On Wed, 21 Oct 2009, Arjen de Korte wrote:
Citeren Charles Lepple <[email protected]>:
could this be a result of setting pollfreq too low?
http://article.gmane.org/gmane.comp.monitoring.nut.user/5043
If this is not how pollfreq works, then I stand corrected - but if the
device is fully polled once every 30 seconds, and a power outage occurs in
that 30-second window, I would think that NUT would get an interrupt
report.
In between full polls, we do quick polls every 'pollinterval' (default: 2
seconds) to retrieve some info should the UPS not provide interrupt reports.
Only NUT variables with the HU_FLAG_QUICK_POLL will be retrieved then, which
typically means that we only need to refresh two or three reports (since
status bits are usually aggregated in one or two reports), which limits the
load to the UPS.
Setting the pollfreq to 5 seconds is counter productive here, since this will
only increase the amount of reports to retrieve (which is something some UPS
devices can't handle), while the things Justin is interested in will already
be polled every 2 seconds anyway.
Hello,
Even without the poll option, the error persists, but it takes longer to
trigger (3-5 minutes vs. 1-2 minutes @ 5 second follreq)
Broadcast Message from [email protected]
(somewhere) at 5:54 ...
Communications with UPS a...@localhost lost
Broadcast Message from [email protected]
(somewhere) at 5:54 ...
Communications with UPS a...@localhost established
$ cat /etc/nut/ups.conf
# USB:
[apc]
driver = usbhid-ups
port = auto
desc = "APC 1500VA"
# pollfreq = 5
# productid = 0100
Justin.