On Sat, Jun 20, 2009 at 09:23:19AM +0200, Kjell Claesson wrote: >> I've been getting emails from upsmon saying:
>> Subject: UPS pw5...@localhost notification: ONBATT >> UPS pw5...@localhost on battery >> But then the machines on the UPS stay on for hours; we haven't got >> that kind of runtime, more like 10-20 minutes. >> After a few occurrences, it now happened at a time where I could log >> in to see in real time what is happening and: >> $ upsc PW5125 | grep status >> ups.status: TRIM > This is fixed in a later release of the driver. > And also if you upgrade to a later release you have load segment control > and some more info from the PW5125 you run. > Like this: > ~ $ upsc pw5115 > input.frequency.high: 54 > input.frequency.low: 46 > input.transfer.boost.high: 207 > input.transfer.high: 266 > input.transfer.low: 171 > input.transfer.trim.low: 243 > outlet.1.* > outlet.2.* Great! Thanks for the info, and for the commit. I'll schedule an upgrade for when downtime would be acceptable. (As it will be an upgrade from 2.2 to 2.4, I prefer to take the opportunity to test the automatic shutdown procedure again, especially with the Windows clients and all that. And being extra cautious and all that.) -- Lionel _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser