> Hi,
Hi Lionel,
>
> I've been getting emails from upsmon saying:
>
>  Subject: UPS pw5...@localhost notification: ONBATT
>
>  UPS pw5...@localhost on battery
>
> But then the machines on the UPS stay on for hours; we haven't got
> that kind of runtime, more like 10-20 minutes.
>
> After a few occurrences, it now happened at a time where I could log
> in to see in real time what is happening and:
>
> $ upsc PW5125 | grep status
> ups.status: TRIM
>
This is fixed in a later release of the driver.

>From change log:
Wed Jan 14 21:45:10 UTC 2009 / Kjell Claesson <[email protected]>

  - drivers/bcmxcp.c: Changed status info to include OL with BYPASS, BOOST, 
TRIM.
    Add some more meters like power and current.nominal (max).

And also if you upgrade to a later release you have load segment control
and some more info from the PW5125 you run. 

Like this:

~ $ upsc pw5115         
ambient.temperature: 28            
ambient.temperature.high: 70       
battery.charge: 98                 
battery.runtime: 2060              
battery.voltage: 26.95             
driver.name: bcmxcp                
driver.parameter.baud_rate: 9600   
driver.parameter.pollinterval: 2   
driver.parameter.port: /dev/ttyS0  
driver.parameter.shutdown_delay: 10
driver.version: 2.4.1              
driver.version.internal: 0.21      
input.frequency: 49.65
input.frequency.high: 54
input.frequency.low: 46
input.frequency.nominal: 50
input.transfer.boost.high: 207
input.transfer.high: 266
input.transfer.low: 171
input.transfer.trim.low: 243
input.voltage: 234
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 1
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 2
outlet.2.id: 2
outlet.2.status: On
output.current:  0.0
output.current.nominal:  4.5
output.frequency: 49.65
output.phases: 1
output.voltage: 234
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.firmware: Cont:02.03 Inve:02.03
ups.load:   0.0
ups.model: PW5125     1000VA
ups.power: 0
ups.power.nominal: 1000
ups.serial: GB282A0427
ups.status: OL

Regards
Kjell

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to