On Sat, 10 Oct 2009 15:57:24 +0200, Arjen de Korte wrote: > Citeren Jean Delvare <[email protected]>: > > > Now the good news: the battery test command appears to work! > > That's good to hear. > > > The test.battery.start.quick command behaves exactly as when using > > APC's own software. The battery is being tested for a few seconds, then > > the UPS returns online, and ups.test.result is set to "Done and > > passed". Perfect. > > Indeed. > > > I am a little skeptical about the test.battery.start.deep command. When > > I run it, the UPS switches to battery. After one second, nut tells me > > I'm on battery, and one second later that I am back online. However, > > the UPS is _still_ on battery, I can see it on the front panel (and I > > can hear it, too.) > > While this may seem confusing, this is actually what it is supposed to > do. After all, the OL/OB flag only tells you something about the line > status and when you run this command, most likely that is not > changing. So during the test, it is actually correct that the OL flag > is set (so 'online' would be correct). > > > Then I waited some more and nothing changed. After a > > minute I had to issue a test.battery.stop command to return online. > > You probably need to be more patient. It may take quite a while for > before the battery reaches the battery low charge. > > > It worked OK, but now ups.test.result is set to "Aborted". > > Very good, so the test.battery.stop command also works. This seems to > be a resounding success... :-) > > > So maybe I wasn't supposed to stop it? How long is it supposed to last? > > I couldn't find documentation on how the deep test is supposed to behave. > > Usually until the battery charge reaches the 'low' level, at which > time the UPS should stop the test and resume to normal. Depending on > the amount of time since the test was started and the load present, it > may also inform you about the health of the battery.
Ah, OK. Then indeed I have not been patient enough, as my UPS has 33 minutes of runtime when the battery is full (which it was) and battery.charge.low is 10/100 so I guess I should have waited for about 30 minutes before the low limit would have been hit. > > After that I couldn't issue a test.battery.start.deep command again, > > nothing happened when I tried. test.battery.start.quick still works > > though. > > I just recalled that some UPSes will refuse to run a deep discharge > test when the battery isn't fully charged and/or need to be charging > continuously for an 'X' amount of hours (with 'X' typically being 12 > to 24). So chances are this will work again if you wait a day or so. Yes, that could be what happened, as the battery was still recharging after the first (aborted) deep test when I started the second one. Makes sense. > PS Also, be advised that running deep discharge tests wear out your > battery, so you should only run these once every three to six months > (at most). Thanks for the hint. I didn't intend to use it again any time soon anyway. I presume it is essentially useful when you suspect that the battery needs to be replaced. Which I hope I won't have to do before 4 years or so. Thanks a lot again for your excellent support :) -- Jean Delvare _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser