Hi,

On 8/17/06, Martin Ivanov <[EMAIL PROTECTED]> wrote:
So, this is the result of upsc [EMAIL PROTECTED] with the UPS connected to the 
mains:
battery.charge: 97.7
driver.name: powercom
driver.parameter.linevoltage: 220
driver.parameter.port: /dev/ttyS0
driver.parameter.type: KIN1500AP
driver.version: 2.0.4
driver.version.internal: $ Revision: 0.5 $
input.frequency: 49.61
input.voltage: 236.3
input.voltage.nominal: 220
output.frequency: 49.10
output.voltage: 236.3
ups.load: 38.9
ups.mfr: PowerCom
ups.model: Unknown
ups.model.type: KIN1500AP
ups.serial: Unknown
ups.status: OL

and this is the same, but with the UPS disconnected from the mains:

battery.charge: 145.0
driver.name: powercom
driver.parameter.linevoltage: 220
driver.parameter.port: /dev/ttyS0
driver.parameter.type: KIN1500AP
driver.version: 2.0.4
driver.version.internal: $ Revision: 0.5 $
input.frequency: 0.00
input.voltage: -0.1
input.voltage.nominal: 220
output.frequency: 49.61
output.voltage: 34.5
ups.load: 153.0
ups.mfr: PowerCom
ups.model: Unknown
ups.model.type: KIN1500AP
ups.serial: Unknown
ups.status: OB

I'm afraid you may be right, your UPS may not be supported by the
driver you use, because having a charge of 145% and a ups.load of 153%
is... quite strange ^_^


Mister, I am afraid I do not dare experiment with the UPS, forcing it into "LB" status. 
Once already I had to replace my UPS because of wreck battery, so I do not want to risk it once 
again. I really feel quite content with my system's power control now. The PC switches off 30 sec 
after the power failure and the UPS is far from "LB" status at that time. It goes on 
buzzing, but I think it is safe, for the power consumption from it is minimal. Am I not right? The 
same would happen if my PC is off, there is nobody at home and the power fails: the UPS will start 
buzzing until the power returns.

Yes, without the load of the PC, your UPS can buzz longer than with a
charge (obviously). But how many time... it depends on your UPS model.
It can be hours, or days. Normally, UPS should have a protection and
shutdown themselves if the battery is too low, but with some low price
model, there could not be such a protection. I cannot help you on this
point, try asking the manufacturer.

And if it happens that there are two short power falures one exactly 30 sec 
after the other, my PC will shutdown. Ok, having in mind the possibility for 
such a thing to happen, I do not find it quite annoying really :). Of course if 
you do not see some significant potential problem in all that.
And concerning the UPS shutdown,
I remind you my notifyme script:

echo `date` >> /root/upsLog
echo " No power, shutting down the system!" >> /root/upsLog
sleep 30
control=`/usr/local/ups/bin/upsc [EMAIL PROTECTED] ups.status`
if [ $control != OL ]
then
/sbin/telinit 0
fi

I tried adding the line: "touch /etc/powerdown" to the "notifyme" script and 
the lines:

if (test -f /etc/powerdown)
then
echo "Killing the power, bye!"
/usr/local/ups/bin/upsdrvctl shutdown

sleep 120

fi

to the /etc/rc.d/rc.6 script, but when I simulated a power failure, the system 
shut down, but the UPS did not. I think I did not add the lines at the correct 
place in the rc.6 script, or probably there is poor communication between the 
UPS and the software, for I am not sure the software I am using is for my UPS. 
In Slackware, rc.6 is the script that is executed when the system goes to 
runlevel 0 or 6.
Besides, I am not quite sure whether I need to make the UPS itself go down in 
case of power failure, because if it does not go down, it has the chance to get 
charged when power returns.
So what would you recommend to me? Make the UPS itself power off after system shutdown in 
case of power failure, or leave it buzzing till power returns? Remember, ny system is 
configured to shutdown well before the ups.status becomes "LB".
In case you advise me to make the UPS go down itself after the system shutdown, 
I will be thankful to you if you tell me if the method I suggest to achieve 
that is working and where in the shutdown script I need to add it?

I never worked on the shutdown of UPSs, so I cannot help on this
point. As you said, it is either a mistake you made, that your UPS
don't support shutdown command or that the driver you use don't know
how to properly ask the UPS to shutdown (or maybe a mix of the three
^_^)

Perhaps someone that better know the shutdown process can help you
better than me.


Thank you for your responsiveness.
Regards,
Martin

-----------------------------------------------------------------