>> i just wonder, if it is posible to read the values for all the three >> phases of a mge galaxy 6000 ups? > From looking at the mgemib part of the snmp-ups it doesn't read the data > of all 3 phases (yet). Though this should be fairly easy to add.
I have added this in my local copy for the MGE MIB, so it could work. > If the mge snmp adapter supports queries using the ietf mib that is > another way to get that data. though ietfmib.h in the current version > (and svn) is broken. (Arjen can you add the patch i sent you a while ago? > ietfmib.h uses the wrong OID for the query) Could you send that patch again? As far as I know, I committed all patches you sent, so it could be that I missed one. > And all snmp-ups driven upsen don't support shutdowns properly (yet). They probably never will support it in the same way as other NUT drivers do. This is because by the time we run 'upsdrvctl shutdown', we won't have networking capabilities anymore. So the only way to shutdown a SNMP UPS is by sending it an instcmd "shutdown.(return|stayoff|reboot)". This requires careful planning, as you want to make sure that the system you send this command from, has enough time to shutdown cleanly. You can either do this by allowing sufficient delay before the shutdown, or powering it from an alternative power source. Neither of these is without risk, so we must consider this carefully. Best regards, Arjen -- Eindhoven - The Netherlands Key fingerprint - 66 4E 03 2C 9D B5 CB 9B 7A FE 7E C1 EE 88 BC 57 _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser