L1/L2/N/G is considered single phase, just 2 hots.

FWIW . . .

On November 11, 2024 7:28:59 PM EST, John Ackermann N8UR via Nut-upsuser 
<[email protected]> wrote:
>Thanks, Tim.  The unit was available with single as well as split phase 
>output, and from the data I can find the input was single phase, though the 
>input connector has L1/L2/N/G wires.  I'm digging through the MIB to see what 
>the raw data looks like.
>
>Thanks!
>John
>----
>
>On 11/11/24 19:14, Tim Dawson wrote:
>> Sounds pretty normal from what I see. It appears that this is *NOT* a true 
>> 240v UPS, but rather one that provides two legs of 120v output from two legs 
>> of 120 input, and what is seen as "L2" is actually neutral, and the line 
>> names are reporting incorrectly. With that in mind, each leg in should be 
>> 120v, as well as the outputs, which is exactly what you are seeing.(The fact 
>> tht L1 to L3 is 240v really isn't relevant).
>> 
>> - Tim
>> 
>> 
>> On November 11, 2024 6:56:51 PM EST, Greg Troxel via Nut-upsuser 
>> <[email protected]> wrote:
>> 
>>     John Ackermann N8UR via Nut-upsuser
>>     <[email protected]> writes:
>> 
>>         I am monitoring via the SNMP driver an APC SmartUPS that has split
>>         phase (2L + neutral) 240V input and 120/120 volt outputs. The data
>>         for the voltages is not what I'm expecting, and I am wondering how I
>>         should interpret it.
>> 
>> 
>>     Wow, that sounds kind of industrial. Model?
>> 
>>     Is the input an L14-20P? Or equivalent non-twistlock?
>> 
>>         Here is an example from upsc:
>> 
>>         input.L1-L2.voltage: 121
>>         input.L2-L3.voltage: 120
>>         input.voltage: 121.20
>>         output.current: 5.90
>>         output.L1-L2.voltage: 119
>>         output.L1.current: 5.90
>>         output.L2-L3.voltage: 119
>>         output.L2.current: 1
>> 
>>         The "input.voltage" value doesn't reflect the 240 volts that is
>>         actually being applied. To get that, would I combine the L1-L2 and
>>         L2-L3 voltages?
>> 
>> 
>>     I would address figuring this out as two steps. One is to see what the
>>     device actually sends and what makes sense there. And then to see if
>>     NUT is mapping or making synthetic.
>> 
>>     I find it odd for the neutral to be labeled L2, as it seems to be. I
>>     would think there would be L1 and L2, both reported as phase-to-neutral.
>>     You might see if there is confusion.
>> 
>>     odd for output.L2.current, vs L3, given that voltage seems to be L1/L3
>>     vs L2.
>> 
>>     Probably the first voltage is mapped to just 'voltage' and probably it
>>     would be better to use the L1/L3 voltage. Similar for output.voltage.
>> 
>>     output.current should probably be average if output.voltage is 240ish.
>>     Or better yet
>> 
>>         Note that the "output.current" value matches the L1 output current,
>>         ignoring the L2 current. Perhaps that is a clue that the overall
>>         "input" and "output" values are not meaningful in this case?
>> 
>> 
>>     yes, and they are perhaps mapped from something else?
>> 
>>         How should I interpret these values to know the actual input and
>>         output voltages and currents?
>> 
>> 
>>     You're going to need to put a meter on it and compare to the reports, I
>>     suspect.
>> 
>>     First, see if you can get specs, and look at the snmp mib directly and
>>     see what you can figure out. Turn up debugging/verbose in nut.
>>     ------------------------------------------------------------------------
>>     Nut-upsuser mailing list
>>     [email protected]
>>     https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>     <https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser>
>> 
>> -- 
>> Sent from my Android device with K-9 Mail. Please excuse my brevity.
>> 
>> _______________________________________________
>> Nut-upsuser mailing list
>> [email protected]
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
>_______________________________________________
>Nut-upsuser mailing list
>[email protected]
>https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

-- 
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser