On 5/7/07, Tom Laermans <[EMAIL PROTECTED]> wrote:
I have not tried Windows with PowerChute yet to see if it is reported corretly there; other values in the UPS data seem to be correct and valid.
It's always good to check and see if it's coming across correctly - each value in newhidups (usbhid-ups in post-2.0.5) comes from a table, and elements in that table may not all be supported the same way by all HID UPSes. You can also try starting the driver manually with debugging output enabled. Check to see the parameters passed to newhidups (e.g. "ps auxww|grep newhidups"). Then, stop the old driver, and add "-DD" to the parameters passed in by your startup script. There will be a good quantity of debug information. Let it run for about a minute or two, and see if you can't pick out the load value. Then gzip and send your log to the list, and we can try to figure out where the problem lies. -- - Charles Lepple _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser