On 8/31/07, Criggie <[EMAIL PROTECTED]> wrote: > Yes - Megatec works perfectly in nut 2.2 The only thing that has been > lost is "battery-charge" percentage.
If you find the "battery.voltage" when the UPS is fully discharged, and the voltage when the UPS is fully charged, you can use those two values in "ups.conf", in the "battvolts" parameter (for example: "battvolts=11.5:13.6). To find these values, the easiest way is to remove any important stuff being powered by the ups, and then run "megatec -DDD -a yourups > logfile.txt". And then sending me the output. I'll check the values to see if they can be added to the built-in table in the driver. > Megatec has introduced "UPS-temperature" but sadly it reads 0 for me. That means your model has no temperature sensor. > Apparently the same model is badged by many different suppliers. If it > looks basically like this then it should work. > http://cdlnz.com/productimages/jpegs/ups1700d.jpg -- Carlos Rodrigues _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser