Bill Gee <[email protected]> writes: > I have been getting very frustrated by the short runtime of my main > UPS. It is an APC BR1500G. I have a pair of 35ah batteries on it, > but even so it runs for only 10 minutes. The batteries are good > (independent testing) and the load is only 350 watts. I think the UPS > runtime calibration just does not work.
Did the testing do a controlled discharge at 25A and measure the capacity to 10.5V? Change your shutdown to trigger at 22V, instead of remaining lifetime. I suggest logging battery voltage and claimed remaining runtime, and doing a test with a simulated failure, graphing that, and posting it for comment. > Recently I noticed that some models of Bluetti power bank, such as > AC200L and Fridge, have a "UPS" feature. They boast of switching time > under 10ms in event of a power failure on the AC mains. The energy > capacity is around 2kwh which should run my load for three to four > hours. Expansion batteries can be added. And the price is not much > different from a brand new 1500 VA traditional UPS. That's interesting. The first thing I checked was the battery technology. Units like this used to have Lithium ion and that would seem dangerous. This says it is LiFePO4. It claims listing to UL2743. > Has anyone used one of these as a computer UPS? not me :-) > Is there a way to have NUT monitor it? It looks like bluetooth/app, the modern disease. I would suggest contacting bluetti, exlaining NUT, and asking for protocol details. I suspect if you asked a lot the manufacturers of UL listed LiFePO4 power banks, one of them might end up being reasonable. _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser