"Kevin P. Fleming via Nut-upsuser" <[email protected]>
writes:

> On Mon, Aug 17, 2026, at 11:24, Greg Troxel via Nut-upsuser wrote:
>> How do you get those machines to come back on when power is on and say
>> stable for an hour?
>
> The PDUs have the ability to delay power-on of individual ports, so
> the ones that need to come up 'after the core' are delayed by 10-15
> minutes. The PDUs don't know about power stability though, only
> availability, but they don't receive power until the UPS thinks the
> power is stable enough (and there's a decent amount of battery
> charge).

Sorry, I meant that differently:

  If you aren't using an ePDU, and you just "shutdown -p" the host, and
  say that power comes back before the UPS runs out (because, on
  important-loads-only, it lasted long enough), how does the host that
  shutdown restart?  In this case, an ePDU with commanded power off and
  power on would solve the problem.


_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to