> My thought was not to worry about shutting down the UPS. Since I want to > manually start the servers after a temp shutdown then if the server powers > off as a slave monitoring the fake UPS the server will never reboot as the > UPS will stay powered on. Or I could just be totally out in left field.
That will only work if the system running the upsmon master for the 'real' UPS, isn't monitoring the 'fake' UPS (if it is, it will set the POWERDOWNFLAG and the UPS will reboot). Consequently, it will never know that the temperature is too high. However, it is quite possible that by shedding the load of 30 systems, the dissipation will drop enough so that the room temperature stops rising, despite the lack of A/C. But that means that you leave at least one system running (the upsmon master). If that's OK, your solution is indeed simple enough. One resistor, some wiring and a (mechanical) thermostat that opens a contact above a certain temperature connected to a serial port should create something that mimicks a contact closure UPS. If not, you could still use a 'fake' UPS that is monitored by your upsmon master and use the NOTIFYCMD to create a flag that prevents 'upsdrvctl shutdown' from being called. Best regards, Arjen -- Eindhoven - The Netherlands Key fingerprint - 66 4E 03 2C 9D B5 CB 9B 7A FE 7E C1 EE 88 BC 57 _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser