On 4/24/06, lonely wolf <[EMAIL PROTECTED]> wrote: > Secondary question: as you can see at > http://wdl.lug.ro/ablerex/upsilon.status.screen (and > http://wdl.lug.ro/ablerex/upsilon.config.screen ), upsilon reports: > ACfail Shutdown Delay: 1440 Min > UPS Turn Off Delay : 10.0 Min > 1440 min = a 24h (maximum allowed value) delay I have setup when > discharging the UPS, so that I can test nut while being sure upsilon > will not shutdown the computer used for tests. > Shouldn't these values be seen somewhere in upsc output ? How are they > related to "ups.delay.shutdown: 2" and "ups.delay.start: 3" ?
When NUT tells the driver to poweroff the UPS (after the machine has completed the shutdown sequence, and before it powers off), the UPS will stay on for "ups.delay.shutdown" minutes. After the UPS has been powered down, when (line) power comes back, the UPS will wait "ups.delay.start" minutes before powering itself on again (to lower the possibility of powering on when the power just came back momentarily). -- Carlos Rodrigues _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser