Thanks, Tim. The unit was available with single as well as split phase
output, and from the data I can find the input was single phase, though
the input connector has L1/L2/N/G wires. I'm digging through the MIB to
see what the raw data looks like.
Thanks!
John
----
On 11/11/24 19:14, Tim Dawson wrote:
Sounds pretty normal from what I see. It appears that this is *NOT* a
true 240v UPS, but rather one that provides two legs of 120v output from
two legs of 120 input, and what is seen as "L2" is actually neutral, and
the line names are reporting incorrectly. With that in mind, each leg in
should be 120v, as well as the outputs, which is exactly what you are
seeing.(The fact tht L1 to L3 is 240v really isn't relevant).
- Tim
On November 11, 2024 6:56:51 PM EST, Greg Troxel via Nut-upsuser
<[email protected]> wrote:
John Ackermann N8UR via Nut-upsuser
<[email protected]> writes:
I am monitoring via the SNMP driver an APC SmartUPS that has split
phase (2L + neutral) 240V input and 120/120 volt outputs. The data
for the voltages is not what I'm expecting, and I am wondering how I
should interpret it.
Wow, that sounds kind of industrial. Model?
Is the input an L14-20P? Or equivalent non-twistlock?
Here is an example from upsc:
input.L1-L2.voltage: 121
input.L2-L3.voltage: 120
input.voltage: 121.20
output.current: 5.90
output.L1-L2.voltage: 119
output.L1.current: 5.90
output.L2-L3.voltage: 119
output.L2.current: 1
The "input.voltage" value doesn't reflect the 240 volts that is
actually being applied. To get that, would I combine the L1-L2 and
L2-L3 voltages?
I would address figuring this out as two steps. One is to see what the
device actually sends and what makes sense there. And then to see if
NUT is mapping or making synthetic.
I find it odd for the neutral to be labeled L2, as it seems to be. I
would think there would be L1 and L2, both reported as phase-to-neutral.
You might see if there is confusion.
odd for output.L2.current, vs L3, given that voltage seems to be L1/L3
vs L2.
Probably the first voltage is mapped to just 'voltage' and probably it
would be better to use the L1/L3 voltage. Similar for output.voltage.
output.current should probably be average if output.voltage is 240ish.
Or better yet
Note that the "output.current" value matches the L1 output current,
ignoring the L2 current. Perhaps that is a clue that the overall
"input" and "output" values are not meaningful in this case?
yes, and they are perhaps mapped from something else?
How should I interpret these values to know the actual input and
output voltages and currents?
You're going to need to put a meter on it and compare to the reports, I
suspect.
First, see if you can get specs, and look at the snmp mib directly and
see what you can figure out. Turn up debugging/verbose in nut.
------------------------------------------------------------------------
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
<https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser>
--
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser