytes: '00'
        10.975271     [D2] Parameter STOK 00
        10.975286     [D3] Ignored value: STOK 00
        11.023214     [D3] upscrecv: 4 bytes: 'STBO'
        11.055157     [D3] upscrecv: 2 bytes: '00'
        11.055188     [D2] Parameter STBO 00
        11.103112     [D3] upscrecv: 4 bytes: 'STBL'
        11.135092     [D3] upscrecv: 2 bytes: '00'
        11.135123     [D2] Parameter STBL 00
        11.183039     [D3] upscrecv: 4 bytes: 'STBM'
        11.247011     [D3] upscrecv: 2 bytes: 'RS'
        11.247042     [D2] Parameter STBM RS
        11.247057     [D3] Ignored value: STBM RS
        11.294911     [D3] upscrecv: 4 bytes: 'STLR'
        11.326885     [D3] upscrecv: 2 bytes: 'NO'
        11.326917     [D2] Parameter STLR NO
        11.326933     [D3] Ignored value: NO 11
        11.438776     [D3] upscrecv: 5 bytes: 'BTIME'
        11.550705     [D3] upscrecv: 7 bytes: '0044.00'
        11.550736     [D2] Parameter BTIME 0044.00
        11.630638     [D3] upscrecv: 5 bytes: 'MIUL1'
        11.710552     [D3] upscrecv: 7 bytes: '0123.00'
        11.710583     [D2] Parameter MIUL1 0123.00
        11.758512     [D3] upscrecv: 5 bytes: 'MBUUU'
        11.854411     [D3] upscrecv: 7 bytes: '0052.40'
        11.854442     [D2] Parameter MBUUU 0052.40
        11.934326     [D3] upscrecv: 5 bytes: 'MOUL1'
        12.030259     [D3] upscrecv: 7 bytes: '0123.00'
        12.030292     [D2] Parameter MOUL1 0123.00
        12.110180     [D3] upscrecv: 5 bytes: 'MOIL1'
        12.190129     [D3] upscrecv: 7 bytes: '0001.61'
        12.190160     [D2] Parameter MOIL1 0001.61
        12.318027     [D3] upscrecv: 5 bytes: 'MOPL1'
        12.445896     [D3] upscrecv: 7 bytes: '0000.14'
        12.445927     [D2] Parameter MOPL1 0000.14
        12.493846     [D3] upscrecv: 5 bytes: 'MOSL1'
        12.573801     [D3] upscrecv: 7 bytes: '0000.19'
        12.573833     [D2] Parameter MOSL1 0000.19
        12.637719     [D3] upscrecv: 5 bytes: 'MOFFF'
        12.701675     [D3] upscrecv: 7 bytes: '0060.00'
        12.701707     [D2] Parameter MOFFF 0060.00
        12.703253     [D3] upscsend: 'UPDV'
        12.997414     [D3] upscrecv: Empty line
        13.045369     [D3] upscrecv: 5 bytes: 'NIUNN'
        13.125288     [D3] upscrecv: 7 bytes: '0120.00'
        13.125320     [D2] Parameter NIUNN 0120.00
        13.173272     [D3] upscrecv: 5 bytes: 'NIUHH'
        13.253195     [D3] upscrecv: 7 bytes: '0145.00'
        13.253227     [D2] Parameter NIUHH 0145.00
        13.317124     [D3] upscrecv: 5 bytes: 'NIULL'
        13.381064     [D3] upscrecv: 7 bytes: '0084.00'
        13.381096     [D2] Parameter NIULL 0084.00
        13.444995     [D3] upscrecv: 5 bytes: 'NBUNN'
        13.508999     [D3] upscrecv: 7 bytes: '0048.00'
        13.509031     [D2] Parameter NBUNN 0048.00
        13.572871     [D3] upscrecv: 5 bytes: 'NBUHH'
        13.652790     [D3] upscrecv: 7 bytes: '0056.40'
        13.652822     [D2] Parameter NBUHH 0056.40
        13.700718     [D3] upscrecv: 5 bytes: 'NBULL'
        13.780646     [D3] upscrecv: 7 bytes: '0040.00'
        13.780678     [D2] Parameter NBULL 0040.00
        13.828610     [D3] upscrecv: 5 bytes: 'NBAHN'
        13.908534     [D3] upscrecv: 7 bytes: '0017.00'
        13.908565     [D2] Parameter NBAHN 0017.00
