> Here is more informations.  I hope this can help.  Tell me if you need other
> information.
>
> Version :       Network UPS Tools upsd 2.2.0-
> Driver  :       usbhid-ups
>                Network UPS Tools: 0.28 USB communication driver 0.28 - core
> 0.30 (2.2.0-)

Many improvements have been made to usbhid-ups since 2.2.0. You may
want to upgrade, or at least check the ChangeLog to see what you might
be missing.

Try "upsrw u...@localhost" to see if your version of usbhid-ups has any
options that might affect the low-battery charge setting.

> [trixbox.logilys.net /]# upsc u...@localhost
> battery.charge: 9
> battery.charge.low: 10
> battery.charge.warning: 50
> battery.date: not set
> battery.mfr.date: 2008/11/25
> battery.runtime: 90
> battery.runtime.low: 120
> battery.type: PbAc
> battery.voltage: 12.4
> battery.voltage.nominal: 12.0
> driver.name: usbhid-ups
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.2.0-
> driver.version.data: APC/CyberPower HID 0.9
> driver.version.internal: 0.30
> input.transfer.high: 139
> input.transfer.low: 92
> input.voltage: 122.0
> input.voltage.nominal: 115
> ups.beeper.status: enabled
> ups.delay.shutdown: -1
> ups.firmware: 843.K1 .D
> ups.firmware.aux: K1
> ups.load: 38
> ups.mfr: APC
> ups.mfr.date: 2008/11/25
> ups.model: Back-UPS ES 550
> ups.productid: 0002
> ups.serial: 3B1808X13737
> ups.status: OL CHRG LB
> ups.vendorid: 051d
>
> Thank you
>
> Christian,
>
>
> -----Message d'origine-----
> De : Charles Lepple [mailto:[email protected]]
> Envoyé : 26 août 2009 20:13
> À : Christian Dubois
> Cc : NUT user list
> Objet : Re: [Nut-upsuser] Linux and the APC Back-UPS ES
>
>
> On Aug 26, 2009, at 7:01 PM, Peter Selinger wrote:
>
>> Dear Christian,
>>
>> thanks for writing. I am no longer active in driver development, so I
>> am forwarding your question to the NUT user list. The people on the
>> list are very helpful.
>>
>> Best wishes, -- Peter
>>
>> Christian Dubois wrote:
>>>
>>> Hi there, I found this document on the internet and it was very
>>> useful
>>> for me (http://www.mscs.dal.ca/~selinger/ups/backups.html), thank
>>> you.
>>>
>>> I successfully install and configure my ups over a Centos.  My ups go
>>> down on low battery when the power fail for a long period.
>>>
>>> But there is just a bug : my ups run out of battery before the end of
>>> the shutdown process (a full shutdown take less than 2 minutes).
>>>
>>> Is there a way to "start the shutdown process earlier", or to
>>> change the
>>> battery.charge.low or battery.runtime.low variables?
>>>
>>> I try to set a FinalDelay to 0, but it doesn't help.
>>>
>>> Do you have any idea to help me?
>>>
>>> Thank you.
>
> Christian,
>
> Can you please post some more details, such as the version of NUT
> which you are using, and which driver?




-- 
- Charles Lepple