        13.972466     [D3] upscrecv: 5 bytes: 'NOUNN'
        14.036388     [D3] upscrecv: 7 bytes: '0120.00'
        14.036420     [D2] Parameter NOUNN 0120.00
        14.100339     [D3] upscrecv: 5 bytes: 'NOUHH'
        14.164293     [D3] upscrecv: 7 bytes: '0128.00'
        14.164325     [D2] Parameter NOUHH 0128.00
        14.228232     [D3] upscrecv: 5 bytes: 'NOULL'
        14.308156     [D3] upscrecv: 7 bytes: '0108.00'
        14.308187     [D2] Parameter NOULL 0108.00
        14.372081     [D3] upscrecv: 5 bytes: 'NOINN'
        14.436035     [D3] upscrecv: 7 bytes: '0020.00'
        14.436066     [D2] Parameter NOINN 0020.00
        14.499991     [D3] upscrecv: 5 bytes: 'NOIHH'
        14.563980     [D3] upscrecv: 7 bytes: '0022.80'
        14.564012     [D2] Parameter NOIHH 0022.80
        14.627857     [D3] upscrecv: 5 bytes: 'NOPNN'
        14.707804     [D3] upscrecv: 7 bytes: '0001.60'
        14.707835     [D2] Parameter NOPNN 0001.60
        14.755763     [D3] upscrecv: 5 bytes: 'NOSNN'
        14.835705     [D3] upscrecv: 7 bytes: '0002.40'
        14.835737     [D2] Parameter NOSNN 0002.40
        14.883676     [D3] upscrecv: 5 bytes: 'NOFHH'
        14.979582     [D3] upscrecv: 7 bytes: '0063.00'
        14.979614     [D2] Parameter NOFHH 0063.00
        15.027550     [D3] upscrecv: 5 bytes: 'NOFLL'
        15.107450     [D3] upscrecv: 7 bytes: '0057.00'
        15.107481     [D2] Parameter NOFLL 0057.00
        15.107536     [D2] ups.load: 8.1
        15.107666     [D2] dstate_init: sock /run/nut/upscode2-malaysia open on fd 5
        15.109232     [D3] upscsend: 'UPDS'
        15.210376     [D3] upscrecv: Empty line
        15.258350     [D3] upscrecv: 4 bytes: 'STOK'
        15.306305     [D3] upscrecv: 2 bytes: '00'
        15.306336     [D2] Parameter STOK 00
        15.306352     [D3] Ignored value: STOK 00
        15.354256     [D3] upscrecv: 4 bytes: 'STBO'
        15.386220     [D3] upscrecv: 2 bytes: '00'
        15.386255     [D2] Parameter STBO 00
        15.434171     [D3] upscrecv: 4 bytes: 'STBL'
        15.466145     [D3] upscrecv: 2 bytes: '00'
        15.466176     [D2] Parameter STBL 00
        15.514102     [D3] upscrecv: 4 bytes: 'STBM'
        15.578049     [D3] upscrecv: 2 bytes: 'RS'
        15.578080     [D2] Parameter STBM RS
        15.578095     [D3] Ignored value: STBM RS
        15.625999     [D3] upscrecv: 4 bytes: 'STLR'
        15.673979     [D3] upscrecv: 2 bytes: 'NO'
        15.674011     [D2] Parameter STLR NO
        15.674026     [D3] Ignored value: NO 11
        15.769877     [D3] upscrecv: 5 bytes: 'BTIME'
        15.881803     [D3] upscrecv: 7 bytes: '0044.00'
        15.881834     [D2] Parameter BTIME 0044.00
        15.961721     [D3] upscrecv: 5 bytes: 'MIUL1'
        16.041667     [D3] upscrecv: 7 bytes: '0123.00'
        16.041699     [D2] Parameter MIUL1 0123.00
        16.089620     [D3] upscrecv: 5 bytes: 'MBUUU'
        16.185517     [D3] upscrecv: 7 bytes: '0052.40'
        16.185548     [D2] Parameter MBUUU 0052.40
        16.265414     [D3] upscrecv: 5 bytes: 'MOUL1'
        16.361340     [D3] upscrecv: 7 bytes: '0123.00'
        16.361371     [D2] Parameter MOUL1 0123.00
        16.441295     [D3] upscrecv: 5 bytes: 'MOIL1'
        16.521219     [D3] upscrecv: 7 bytes: '0001.61'
        16.521250     [D2] Parameter MOIL1 0001.61
        16.649089     [D3] upscrecv: 5 bytes: 'MOPL1'
        16.776990     [D3] upscrecv: 7 bytes: '0000.14'
        16.777021     [D2] Parameter MOPL1 0000.14
        16.840963     [D3] upscrecv: 5 bytes: 'MOSL1'
        16.904897     [D3] upscrecv: 7 bytes: '0000.19'
        16.904928     [D2] Parameter MOSL1 0000.19
        16.968835     [D3] upscrecv: 5 bytes: 'MOFFF'
        17.048768     [D3] upscrecv: 7 bytes: '0060.00'
        17.048800     [D2] Parameter MOFFF 0060.00
        17.048843     [D2] ups.load: 8.1
        17.109379     [D3] upscsend: 'UPDS'
        17.211638     [D3] upscrecv: Empty line
        17.259590     [D3] upscrecv: 4 bytes: 'STOK'
        17.307555     [D3] upscrecv: 2 bytes: '00'
        17.307586     [D2] Parameter STOK 00
        17.307602     [D3] Ignored value: STOK 00
        17.355513     [D3] upscrecv: 4 bytes: 'STBO'
        17.387488     [D3] upscrecv: 2 bytes: '00'
        17.387520     [D2] Parameter STBO 00
        17.435441     [D3] upscrecv: 4 bytes: 'STBL'
        17.467414     [D3] upscrecv: 2 bytes: '00'
        17.467445     [D2] Parameter STBL 00
        17.515380     [D3] upscrecv: 4 bytes: 'STBM'
        17.579312     [D3] upscrecv: 2 bytes: 'RS'
        17.579343     [D2] Parameter STBM RS
        17.579359     [D3] Ignored value: STBM RS
        17.627263     [D3] upscrecv: 4 bytes: 'STLR'
        17.659249     [D3] upscrecv: 2 bytes: 'NO'
        17.659280     [D2] Parameter STLR NO
        17.659296     [D3] Ignored value: NO 11
        17.771136     [D3] upscrecv: 5 bytes: 'BTIME'
        17.883029     [D3] upscrecv: 7 bytes: '0044.00'
        17.883061     [D2] Parameter BTIME 0044.00
        17.962979     [D3] upscrecv: 5 bytes: 'MIUL1'
        18.042958     [D3] upscrecv: 7 bytes: '0122.90'
        18.042990     [D2] Parameter MIUL1 0122.90
        18.090962     [D3] upscrecv: 5 bytes: 'MBUUU'
        18.186809     [D3] upscrecv: 7 bytes: '0052.40'
        18.186840     [D2] Parameter MBUUU 0052.40
        18.266757     [D3] upscrecv: 5 bytes: 'MOUL1'
        18.362674     [D3] upscrecv: 7 bytes: '0122.90'
        18.362705     [D2] Parameter MOUL1 0122.90
        18.442624     [D3] upscrecv: 5 bytes: 'MOIL1'
        18.522581     [D3] upscrecv: 7 bytes: '0001.61'
        18.522613     [D2] Parameter MOIL1 0001.61
        18.650481     [D3] upscrecv: 5 bytes: 'MOPL1'
        18.778378     [D3] upscrecv: 7 bytes: '0000.14'
        18.778409     [D2] Parameter MOPL1 0000.14
        18.842321     [D3] upscrecv: 5 bytes: 'MOSL1'
        18.906289     [D3] upscrecv: 7 bytes: '0000.19'
        18.906321     [D2] Parameter MOSL1 0000.19
        18.970249     [D3] upscrecv: 5 bytes: 'MOFFF'
        19.034175     [D3] upscrecv: 7 bytes: '0060.00'
        19.034237     [D2] Parameter MOFFF 0060.00
        19.034282     [D2] ups.load: 8.1
        19.109547     [D3] upscsend: 'UPDS'
        19.210993     [D3] upscrecv: Empty line
        19.258968     [D3] upscrecv: 4 bytes: 'STOK'
        19.306942     [D3] upscrecv: 2 bytes: '00'
        19.306974     [D2] Parameter STOK 00
        19.306989     [D3] Ignored value: STOK 00
        19.354951     [D3] upscrecv: 4 bytes: 'STBO'
        19.386848     [D3] upscrecv: 2 bytes: '00'
        19.386879     [D2] Parameter STBO 00
        19.434847     [D3] upscrecv: 4 bytes: 'STBL'
        19.466816     [D3] upscrecv: 2 bytes: '00'
        19.466848     [D2] Parameter STBL 00
        19.514772     [D3] upscrecv: 4 bytes: 'STBM'
        19.578715     [D3] upscrecv: 2 bytes: 'RS'
        19.578745     [D2] Parameter STBM RS
        19.578761     [D3] Ignored value: STBM RS
        19.626684     [D3] upscrecv: 4 bytes: 'STLR'
        19.658646     [D3] upscrecv: 2 bytes: 'NO'
        19.658677     [D2] Parameter STLR NO
        19.658693     [D3] Ignored value: NO 11
        19.770573     [D3] upscrecv: 5 bytes: 'BTIME'
        19.882444     [D3] upscrecv: 7 bytes: '0044.00'
        19.882476     [D2] Parameter BTIME 0044.00
        19.962369     [D3] upscrecv: 5 bytes: 'MIUL1'
        20.042297     [D3] upscrecv: 7 bytes: '0122.80'
        20.042329     [D2] Parameter MIUL1 0122.80
        20.090245     [D3] upscrecv: 5 bytes: 'MBUUU'
        20.186167     [D3] upscrecv: 7 bytes: '0052.40'
        20.186231     [D2] Parameter MBUUU 0052.40
        20.266130     [D3] upscrecv: 5 bytes: 'MOUL1'
        20.362041     [D3] upscrecv: 7 bytes: '0122.80'
        20.362072     [D2] Parameter MOUL1 0122.80
        20.441966     [D3] upscrecv: 5 bytes: 'MOIL1'
        20.521933     [D3] upscrecv: 7 bytes: '0001.61'
        20.521963     [D2] Parameter MOIL1 0001.61
        20.649756     [D3] upscrecv: 5 bytes: 'MOPL1'
        20.777607     [D3] upscrecv: 7 bytes: '0000.14'
        20.777638     [D2] Parameter MOPL1 0000.14
        20.825556     [D3] upscrecv: 5 bytes: 'MOSL1'
        20.905456     [D3] upscrecv: 7 bytes: '0000.19'
        20.905487     [D2] Parameter MOSL1 0000.19
        20.969405     [D3] upscrecv: 5 bytes: 'MOFFF'
        21.033378     [D3] upscrecv: 7 bytes: '0060.00'
        21.033410     [D2] Parameter MOFFF 0060.00
        21.033452     [D2] ups.load: 8.1
        21.109675     [D3] upscsend: 'UPDS'
        21.211208     [D3] upscrecv: Empty line
        21.259161     [D3] upscrecv: 4 bytes: 'STOK'
        21.307134     [D3] upscrecv: 2 bytes: '00'
        21.307165     [D2] Parameter STOK 00
        21.307181     [D3] Ignored value: STOK 00
        21.355107     [D3] upscrecv: 4 bytes: 'STBO'
        21.387063     [D3] upscrecv: 2 bytes: '00'
        21.387095     [D2] Parameter STBO 00
        21.435034     [D3] upscrecv: 4 bytes: 'STBL'
        21.467030     [D3] upscrecv: 2 bytes: '00'
        21.467061     [D2] Parameter STBL 00
        21.515006     [D3] upscrecv: 4 bytes: 'STBM'
        21.578958     [D3] upscrecv: 2 bytes: 'RS'
        21.578990     [D2] Parameter STBM RS
        21.579005     [D3] Ignored value: STBM RS
        21.626930     [D3] upscrecv: 4 bytes: 'STLR'
        21.658933     [D3] upscrecv: 2 bytes: 'NO'
        21.658964     [D2] Parameter STLR NO
        21.658980     [D3] Ignored value: NO 11
        21.770804     [D3] upscrecv: 5 bytes: 'BTIME'
        21.882679     [D3] upscrecv: 7 bytes: '0044.00'
        21.882710     [D2] Parameter BTIME 0044.00
        21.962630     [D3] upscrecv: 5 bytes: 'MIUL1'
        22.042523     [D3] upscrecv: 7 bytes: '0122.70'
        22.042555     [D2] Parameter MIUL1 0122.70
        22.090496     [D3] upscrecv: 5 bytes: 'MBUUU'
        22.186404     [D3] upscrecv: 7 bytes: '0052.40'
        22.186435     [D2] Parameter MBUUU 0052.40
        22.266327     [D3] upscrecv: 5 bytes: 'MOUL1'
        22.362259     [D3] upscrecv: 7 bytes: '0122.70'
        22.362291     [D2] Parameter MOUL1 0122.70
        22.442178     [D3] upscrecv: 5 bytes: 'MOIL1'
        22.522100     [D3] upscrecv: 7 bytes: '0001.61'
        22.522131     [D2] Parameter MOIL1 0001.61
        22.650010     [D3] upscrecv: 5 bytes: 'MOPL1'
        22.777925     [D3] upscrecv: 7 bytes: '0000.14'
        22.777956     [D2] Parameter MOPL1 0000.14
        22.825840     [D3] upscrecv: 5 bytes: 'MOSL1'
        22.905771     [D3] upscrecv: 7 bytes: '0000.19'
        22.905803     [D2] Parameter MOSL1 0000.19
        22.969722     [D3] upscrecv: 5 bytes: 'MOFFF'
        23.033673     [D3] upscrecv: 7 bytes: '0060.00'
        23.033705     [D2] Parameter MOFFF 0060.00
        23.033748     [D2] ups.load: 8.1
        23.109839     [D3] upscsend: 'UPDS'
        23.211517     [D3] upscrecv: Empty line
        23.259472     [D3] upscrecv: 4 bytes: 'STOK'
        23.307419     [D3] upscrecv: 2 bytes: '00'
        23.307450     [D2] Parameter STOK 00
        23.307465     [D3] Ignored value: STOK 00
        23.355368     [D3] upscrecv: 4 bytes: 'STBO'
        23.387348     [D3] upscrecv: 2 bytes: '00'
        23.387378     [D2] Parameter STBO 00
        23.435293     [D3] upscrecv: 4 bytes: 'STBL'
        23.467300     [D3] upscrecv: 2 bytes: '00'
        23.467332     [D2] Parameter STBL 00
        23.515242     [D3] upscrecv: 4 bytes: 'STBM'
        23.579192     [D3] upscrecv: 2 bytes: 'RS'
        23.579223     [D2] Parameter STBM RS
        23.579238     [D3] Ignored value: STBM RS
        23.627141     [D3] upscrecv: 4 bytes: 'STLR'
        23.659116     [D3] upscrecv: 2 bytes: 'NO'
        23.659146     [D2] Parameter STLR NO
        23.659162     [D3] Ignored value: NO 11
        23.771015     [D3] upscrecv: 5 bytes: 'BTIME'
        23.882913     [D3] upscrecv: 7 bytes: '0044.00'
        23.882945     [D2] Parameter BTIME 0044.00
        23.962838     [D3] upscrecv: 5 bytes: 'MIUL1'
        24.042766     [D3] upscrecv: 7 bytes: '0122.90'
        24.042798     [D2] Parameter MIUL1 0122.90
        24.090688     [D3] upscrecv: 5 bytes: 'MBUUU'
        24.186636     [D3] upscrecv: 7 bytes: '0052.40'
        24.186668     [D2] Parameter MBUUU 0052.40
        24.266579     [D3] upscrecv: 5 bytes: 'MOUL1'
        24.362485     [D3] upscrecv: 7 bytes: '0122.90'
        24.362517     [D2] Parameter MOUL1 0122.90
        24.442409     [D3] upscrecv: 5 bytes: 'MOIL1'
        24.522328     [D3] upscrecv: 7 bytes: '0001.61'
        24.522359     [D2] Parameter MOIL1 0001.61
        24.650229     [D3] upscrecv: 5 bytes: 'MOPL1'
        24.778081     [D3] upscrecv: 7 bytes: '0000.14'
        24.778112     [D2] Parameter MOPL1 0000.14
        24.826025     [D3] upscrecv: 5 bytes: 'MOSL1'
        24.905956     [D3] upscrecv: 7 bytes: '0000.19'
        24.905987     [D2] Parameter MOSL1 0000.19
        24.969900     [D3] upscrecv: 5 bytes: 'MOFFF'
        25.033908     [D3] upscrecv: 7 bytes: '0060.00'
        25.033940     [D2] Parameter MOFFF 0060.00
        25.033983     [D2] ups.load: 8.1
        25.109986     [D3] upscsend: 'UPDS'

    ------------->%-------------------------------------------

      From ups.conf

    user = nut
    maxretry = 3
    [malaysia]
    #        driver = usbhid-ups
    #               port = auto

    #       port = /dev/usb/hiddev0
    #       desc = "Triplite SU1500xl"



       driver = upscode2
    # port = /dev/ttyUSB-nut
       port = /dev/ttyUSB0
              manufacturer=Exide
    #        baudrate=1200
    ##      input_timeout=30
    #       full_update_timer=60
    ##        pollinterval=4

               desc="Exide PCR2400"

    #Acceptable values for  this driver:

    #  manufacturer [unknown] : -x manufacturer=<value>
    #  Serial interface baudrate [1200] : -x baudrate=<value>
    #  Command response timeout [2] : -x input_timeout=<value>
    #  Output character delay in usecs [200] : -x output_pace=<value>
    #  Delay between full value downloads [60] : -x full_update=<value>
    #  Use CR-LF to terminate commands to UPS : -x use_crlf
    #  Use LF to introduce commands to UPS : -x use_pre_lf

    #KPS - persistant name from usb-serial converter - see /etc/udev/rules.d/52_nut-serialups.rules

    # Set maxretry to 3 by default, this should mitigate race with slow devices:
    root@malaysia:~#



    -- --------------------------------------------------------------------------------     Karl Schmidt                                  EMail [email protected] <mailto:[email protected]>
    3209 West 9th Street                          Ph (785) 841-3089
    Lawrence, KS 66049

    If the government is allowed to break the law during emergencies,
    They will create emergencies to break the law.
    ?
--------------------------------------------------------------------------------

    _______________________________________________
    Nut-upsuser mailing list
    [email protected] <mailto:[email protected]>
    https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
<https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser>



Cheers, Gene Heskett.
--
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author, 1940)
If we desire respect for the law, we must first make the law respectable.
 - Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/>


_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to